hi i have just installed to 15kw grant ashps to a 16th century manor rebuild and a grant 26kw oil boiler to meet the demand for heat and water when the ashp's dont meet the demand, the whole systems set up correctly through a low loss header in the basement... but my problem is the air sources are drawing close to 300 amps when the start up, this spike happens at least 30 times a day and everyone else in the area has problems with their lights etc when this happens, the electric board are now threatening to cut the power to the house... when we went back to grant they didnt have a clued and kept fobbing us off with excuses like they have come out to look at it when they havent and they are making something to fix this??? which if they havent looked at the ashp's how can they know??? has anyone else out there had any similar problems?? many thanks alastair
 
are you sure youve got that right 300 amps equates to 69kw on a 15Kw heatpump. If so tell grant to remove it immediatley refund your money and give you some compensation for your electric bills
 
You got a big problem shut off the heat pump and just use the oil boiler till sorted
 
Started current if DOL can cause the initial current inrush to be 6 - 8 time FLA you could reduce this with a soft start by about 50 %
 
thank you just for the record its not on my house but the customers i installed it in but thanks has anyone used these grant aronas before??
 
thank you just for the record its not on my house but the customers i installed it in but thanks has anyone used these grant aronas before??

You installed it there is no way that can be set up correctly
 
I was referring to the heat pump as to which grant are far from the best. but agree with you on the oil
 
I was referring to the heat pump as to which grant are far from the best. but agree with you on the oil

I know nothing about heat pumps and at a running cost of £7000 I don't want to either
 
it was comisioned by grant themselves and they said it was perfect??? and the customer choose them
 
I presume it is single phase, if this is the case refer to my previous post on a soft start
 
I presume it is single phase, if this is the case refer to my previous post on a soft start

I don't know to many houses on 3 phase
Even with soft start it can't be working correctly with that much draw of electricity
 
I install 25Kw heatpumps on single phase working on 32 amp mcbs with not a single problem, 300 amps sounds completley wrong to me
 
15Kw will be the output of the heat pump hence the input would be around 4 or 5Kw however the 300 or so amp start up is only for a fraction of a second i.e 3 or 4 cycles or 0.02 of a second.
many factors determine start current but it would seem logical to fit a soft start if the electric installation is correct
 
Hi I know it,s a bit late but only just found this thread I too have installed 2 13kw output Grant air source heaters and we are having no end of trouble with them.....
It seems that when they go into defrost mode the current goes through the roof although in the paperwork that comes with them states that they have a maximum operating current of 30Amps we have seen them taking over 80Amps but only when in defrost mode.... But when you talk to Grant they say it's impossible.... so we have purchased 2 owl electricity monitors to record the electricity useage to attempt to prove that they do take over 80Amps....
I guess it just depends on them beliveing the data collected.... Due to the fact that the engineers have to travel up from somewhere in Sussex ( we are in the West Mids ) they just don't want to wait around for it to happen they just want to be back on the way home asap. But when they do come apparently we are the only people in the country having these problems or so they tell us but I now know this to be lies since seeing this.

How are your problems going are they sorted yet??
might pay us to get together and sort them out???
 
Hi,

Is the back up immersion 3kw or (6kw available) kicking in?

That would explain the extra Amps

Edit just noticed the 30Amps includes 3kw immersion but they may have 6kw heaters but that wouldn't take it to 80 Amps?
 
Last edited by a moderator:
how long has the 80 amp current been happening? is it recent or has it been for quite a few months
 
In Response...

When the current is high i.e going to 80Amps no the immersion heaters are not on the ones we have only have the 3kw heaters.
But in the paperwork it clearly states that the total load is 30Amps should these figures include when the heaters are on?
the label on the rear of the ASHP states that it's running current is only 11Amps but we were told those stickers are not for the U.K market which makes no sense at all as no matter where in the world it is the calculation for the amps on a 240V machine remains the same i.e
watts divided by volts gives you the amps
 
how long has the 80 amp current been happening? is it recent or has it been for quite a few months

This has been an ongoing problem since around October 2010 they haven't run correctly since they were installed....
they only go into the 80Amps when in De-frost mode. You can hear the compressor getting harder and harder to spin as if there is supposed to be a solonoid to switch over for its de-frost cycle but it doesn't open. so the pressure builds and builds therefore causing the current to creep up and up as the pressure builds. sounds like its just gonna blow up when it reaches its peak the whole ASHP is going to shake itself to bits...
 
You need a refrigeration engineer to evaluate the refrigeration/electrical circuits, Where are you based ?
 
You need a refrigeration engineer to evaluate the refrigeration/electrical circuits, Where are you based ?

I agree but while Grant have not yet started their warranty it has to be up to them to repair it if we get an independant engineer to look at it or possibly sort it out will this not then result in them cancelling any warranty?

I'm sure if I delved in deep enough I could probably sort it but it's not my responsibillity I just feel sorry for my customer that has them fitted...

also info not stated yet is that when the units were first put in they come fitted with an outside air temp sensor... when the units froze up in the very cold winter we had the first thing they did was to disconnect the air temp sensor and fit a resistor in its place so now they are still going into a de-frost mode but surely in this milder weather they should never need to go into this de-frost mode where they essentially just waste heat blowing it outside... which in turn makes them uneconomical when this is mentioned to Grant they tell us that all the units are now being done like this... going back to them telling us we have the only units that are playing up why would they roll out a second rate modification that forces the units to use more electricity.
 
just realised I never answered where are we based this is the West Midlands U.K
 
I would suggest that if they are going into defrost in this weather then Grant need to come and see to these units asap
 
Like I said they are only going into De-frost mode due to the fact they have disconnected the outside air temp sensor and replaced it wit a resistor which is ther to fool the controls into thinking it is colder than it is
 
If I were in your position or the customers I would be would getting Grant out everyday until they got the unit working correctly. If Grant claim that the units are working correctly then clearly the unit is not fit for purpose and should be removed and the customer gets their money back and some compensation
 
Most definatley Grant responsability I have on many occasions evaluated underperforming systems as an independant 3rd party and have never yet failed to get a positive result from the manufacturer
 
If I were in your position or the customers I would be would getting Grant out everyday until they got the unit working correctly. If Grant claim that the units are working correctly then clearly the unit is not fit for purpose and should be removed and the customer gets their money back and some compensation

My thoughts Exactly...
 
I agree with Unguided1, get grant out asap and the weather comp being by-passed is a joke
 
Most definatley Grant responsability I have on many occasions evaluated underperforming systems as an independant 3rd party and have never yet failed to get a positive result from the manufacturer

Are you talking about probs with ASHP's if so have you had any dealings with Grant?
 
I agree with Unguided1, get grant out asap and the weather comp being by-passed is a joke

like I said in earlier posts Grant do come to look at it but they can't wait to get back in the van and on the way back home due to the distance they have to travel and when contacted they seem very lax in coming to see them it can take weeks to get them there and when they leave they say they will put together a report on there findings but when we call them back eveyone denies any knowledge of previous visits
 
like I said in earlier posts Grant do come to look at it but they can't wait to get back in the van and on the way back home due to the distance they have to travel and when contacted they seem very lax in coming to see them it can take weeks to get them there and when they leave they say they will put together a report on there findings but when we call them back eveyone denies any knowledge of previous visits

I reckon that if you block their van in they have got stay as long as you do, and If it were my customer I would make sure that I turned up with a sleeping bag, mind you the giant thumb of doom hates it when I refer to her as my sleeping bag!!!!!!!!!!
 
Last edited:
As Unguided says, block their van in or take a photo of them whilst they are looking at the unit. That way they cannot deny any knowledge of the unit/visit.
 
I reckon that if you block their van in they have got stay as long as you do, and If it were my customer I would make sure that I turned up with a sleeping bag, mind you the giant thumb of doom hates it when I refer to her as my sleeping bag!!!!!!!!!!

lol like ur style but u haven't seen the size of the driveway...... might be better to get a wheel clamp....
 
Usually any heat pump that has an immersion fitted is because the manufacturer has optimised the heat pump to comply with EN14511, so that the unit can attain MCS accreditation, and because the unit has been optimised to work at between 6 and 7 degrees c this means that when they work at temperatures below minus ten c they start to fall down hence the back up immersion, so really I would say that in reality it is not fit for purpose especially if these units are doing both heating and hot water
 
Last edited:
yes they are doing both heating and hot water but obviously at the moment only hot water due to the fact that the building is a new build with a very high standard of insulation even down to triple glazing and far and above building regs insulation for walls and ceilings
 
yes they are doing both heating and hot water but obviously at the moment only hot water due to the fact that the building is a new build with a very high standard of insulation even down to triple glazing and far and above building regs insulation for walls and ceilings

so at what temperature are the flow and return temps on the heat pumps
 
lol like ur style but u haven't seen the size of the driveway...... might be better to get a wheel clamp....
I served my time way back when as an electrcian , Then went into refrigeration / HVAC the rest is history and a long one at that
 
I served my time way back when as an electrcian , Then went into refrigeration / HVAC the rest is history and a long one at that

ok cool wel my customer is now watching this thread too so if he gets intouch with me and wants ur contact details i will pm you :)
 
so at what temperature are the flow and return temps on the heat pumps

I can oly tell you what it says on the ATC controller indoors reads mid 40 C but I don't know if thats the output from the ASHP or the return temp....
 
Is this aerona fitted with a BTC controller because it could be that upsetting it all
 
Status
Not open for further replies.

Reply to GRANT Air Source Heat Pumps in the Plumbing Jobs | The Job-board area at PlumbersForums.net

Similar plumbing topics

Hi, Short version: Do frost protection valves trigger when the water in the pipe gets to threshold, or when the air temp drops? Long version...
Replies
3
Views
135
hi everybody i need some help please, i can't remember how to adjust the temperature setting in heat mode on my dream air source heat pump does...
Replies
3
Views
2K
Mike marks
M
C
Do you have some experience with Air Source Heat Pumps and are looking for your next role? Evergreen Energy are hiring for a Commissioning...
Replies
0
Views
785
Cecile
C
    • Like
    • Agree
I'm getting so sick of the media and tories plugging ashp's like they are the solution to all our heating needs. Latest news today, £5k grant...
Replies
70
Views
10K
Would it possible to connect an air source heat pump into 2 UFH (unused) ports on a thermal store? The property is heated by oil and a wood...
Replies
1
Views
1K
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock