Wondering if there are plumbing gurus here who can suggest what could be the issue .Recently changed to gas heating and have a viessmann vitoden 100 , 26 kw condensing boiler .The old oil boiler was a firebird 26 Kw and I have almost already started missing it .

The house is well insulated and has 12 rads /3 zones . I've noticed that the with the thermostats set to 21 deg as before , the rads are lukewarm and dont heat up quickly . The room temp slowly ramps to the set temperature as I can see that the thermostat keeps cutting off frequently .

I've changed the boiler flow temp from the initial setting of 71 deg to 76 and then 78 , but that dosen't seem to have made a big difference.
The only way to heat up to the same temp as before seems to be by setting the thermostat to around 25 , but even with that it seems that the boiler keeps cutting off and when its back on , its not ON for long enough to heat up all the rads .I read the boiler pressure and the boiler pressure is around near the notch near 1 bar .
 

Attachments

  • thumbnail (3).jpg
    thumbnail (3).jpg
    56.2 KB · Views: 51
Do you have a weather compensation sensor?
No , I dont .
Since posting here ive also tried increasing the flow temp to max /80 keeping the room stats at around 25 and the boiler comes on for a little longer for around 2/3 minutes and then cuts off and then starts after a while again .
 
You got a pic further back of the whole boiler and pipe work ?

also pressure wants upping around 1.2 for a cold system
 
Is the bypass set below the boiler and not open ? Should be around 3-4 set level
 
Since posting here ive also tried increasing the flow temp to max /80 keeping the room stats at around 25 and the boiler comes on for a little longer for around 2/3 minutes and then cuts off and then starts after a while again .
From your description, I suspect that your boiler is 'short-cycling' because heat is not being transferred from the boiler to the radiators fast enough. It's a common problem with small zones and/or TRVs and well-insulated houses. IIRC, your boiler's minimum output is 9kW (1:3 turndown) so when the demand from the emitters is low, which it often will be in a well-insulated and zoned house, the boiler will be providing short pulses of 9kW in an attempt to meet the demand.

If my guess is right, and the commissioning was done correctly, the only really satisfactory solution to this problem is to increase the thermal mass of the water in the system, which you're doing to some extent by increasing the water temperature, but which really needs more water. Ideally, you'll have a buffer tank added to the system. If that's a step too far, you'll get a considerable improvement by abandoning separate zones and TRVs so the boiler has all the water in the system to use as a thermal mass. (Use weather compensation and/or a single thermostat controlling the boiler as the main form of control).

The good news is that this is only really a problem in mild weather, once your demand goes up to 9kW the problem will disappear.
 
Last edited:
Is the bypass set below the boiler and not open ? Should be around 3-4 set level
Thanks will have a closer look tomorrow and post
[automerge]1578616832[/automerge]
From your description, I suspect that your boiler is 'short-cycling' because heat is not being transferred from the boiler to the radiators fast enough. It's a common problem with small zones and/or TRVs and well-insulated houses. IIRC, your boiler's minimum output is 9kW (1:3 turndown) so when the demand from the emitters is low, which it often will be in a well-insulated and zoned house, the boiler will be providing short pulses of 9kW in an attempt to meet the demand.

If my guess is right, and the commissioning was done correctly, the only really satisfactory solution to this problem is to increase the thermal mass of the water in the system, which you're doing to some extent by increasing the water temperature, but which really needs more water. Ideally, you'll have a buffer tank added to the system. If that's a step too far, you'll get a considerable improvement by abandoning separate zones and TRVs so the boiler has all the water in the system to use as a thermal mass. (Use weather compensation and/or a single thermostat controlling the boiler as the main form of control).

The good news is that this is only really a problem in mild weather, once your demand goes up to 9kW the problem will disappear.

Thanks for that .
Shouldn't the boiler do the opposite , that is start at 26 KW and then go down to 9 kw when it perceives the demand from the emitters to be low ? The heating coming on in short cycles seems to be the issue here but would you then say that this is a boiler issue rather than anything else .
after all many other houses with even better insulation levels with the same setup as well .
 
Last edited:
Wondering if there are plumbing gurus here who can suggest what could be the issue .Recently changed to gas heating and have a viessmann vitoden 100 , 26 kw condensing boiler .The old oil boiler was a firebird 26 Kw and I have almost already started missing it .

The house is well insulated and has 12 rads /3 zones . I've noticed that the with the thermostats set to 21 deg as before , the rads are lukewarm and dont heat up quickly . The room temp slowly ramps to the set temperature as I can see that the thermostat keeps cutting off frequently .

I've changed the boiler flow temp from the initial setting of 71 deg to 76 and then 78 , but that dosen't seem to have made a big difference.
The only way to heat up to the same temp as before seems to be by setting the thermostat to around 25 , but even with that it seems that the boiler keeps cutting off and when its back on , its not ON for long enough to heat up all the rads .I read the boiler pressure and the boiler pressure is around near the notch near 1 bar .

I agree re your Firebird boiler, I have one for the past15 years and it has never locked on any fault condition, however, we are where we are.
To rule out constant cycling when the rad(s) output is > the boiler min output you might consider the following or at least run with both CH zones and all l/shield+TRVs opened if the boiler/system is already up to temperature, also roomstats turned up fully:
You have 12 rads, don't know their combined output but assume ~ 18kw and total system water contents of say 80 litres., can you switch in the two heating zones (from cold conditions) with all rad lock shield valves & any TRVs fully open, assuming a boiler SP of 70C then the boiler should fire (100%) continuously for ~ 25 to 30 minutes to reach SP temp and should then continue to run continuously in modulating mode at ~ 58% say 15 kw output. If any big deviations from this then you have a problem but you have to start somewhere. Also as mentioned above, check the setting of the ABV just below the boiler, I would suggest shutting it off (index 0.6 0r 6?) initially and if no problems then set it to ~4.
 
Last edited:
Recently changed to gas heating and have a viessmann vitoden 100 , 26 kw condensing boiler .The old oil boiler was a firebird 26 Kw ...
Which type of boiler do you have - combi, system or open vent?

Was a heat-loss calculation carried out before selecting a 26kW boiler (not important if you have a combi)? After all, you do say that the house is well insulated which, presumably, was done after the Firebird was installed. So a smaller boiler would be more likely.
 
Shouldn't the boiler do the opposite , that is start at 26 KW and then go down to 9 kw when it perceives the demand from the emitters to be low?

The behaviour of the boiler is determined by the manufacturer. A typical boiler will ignite at full (or relatively high) power, then modulate down rapidly to a low power and then gradually ramp up the power while monitoring the temperature of the water flowing through the heat exchanger.

The short cycles occur because the boiler shuts down when a thermometer near the heat exchanger (either on the HX itself or in the exiting water) rises about a limit, typically 5°C above the target setpoint.

would you then say that this is a boiler issue rather than anything else .
after all many other houses with even better insulation levels with the same setup as well .

It might be an problem with your boiler, perhaps a parameter set incorrectly during commissioning.

I think, however, it's just physics. If your house requires 0.9kW average to stay at 21°C, and your boiler has a minimum output of 9kW it has to spend 10% of it's time on and 90% off. The heat capacity of the water in the system will change whether that's a duty cycle of 1 minute on and 9 minutes off, or 5 minutes on and 50 minutes off. If the boiler is connected directly to the radiators occupants may notice the pulsing on/off. Some people seem more sensitive to this than others. The problem can be mitigated by means of a 'buffer tank', which smoothes out the temperature fluctuations arising from the on/off action of the boiler.
 
If the heating zones above are run only on their roomstats, then even just running one zone should require a heating demand > the minimum output of the boiler which I think is ~ 6 kw resulting in the boiler running continuously, that is way I suggest using the above methods to see if there is fundamentally something wrong in the set up or whatever. The problem with cycling gas boilers is that the Hx contents of ~ 3 to 4 litres have really no thermal buffering whereas a oil fired boiler has Hx contents of ~ 25 litres plus they have 4 hefty steel baffles which run practically red hot and will further add to the thermal buffering when the boiler is off, for example with a 4 kw heat demand an oil fired boiler (with 10 deg hysteresis) will stay off for at least 4 to 5 minutes before cutting back in whereas a gas boiler will fall by this 10 deg in only 42 secs which leads to very very rapid cycling and if/with a anti fast cycle time of 3 to 5 minutes will result in a very cold flow temperature to the rads before firing up again.
 
