Discuss back boiler heating circulation issues in the Plumbing Jobs | The Job-board area at PlumbersForums.net

Status
Not open for further replies.

Nas

Plumbers Arms member
Plumber
Gas Engineer
Messages
137
I hope someone can help as its driving me round the bend.
Its and open vented system with a baxi 552 back boiler. the water work perfectly but the heating flow pipes to the radiators get hot but there is no circulation . The flow pipe is hot to all the radiators but the return pipe is cold

Things ive checked:-
1) the pump is fine (its new)
2) the 2 port valve controlled by the room stat work is ok.
3) all the return pipes have water in them indicating no blockage.


the sytem has 10mm pipe running off the 22mm flow and return.

Am I Missing something obvious? Any suggestion appreciated

Thanks in advance
 
Sounds like blockage the return will have water in regardless as it feeds through boiler and coil. Manifold?
 
As above. Restricted circulation.

Did pump valves open properly after pump was changed ?
 
As above. Restricted circulation.

Did pump valves open properly after pump was changed ?
 
Check for blockage where cold feed meets the heating system return. Also check for failed anti gravity check valve fitted in return pipework from heating often enclosed in fireplace adjacent boxing if still on gravity hot water or not removed when converted to fully pumped.
 
Status
Not open for further replies.

Reply to back boiler heating circulation issues in the Plumbing Jobs | The Job-board area at PlumbersForums.net

Similar plumbing topics

Hi, I have a Worcester 28i junior boiler that has started to lose pressure, only when using the central heating. When using hot water I have no...
Replies
6
Views
283
  • Question
Ideal Logic 24, Previous problem was that the hot water was only cold or barely warm if the heating was in use. If heating was off and boiler cold...
Replies
2
Views
229
Every two weeks or so I have to go and top up the system because the hot taps are running cold. Boiler display is flashing 0.6 bar and I fill up...
Replies
2
Views
299
PSxxxxxx
P
Hi everyone, Looking for a bit of advice, recently went to a job where heating was operating when called for however not for the hot water. I...
Replies
8
Views
404
S
Hi, I seemed to have a blockage in kitchen sink. A plumber came and cleared all the pipework that is visible inside my home (there was debris and...
Replies
2
Views
164
Sonya K
S
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock