I need a new boiler and would prefer a 35KW combi boiler but wanted to know if my existing gas pipe will allow it. I wanted to check this first so i can look at my boiler options before getting somebody around.
I don't have any other gas appliances and my existing pipe is 22mm. The gas meter is located next to our front door in a box at ground level. I have no wish to take up my Oak floor to lay a new pipe.
I have attached a rough sketch of the gas pipe run and would appreciate any advise. Thanks .
 

Attachments

  • boiler 1.jpeg
    boiler 1.jpeg
    14.2 KB · Views: 40
1. Your gas run is roughly 20 metres.
2. You appear to have 7 elbows. I'd suggest you count this as 10 (allowing for ones by the meter which may have been missed), so a further equivalent 5 metres.
3. The manufacturer's data will tell you exactly, but a 35 kW boiler will require around 3.8 cubic metres of gas per hour.
4. A 25 metre run of 22 mm pipe will only support a flow rate of 2.6 m cubic metres / hour, so is inadequate.
5. Subject to a specific site survey, you would need 28 mm pipe for the run.
6. Because gas is compressible, a required flow rate may be achievable with a mixture of pipe sizes. This would need a precise on the spot calculation. It can't be done over the internet. However, it MIGHT allow you to avoid damaging a floor.
7. For those who might consider this too much information, all the above is freely available on the internet. Mostly at https://copperplumbing.org.uk/sites...achments/domestic-gas-planning-and-sizing.pdf
 
Gut feeling 28mm required as it’s around 20m

24kw is pushing it for 20m on 22mm
 
Ok thanks all. New pipe was my gut feeling but it's a real pain having to lift an oak floor and chase across a newly tiled kitchen floor.
I was looking at a 35k Worcester greenstar 8000 lifestyle as we have a Bosch Worcester floor mounted 400 high flow at the moment, the difference being the floor mounted has a hot water storage tank in it.
I have 5 bedrooms, one bathroom and one shower room and no other gas appliances so maybe a smaller KW would be ok. What do you think?
 
I need a new boiler and would prefer a 35KW combi boiler but wanted to know if my existing gas pipe will allow it. I wanted to check this first so i can look at my boiler options before getting somebody around.
If you can find space for a hot water tank somewhere you could have a (much?) smaller boiler and the pipe capacity would no longer be an issue.
 
I would say unvented cylinder and a boiler if you have the space

if not could you go external with the gas pipe and back in close to the boiler ?
 
Sorry to say a 35kw boiler will need a new 28mm gas supply , you would be better to fit a unvented hot water cylinder paired with a new lower kw output boiler for a family home. Kop
 
I would say unvented cylinder and a boiler if you have the space

if not could you go external with the gas pipe and back in close to the boiler ?
Yes we looked at that as we can avoid going across the front of the house because the front room has carpet and suspended floor. But it would go the full length of our sideway and across the back. We have rendered walls with a black plinth along the bottom which is set back from the render 10mm so even if we tucked it under there it will stick out a fair amount, possibly 35/40mm.
Would look pretty ugly.
[automerge]1600508996[/automerge]
Sorry to say a 35kw boiler will need a new 28mm gas supply , you would be better to fit a unvented hot water cylinder paired with a new lower kw output boiler for a family home. Kop
The only place I have room for a cylinder is below the new wall hung boiler where the existing floor mounted boiler is but I'm not sure that would be enough space. I have attached a picture.
[automerge]1600510574[/automerge]
Thanks for all the advise, even though my original plan was for a smaller neater boiler perhaps I should go like for like and fit a direct replacement (greenstar 440 CDI high flow) which has a 7.5 - 29.2KW rating , I'm guessing that will work with my pipes.
Just trying to get my head around my best option before getting the engineer around . When you book an engineer through Bosch online you have to pick the boiler you want .
 