We recently had a 120 litre Gold unvented cylinder fitted in our first floor airing cupboard. The cylinder's pressure release valve D2 discharge pipe is plastic (originally fitted for the previous twenty year old BoilerMate) and looks about 22mm diameter. There is approx 100mm of vertical section discharge pipe between the tundish and the first 90 degree bend. There are two such bends before a straight run of pipe (with a nice looking fall) about two metres long that goes behind the bath and through the external wall and exits over a concrete path in our garden at a height of about 2500mm. British Gas inspected this last week and refused to insure the central heating under their Homecare plan (a) because of the plastic pipe, and (b) because the pipe exits over a walkway. Their inspector also wasn't happy about the 100mm vertical section between tundish and first bend. The plumber who fitted the cylinder has suggested replacing the D2 with copper (not sure what size he intends using, I'm assuming 22mm is a minimum) and turning the pipe towards the wall where it exits. Not sure what his plan is regarding the 100mm vertical section (I now realise this should be 300mm minimum, though I can't see how he can achieve this as there's precious little vertical room to manoeuvre in the airing cupboard).


I can't see any reference to turning the pipe towards the wall in the G3 building regulations. Is this an acceptable way to terminate the discharge pipe?


Also, just how critical is the 300mm minimum vertical drop between tundish and first bend?


Thanks
 
*If the pipe exits up high he must brim it down to the ground and fit a cage Over the end of the pipe, *there must be 300mm between the tundish and the first elbow
*the plastic pipework must be capable of carrying high temperature water and not just standard plastic
 
back to wall terminations are only allowed in exceptional circumstance and i think you have to get building controll permission
 
Hi Peter,

The reason why the BG Engineers didn't like the D2 termination area is because the water that comes out could potentially be scolding hot and constitutes a danger to anyone walking under it. Extending the pipe down so it is no more than 100mm off the ground, terminates close to the wall and is covered by a guard or cage that maintains visibility should sort it.

The D2 pipe (below the tundish) should be at least one size larger than the D1 pipe (that's the pipe above the tundish) so 22mm should be sufficient so long as the D1 pipe is only 15mm. The effective length of the D2 pipe at 22mm can't be more than 9m long. That includes the resistance of the fittings as well - each elbow equates to 0.8m. This means that if you have 3 elbows (2.4m equivalent) on your D2 pipe run then you can only have 6.6m of 22mm copper pipe. Make sense?

The regulations state that the D2 pipe should be of a material capable of taking high temperature water, which some plastic pipes are, but it also contradicts itself and states that it should be metal pipe. To be safe, take the plumbers advice and use copper. Turning it into the wall isn't enough though, it needs to terminate low down.

Where the pipe goes through the wall it should be sleeved to protect it. Plastic pipe should be good enough for this.

Not sure what to suggest in order to accomplish 300mm of vertical pipe below the tundish without seeing it. It does definitely need to be 300mm though if it is to comply with G3 building regs.

The bottom line is that the system is not that old and does come under current building regs. With that in mind the people who originally installed it have a responsibility to come round and fix it free of charge since the job you paid them for hasn't been completed!

Hope this helps.
 
What paperwork did you get for the install. Sounds like somebody has installed it who shouldnt have.

The sad thing is that you dont even have to refer to the g3 regs, as all the necessary info is in the installation manual. RTFM.
 
SinonG is right. Everything you need to know is in the manufacturer Instructions which the installers should have given you after the job.

Irony is, is that I have come across British Gas installs that contravene all sorts of building regs :)
 
From the logic training course notes. Doesn't say owt about LABC permission being required. I wouldn't bother asking.
 

Attachments

  • UV Discharge.jpg
    UV Discharge.jpg
    85.9 KB · Views: 123
Also, just how critical is the 300mm minimum vertical drop between tundish and first bend?


Thanks

At full volume discharge the water will back up if there isn't sufficient fall between the outlet of the tundish and the first bend.

I can't see how a large cylinder airing cupboard cant accommodate this 300mm fall especially if it is then running under a bath?

If you can connect the discharge from the tundish to the waste pipe under the bath (provided it can withstand 100degC water) you may wish to connect the TRV/PRV with a product called Hotun.

This product has been designed to be both a tundish and a odour trap to prevent foul odours coming back up from the waste pipe. The product has an internal drop sprung seal inside it.

It only costs at list ÂŁ22.60 and trade it should sell for about ÂŁ15.85+vat

Fitting Hotun enables you to do away with the external discharge pipe altogether.

Hot tun Production sample and components dissasembled.jpgHot tun Production sample assembled.jpg

If you have any questions please feel free to ask

regards

Russ
 
English building regs list the back to wall discharge termination as the least liked, but it is still an approved method, and just a note on it, the gap between the wall and the end of the pipe needs to be at least the same size as the pipe itself to allow water to discharge freely
 
Who ever fitted it, needs to come back and fit it according to the standard at there cost. no excuses for such deviations from standards. If it were to discharge it could give someone a scalding hot shower.
 
From the logic training course notes. Doesn't say owt about LABC permission being required. I wouldn't bother asking.
Take care croppie this is only logic's interpretation!
Nowhere does it say that the discharge (D1) pipework from the expansion relief is limited to 600mm !!! that limit applies only from the T&P valve.

I am going to guess that is why the OP thinks it is not possible to achieve the min 300mm vertical below the tun dish on a 120L Gold.

And yes it is important to have at least that, want to no why ? Pull the T&P safety valve, peter, as is required to test it from time to time (this would happen if it went off under high temperature condition)!!!

As others have said get the installer back & ensure that they have registered the installation as required by the Building Reg's if they have not, unfortunately it is you that has broken the Law.
 
At full volume discharge the water will back up if there isn't sufficient fall between the outlet of the tundish and the first bend.

I can't see how a large cylinder airing cupboard cant accommodate this 300mm fall especially if it is then running under a bath?

If you can connect the discharge from the tundish to the waste pipe under the bath (provided it can withstand 100degC water) you may wish to connect the TRV/PRV with a product called Hotun.

This product has been designed to be both a tundish and a odour trap to prevent foul odours coming back up from the waste pipe. The product has an internal drop sprung seal inside it.

It only costs at list ÂŁ22.60 and trade it should sell for about ÂŁ15.85+vat

Fitting Hotun enables you to do away with the external discharge pipe altogether.

View attachment 20139View attachment 20140

If you have any questions please feel free to ask

regards

Russ
Has this been approved for use on un-vented system discharge pipework Russ ???
If not, if not it cannot be used !!!!!
 
Has this been approved for use on un-vented system discharge pipework Russ ???
If not, if not it cannot be used !!!!!

approved by who Chris?

as the regulations stand the product does not have to be approved by anyone! Having said that it does have to comply with 7 regulatory provisions or be no less effective than the guidance given.

This product complies with all relevant regulations and it temperature rated to 100degC

if someone wants to find out more details then please pm me and I will provide ALL compliance documentation

back to Chris, who would you want it "approved" by and I'll let you know what the status is at this time

cheers

russ
 
I bet the 300mm minimum from D2 pipe to first bend is not there because either the D1 pipes are configured too low or/and the D2 has been angled up to too high a position.
The exam I redid recently clearly says the discharge through a wall at, in this case 2500mm high, must be run to within 100mm off the ground with a cage or more ideally into a gulley above the water level but below the grate. As far as I read it, no cage required if discharge fully inside gulley.
 
Russ, does that tundish rely on the weight of the water to compress the spring, and push down the rubber to allow water to get flow into d2?

If so, do you think it will still operate in years to come when the spring potentially scales up?
 
Last edited:
Russ, does that tundish rely on the weight of the water to compress the spring, and push down the rubber to allow water to get flow into d2?

If so, do you think it will still operate in years to come when the spring potentially scales up?

hi tolly

yes your right about the water being used to operate the valve

it has been carefully designed to open at between 4ml-10ml of water acting on the diaphragm to allow low volume flow

it will also take a full discharge volume flow from the TRV/PRV (ie under annual cylinder maintenance valve operation

and it is a requirement of the warranty of the product (2 years parts and labour + 3 further years full product replacement, that Hotun is serviced annually

on the plus side the company is being proactive in its warranty cards in that it will be offering to the installer of the product (and hence cylinder at the same time) that it will write to both installer and end user that the products require annual service and that the installation company should be giving them a call also. So you can pick up cylinder maintenance work!

If Hotun is operated annually the mechanism will work and function as required.

cheers

russ
 
Thanks Ermin

OMG the connection you show is so non compliant for starters

1/ Undue consumption (no visible means of seeing discharge)
2/ Safety issues, if you cant see that the PRV is discharging telling you that there is something wrong with the cylinder then you don't know its malfunctioning
3/ No Back flow contamination from Cat 5 water!!

Householder can be held criminally responsible if the regulator finds out and he doesn't comply with enforcement notices.............

Russ
 
approved by who Chris?

as the regulations stand the product does not have to be approved by anyone! Having said that it does have to comply with 7 regulatory provisions or be no less effective than the guidance given.

This product complies with all relevant regulations and it temperature rated to 100degC

if someone wants to find out more details then please pm me and I will provide ALL compliance documentation
back to Chris, who would you want it "approved" by and I'll let you know what the status is at this time
cheers
russ
Got a vested interest in this one then Russ ?? It would be nice for you to declare it, if this is the case.
All I know is that a couple of years back was talking to Multikwik or McAlpine, can't remember which, they had a spring operated waste valve & I asked their technical was this suitable for use inplace of the HepvO, as it was temp rated & was told no it was not approved & could not be used as it had not been tested.
How do you prove it is fit for purpose ?
 
Last edited:
Thanks Ermin

OMG the connection you show is so non compliant for starters

1/ Undue consumption (no visible means of seeing discharge)
2/ Safety issues, if you cant see that the PRV is discharging telling you that there is something wrong with the cylinder then you don't know its malfunctioning
3/ No Back flow contamination from Cat 5 water!!

Householder can be held criminally responsible if the regulator finds out and he doesn't comply with enforcement notices.............

Russ

Fully complaint with mi. Pulled kitchen mugs. Was there assessing the mess they made 6kw load on 10mm piggy back! Woop woop
 
Got a vested interest in this one then Russ ?? It would be nice for you to declare it, if this is the case.
All I know is that a couple of years back was talking to Multikwik or McAlpine, can't remember which, they had a spring operated waste valve & I asked their technical was this suitable for use inplace of the HepvO, as it was temp rated & was told no it was not approved & could not be used as it had not been tested.
How do you prove it is fit for purpose ?

By vested interest do you mean that I have something to do with the development of the product? In that case yes I do.

The problem the industry faces is to discharge the PRV waste in full compliance with the regs

Historically the PRV was first piped to tundish then pipe to drain safely outside the building, problem with that was it was very expensive. Then someone very clever at Wavin or Hepworth thought of using their Hepvo as an odour trap located after the tundish, it was cheaper and a better solution that overcame most situations. Over the last few years it is fast becoming the staple of EVERY unvented (large) cylinder install and I can see why, so hats off to them.

Now you have spotted something that I did as well and came across the same answer from McAlpine, I asked why not put a tundish then a tun valve after the tundish, as you point out it is temperature rated. I suppose being a big company they tend to be shy of making the wrong recommendations so gave you the answer they did. That said I have seen a few installations put in that way and I am sure they would past muster in terms of regulation compliance and fit for purpose especially as Ermintrude has pointed out above, the alternative non compliant installations.

This new product, Hotun, is innovative because it includes the spring return and within the height of a standard tundish! I tell you it was no easy feat to engineer that one and make it work.

The key really was to ensure it sealed tight against odours but still let trickle volumes through, step in one clever spring manufacturer, get the rate right, know your lengths and tolerances to allow for spring pre-tension, know the all up weight of the sprung components, know intimately how the water regs and bulding regs overlap and how to ensure compliance, solve all that and Hotun is born.

I stand true to the ethos of providing professional help to people and have no problems about telling them what is available as alternatives because ultimately you will find that the other alternative solutions are always more expensive to buy and then install than Hotun. And let us not forget that when dealing with under counter installations space is always at a premium........

But that is for the installation professionals to find out by research.

Over to you guys and I hope I am still on the right side of forum rules if not I will take these posts down without hesitation because I have a difficult balancing act to get right, and on that that's over to you Chris, would you please be as kind to pm me and let me know as I do not want to fall foul of the rules.

Cheers

Russ
 
There's the Building Regs and then there's Approved documents.

We just had a recent interesting run in with our compliance body, when we proved one system highly compliant with the Building Regs and totally contrary to the Approved Documents, it took them three weeks to finally agree we were right and the system we installed was safe and compliant. (Building Control had been happy all along :) )

It was not the Approved Document G, Section G3, it was another regulation, though the principal applies - all you have to do is show that:
From UKSI 2010 No. 2214, The Budilding Regulations 2010

Schedule 1, Part G Paragraph G3 Hot Water Systems:

A hot water system that has a hot water storage vessel must incorporate precautions to -
a) prevent the temperature of the stored water in the vessel at any time exceeding 100°C
b) ensure that any discharge from safety devices is safely conveyed to where it is visible but will not cause a danger to persons in or about the building.

So that's it, just prove the above (no mention of tundishes, no mention of 600mm or 300mm or one size larger....) - easy way roll over and blindly follow the AD, or work with the likes of Russ to find practical solutions. From Russ's point of view an independent test body (any will do) showing temperature and flow parameters could then be used to support your compliance assertions. :)
 
Last edited:
Thanks to everyone for taking the trouble to reply. The installer came back and fitted a 22mm copper discharge pipe down the side of our house and terminating a few inches above ground level. He also reconfigured the pipework in the airing cupboard to give a 300mm vertical section between tundish and first bend/elbow. British Gas inspected today and said it was fine. We're now back on British Gas HomeCare 400.
 
Thanks to everyone for taking the trouble to reply. The installer came back and fitted a 22mm copper discharge pipe down the side of our house and terminating a few inches above ground level. He also reconfigured the pipework in the airing cupboard to give a 300mm vertical section between tundish and first bend/elbow. British Gas inspected today and said it was fine. We're now back on British Gas HomeCare 400.
Thats great & you seem to be happy to be back with BG but was the installation notified to your local Building Control ?
 
Thanks to everyone for taking the trouble to reply. The installer came back and fitted a 22mm copper discharge pipe down the side of our house and terminating a few inches above ground level. He also reconfigured the pipework in the airing cupboard to give a 300mm vertical section between tundish and first bend/elbow. British Gas inspected today and said it was fine. We're now back on British Gas HomeCare 400.

I hope the discharge run is no more than 9 meters including bends
 
We received a "Buildings Regulation Compliance Gas Safety Certificate" shortly after the installation. The discharge pipe is no more than 5 metres long with three bends.
 
Status
Not open for further replies.

Reply to Unvented cylinder discharge pipe in the Plumbing Jobs | The Job-board area at PlumbersForums.net

Similar plumbing topics

Hello I am looking to install a slimline dishwasher (integrated) into a cupboard in my kitchen. The depth of the dishwasher is 550mm and the...
Replies
22
Views
531
Hi, Can anyone advise as to why the cold water to my bathroom keeps airlocking? This originally happened about 12 months ago and has happened 3-4...
Replies
9
Views
414
Creating content since 2001. Untold Media.

Newest Plumbing Threads

Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock