Matt0029

Gas Engineer
Messages
1,138
When testing the safety device on a combi boiler (ideal instinct). I know to make a fault, by turning off the gas supply. If the safety device is working correctly the boiler will go to lock out within 2 minutes and won't fire again once the gas is reinstated without resetting the boiler. What is the correct/best way of checking the gas valve is not passing once it goes to lock out?
 
Would a tightness test at the meter when the boiler goes to lock out after 2 minutes be adequate to test this?
 
Would a tightness test at the meter when the boiler goes to lock out after 2 minutes be adequate to test this?

Yea mate absolutely. Or gauge on gas valve inlet and open boiler iso valve after lock out then close it for test if your only testing the appliance.
 
Status
Not open for further replies.

Reply to Testing safety devices on combi boiler (ideal) in the Plumbing Jobs | The Job-board area at PlumbersForums.net

Similar plumbing topics

  • Article
A Plumber Who Worked Illegally Gets A Suspended Sentence After Falsely Claiming To Be Gas Safe Registered. A Plumber in Herefordshire was...
Replies
0
Views
248
We run a community village hall and have a large kitchen provided for the use of hirers. This includes a Lincat SLR9 gas cooker which I believe is...
Replies
5
Views
562
Hi, Can anyone advise as to why the cold water to my bathroom keeps airlocking? This originally happened about 12 months ago and has happened 3-4...
Replies
9
Views
465
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock