buffy27

went to look at an oil burner tonight .... it was an indoor firebird ..the flue outside was red hot on the inside ..<br>why would this happen on a balanced flue ...<br>owner is a mechanic and said the burner was burning black recently and he adjusted the air damper .burned clean again but a touch louder from the flue outside he noticed ..i am a tad confused &nbsp;with this scenario .any ideas at all ....
 
You need Simon for this. Not me thou. The other Simon. He seems to be the oil expert
 
Too much air = too hot flame.
Baffles may be burnt out. Needs a strip down service, new nozzle and set up properly.
 
ya,, thanks for the great help there tamz...lol
got it sorted ..riello g5x.. ..there were a number of things wrong ,,culminating in too much heat been drawn out flue .. never seen it to happen before ..low level balanced flue reddening ? gave it a full service and had to make alterations to say the least to rectify problem..incorrect atomizer,oil pressure was 14 bar ,,lol ... damper was set to 5 for air intake ..lol [ended up back to nearer 2.25 for complete combustion ] ..baffles wer in completely wrong ..new experience for me to c this happening ..we live and learn ..
 
As tamz says flue temp is too high, if it was burning with black smoke then chances are its nice and sooty inside, and he's then opened the air shutter up to get it to burn cleanly and now its just shoving all the heat strait through the boiler and out the flue. All it should need is a good service.
 
ya,, thanks for the great help there tamz...lol
got it sorted ..riello g5x.. ..there were a number of things wrong ,,culminating in too much heat been drawn out flue .. never seen it to happen before ..low level balanced flue reddening ? gave it a full service and had to make alterations to say the least to rectify problem..incorrect atomizer,oil pressure was 14 bar ,,lol ... damper was set to 5 for air intake ..lol [ended up back to nearer 2.25 for complete combustion ] ..baffles wer in completely wrong ..new experience for me to c this happening ..we live and learn ..

As i said. It happens when people play about with them and being a mechanic the guy probably thought a bit more pressure and plenty air means big horses :lol:
 
Reminds me of when an old tutor of mine modified a burner and built a hog roasting oven out of steel oil barrels in his workshop, and powered it with waste kerosene. Was quite a contraption and could cook a whole pig to perfection.
 
Last edited:
If I hadn't already had me tea that would make me hungry.

You know you're in for a treat when you take the front cover off and there's an assortment of allen keys and spanners in the bottom of the boiler. Time to set it up from scratch.
 
Status
Not open for further replies.

Reply to balanced flue ..problem ...never seen this before in the Plumbing Jobs | The Job-board area at PlumbersForums.net

Similar plumbing topics

H
  • Locked
Any advice much Appreiciated. I was called to Rayburn 480kb its Eco Flam >2001 customer complaining about fumes smell lock out. I Serviced and...
Replies
6
Views
3K
L
    • Like
  • Locked
Well it seems everytime I go to this bleedin bum end of the county, it goes wrong. first 48 miles to get there, and the sat nav delivers me to a...
Replies
6
Views
163
O
  • Locked
Hi, I'm not a heating engineer and I have no intention of touching our boiler, but I really could do with some friendly advice regarding a...
Replies
39
Views
14K
Back
Top