I agree re your Firebird boiler, I have one for the past15 years and it has never locked on any fault condition, however, we are where we are.
To rule out constant cycling when the rad(s) output is > the boiler min output you might consider the following or at least run with both CH zones and all l/shield+TRVs opened if the boiler/system is already up to temperature, also roomstats turned up fully:
You have 12 rads, don't know their combined output but assume ~ 18kw and total system water contents of say 80 litres., can you switch in the two heating zones (from cold conditions) with all rad lock shield valves & any TRVs fully open, assuming a boiler SP of 70C then the boiler should fire (100%) continuously for ~ 25 to 30 minutes to reach SP temp and should then continue to run continuously in modulating mode at ~ 58% say 15 kw output. If any big deviations from this then you have a problem but you have to start somewhere. Also as mentioned above, check the setting of the ABV just below the boiler, I would suggest shutting it off (index 0.6 0r 6?) initially and if no problems then set it to ~4.
The test with the heating on to max with HW on as well was done by the Viessmann installer after commissioning.With the heating cranked up , the boiler didnt cut off and the radiators .I have only noticed the problem now that we have started using it at normal room temperatures of 21 or so and the short cycling issue mentioned above . I might do the test again to check the length of time it stays on .
Meanwhile on the boiler the ABV seems to be set to 5 .
[automerge]1578659265[/automerge]
Which type of boiler do you have - combi, system or open vent?

Was a heat-loss calculation carried out before selecting a 26kW boiler (not important if you have a combi)? After all, you do say that the house is well insulated which, presumably, was done after the Firebird was installed. So a smaller boiler would be more likely.
Yes house was well insulated after the firebird was installed .Its a 26 KW system boiler .Rads were sized up and replaced with new as I had the house replumbed 3 years back during a major refurbishment and removed all old GB pipes as well
( Only replaced the firebird as we wanted to get rid of the huge oil tank in a small back garden)
 

Attachments

  • thumbnail (4).jpg
    thumbnail (4).jpg
    95 KB · Views: 18
Last edited:
Try doing the opposite, open up the TRV's (assuming you have them), set a lower flow temp hopefully that will allow the boiler to fire for a longer periods.
 
was system cleaned i had one a couple of years ago that struggled as wasnt getting the required differential between flow and return this was caused by new alpha pump and also still some sludge in system even though had cleaned
 
was system cleaned i had one a couple of years ago that struggled as wasnt getting the required differential between flow and return this was caused by new alpha pump and also still some sludge in system even though had cleaned
Yes the system was power flushed and inhibitors added . The system was actually quite clean as they found during the power flush cycle .
 
If its a systems boiler I think it will have a 7M Grundfos circ pump set on speed 3 which should provide plenty of circulation, obviously if problems then the boiler delaT will be excessive with constant cycling, but that will bescome fairly evident if boiler cycles with both zones on?.
There has to be some starting point for trouble shooting the problem otherwise we will be talking about it until the cows come home.

Just saw post# 17 there now but yes, no harm to repeat those tests. ABV setting should be OK at 5.
 
Last edited:
... really needs more water. Ideally, you'll have a buffer tank added to the system.

If the boiler is connected directly to the radiators occupants may notice the pulsing on/off. Some people seem more sensitive to this than others. The problem can be mitigated by means of a 'buffer tank', which smoothes out the temperature fluctuations arising from the on/off action of the boiler.

+1 for the suggestion to buffer the heating system.

My heating suffers from this problem. There is just not enough thermal mass in modern rads/piping/boilers to be able to connect the boiler directly to the rads. TRVs make the problem worse. Modulation can definitely help, but IMHO it is a bit of a kludge.
 
Weather comp sensor automatically adjusts the rating and temp so you will get it running constantly
 
IIRC, your boiler's minimum output is 9kW (1:3 turndown) so when the demand from the emitters is low, which it often will be in a well-insulated and zoned house, the boiler will be providing short pulses of 9kW in an attempt to meet the demand.
The installation manual says that the minimum output is 4.3kW @ 80/60C or 4.7kW @ 50/30C. If the house really needs 26kW for heating then the boiler will only go into on/off mode when the outside temperature is about 17C.

I suspect that the boiler output was based on what was there originally, not on the heat loss.
 
Weather comp sensor automatically adjusts the rating and temp so you will get it running constantly

That isn't much help on a 16C day when all you have is 3:1 and you need 20:1.
 
That isn't much help on a 16C day when all you have is 3:1 and you need 20:1.

install a 200 will modulate down to 17:1 or if you can get an older one 20:1
 
I agree re your Firebird boiler, I have one for the past15 years and it has never locked on any fault condition, however, we are where we are.
To rule out constant cycling when the rad(s) output is > the boiler min output you might consider the following or at least run with both CH zones and all l/shield+TRVs opened if the boiler/system is already up to temperature, also roomstats turned up fully:
You have 12 rads, don't know their combined output but assume ~ 18kw and total system water contents of say 80 litres., can you switch in the two heating zones (from cold conditions) with all rad lock shield valves & any TRVs fully open, assuming a boiler SP of 70C then the boiler should fire (100%) continuously for ~ 25 to 30 minutes to reach SP temp and should then continue to run continuously in modulating mode at ~ 58% say 15 kw output. If any big deviations from this then you have a problem but you have to start somewhere. Also as mentioned above, check the setting of the ABV just below the boiler, I would suggest shutting it off (index 0.6 0r 6?) initially and if no problems then set it to ~4.

--> (Current) BF 75 , room temp~21.x ,Boiler cuts off at around 2.4 mins and starts after 3 mins
--> BF75, HW ~60, room temp ~18 with rads cold room stats - 25 - Boiler cuts off at around 8 mins .
--> BF 75 ,HW ~60 ( unchanged), room stats - 35 ( max ) , HW ON - Boiler cuts off around 35 minutes ,All rads heat up to uniformly to around 65 . all TRV's fully opened

Also tried with BF reduced to 65 and no change in the short cycling i,e 2 mins .
 
install a 200 will modulate down to 17:1 or if you can get an older one 20:1

I agree it is possible to fight this problem with technology. Maybe they will develop the "infinitely modulating boiler" that is permanently on at whatever percentage is required for the demand. However, one has to question the expense/complexity/robustness of that solution, when a simple tank of water can solve the problem.
 
I agree it is possible to fight this problem with technology. Maybe they will develop the "infinitely modulating boiler" that is permanently on at whatever percentage is required for the demand. However, one has to question the expense/complexity/robustness of that solution, when a simple tank of water can solve the problem.

surely 1.9kw is enough it’s like two rads ?

ok so why not do this

viessmann 200 combi with a buffer vessel and weather comp

you will be more efficient than your set up and have your rads acceptable to you ?
 
surely 1.9kw is enough it’s like two rads ?

Two rads on a very cold day. It is a very good question how low the "infinitely modulating boiler" would need to go to completely eliminate cycling in a small energy efficient house. My guess would be less than .5kW.
 
--> (Current) BF 75 , room temp~21.x ,Boiler cuts off at around 2.4 mins and starts after 3 mins
--> BF75, HW ~60, room temp ~18 with rads cold room stats - 25 - Boiler cuts off at around 8 mins .
--> BF 75 ,HW ~60 ( unchanged), room stats - 35 ( max ) , HW ON - Boiler cuts off around 35 minutes ,All rads heat up to uniformly to around 65 . all TRV's fully opened

Also tried with BF reduced to 65 and no change in the short cycling i,e 2 mins .

something isn’t right sorry to say time to get the installers back
[automerge]1578685049[/automerge]
Two rads on a very cold day. It is a very good question how low the "infinitely modulating boiler" would need to go to completely eliminate cycling in a small energy efficient house. My guess would be less than .5kW.

weather comp would adjust the temp to suite
 
If manufacturers offered boilers with high modulation ratios then IMO this would cover most demands without the added expense of a buffered system, manufacturers like Vokera offered 10:1 modulation years ago I think, if you had a heat only boiler with a heat requirement of say 15kw then a 10:1 ratio will give a minimum output of 1.5 kw, some manufacturers as well basically fit the same burner to a range of boilers to keep manufacturing costs down and because the minimum output is governed by the burner size/characteristics then one might only get a effective modulation ratio of say 3:1 at the lower lower end of their power range but a effective modulation ratio of say 6:1 at the higher end of their power range. Combi boilers present a bigger challenge as the HW demand can be well over twice the CH demand and buffering may be the only realistic solution here but sort of defeats the purpose of the combi. I know two people who changed from oil to gas who found it very hard to understand/accept that their constantly cycling oil boiler gave better temperature control than their new gas boiler, at very low heat demands.
Having said that it does seem that some makes of gas boilers can perform better than other makes when cycling, all seem to perform fine as long as operating in their modulation range.
[automerge]1578687456[/automerge]
--> (Current) BF 75 , room temp~21.x ,Boiler cuts off at around 2.4 mins and starts after 3 mins
--> BF75, HW ~60, room temp ~18 with rads cold room stats - 25 - Boiler cuts off at around 8 mins .
--> BF 75 ,HW ~60 ( unchanged), room stats - 35 ( max ) , HW ON - Boiler cuts off around 35 minutes ,All rads heat up to uniformly to around 65 . all TRV's fully opened

Also tried with BF reduced to 65 and no change in the short cycling i,e 2 mins .

Your first "bullet" point: is your room temperature at its SP temperature, with cycling?
Point2 & 3 seem to be stating that with the room stats at 25C that the boiler only runs for 8 minutes and with the room stats at 35C that the boiler runs for 35 minutes, this is very strange if one assumes that the room stat hasn't been satisfied in either case.

Excuse my ignorance, but I assume BF75 refers to the boiler flow temperature and HW60 refers to the hot water cylinder stat SP?
 
Last edited:
If manufacturers offered boilers with high modulation ratios then IMO this would cover most demands without the added expense of a buffered system, manufacturers like Vokera offered 10:1 modulation years ago I think, if you had a heat only boiler with a heat requirement of say 15kw then a 10:1 ratio will give a minimum output of 1.5 kw, some manufacturers as well basically fit the same burner to a range of boilers to keep manufacturing costs down and because the minimum output is governed by the burner size/characteristics then one might only get a effective modulation ratio of say 3:1 at the lower lower end of their power range but a effective modulation ratio of say 6:1 at the higher end of their power range. Combi boilers present a bigger challenge as the HW demand can be well over twice the CH demand and buffering may be the only realistic solution here but sort of defeats the purpose of the combi. I know two people who changed from oil to gas who found it very hard to understand/accept that their constantly cycling oil boiler gave better temperature control than their new gas boiler, at very low heat demands.
Having said that it does seem that some makes of gas boilers can perform better than other makes when cycling, all seem to perform fine as long as operating in their modulation range.
[automerge]1578687456[/automerge]

Your first "bullet" point: is your room temperature at its SP temperature, with cycling?
Point2 & 3 seem to be stating that with the room stats at 25C that the boiler only runs for 8 minutes and with the room stats at 35C that the boiler runs for 35 minutes, this is very strange if one assumes that the room stat hasn't been satisfied in either case.

Excuse my ignorance, but I assume BF75 refers to the boiler flow temperature and HW60 refers to the hot water cylinder stat SP?

Yes thats correct .

The boiler is normally cutting off in cycles of 2.5 mins when the room temp is set anywhere between 21 and 25 . However as suggested when I ran the heating from completely cold , I did notice that the boiler cut off was much longer that is around 8 minutes both upstairs and downstairs .
If manufacturers offered boilers with high modulation ratios then IMO this would cover most demands without the added expense of a buffered system, manufacturers like Vokera offered 10:1 modulation years ago I think, if you had a heat only boiler with a heat requirement of say 15kw then a 10:1 ratio will give a minimum output of 1.5 kw, some manufacturers as well basically fit the same burner to a range of boilers to keep manufacturing costs down and because the minimum output is governed by the burner size/characteristics then one might only get a effective modulation ratio of say 3:1 at the lower lower end of their power range but a effective modulation ratio of say 6:1 at the higher end of their power range. Combi boilers present a bigger challenge as the HW demand can be well over twice the CH demand and buffering may be the only realistic solution here but sort of defeats the purpose of the combi. I know two people who changed from oil to gas who found it very hard to understand/accept that their constantly cycling oil boiler gave better temperature control than their new gas boiler, at very low heat demands.
Having said that it does seem that some makes of gas boilers can perform better than other makes when cycling, all seem to perform fine as long as operating in their modulation range.
[automerge]1578687456[/automerge]


Your first "bullet" point: is your room temperature at its SP temperature, with cycling?
Point2 & 3 seem to be stating that with the room stats at 25C that the boiler only runs for 8 minutes and with the room stats at 35C that the boiler runs for 35 minutes, this is very strange if one assumes that the room stat hasn't been satisfied in either case.

Excuse my ignorance, but I assume BF75 refers to the boiler flow temperature and HW60 refers to the hot water cylinder stat SP?
If manufacturers offered boilers with high modulation ratios then IMO this would cover most demands without the added expense of a buffered system, manufacturers like Vokera offered 10:1 modulation years ago I think, if you had a heat only boiler with a heat requirement of say 15kw then a 10:1 ratio will give a minimum output of 1.5 kw, some manufacturers as well basically fit the same burner to a range of boilers to keep manufacturing costs down and because the minimum output is governed by the burner size/characteristics then one might only get a effective modulation ratio of say 3:1 at the lower lower end of their power range but a effective modulation ratio of say 6:1 at the higher end of their power range. Combi boilers present a bigger challenge as the HW demand can be well over twice the CH demand and buffering may be the only realistic solution here but sort of defeats the purpose of the combi. I know two people who changed from oil to gas who found it very hard to understand/accept that their constantly cycling oil boiler gave better temperature control than their new gas boiler, at very low heat demands.
Having said that it does seem that some makes of gas boilers can perform better than other makes when cycling, all seem to perform fine as long as operating in their modulation range.
[automerge]1578687456[/automerge]


Your first "bullet" point: is your room temperature at its SP temperature, with cycling?
Point2 & 3 seem to be stating that with the room stats at 25C that the boiler only runs for 8 minutes and with the room stats at 35C that the boiler runs for 35 minutes, this is very strange if one assumes that the room stat hasn't been satisfied in either case.

Excuse my ignorance, but I assume BF75 refers to the boiler flow temperature and HW60 refers to the hot water cylinder stat SP?
Sorry that I am typing my response all in one go as I am logged in with a device with a rather small screen at the moment and cant seem to get the multi quote working .

.The boiler is normally cutting off in cycles of 2.5 mins when the room temp is set anywhere between 21 and 25 . However as suggested when I ran the heating from completely cold , I did notice that the boiler cut off was much longer i,e around 8 minutes both upstairs and downstairs .
When the SP temp was 25 , I did measure with an infrared thermometer the temp on the wall facing the upstairs thermostat and it was 25.7 ( the thermostat is on a stairway directly facing the radiator on the stairs (bad design)) .

I really dont know why the boiler cuts off when the SP is set to max as with the old OFCH the heating would have gone on till eternity .

Yes the BF is the boiler flow temp
 
The sad fact is these issues are not about TRV’s , weather compensation, boiler modulation or smart controls ( most of which are excellent). The issue is that the system has been installed without being properly designed - or in some cases not designed at all.

With the extensive variety of products ( both boilers and control systems) on the market, there is no excuse for “getting it wrong”.

I will await the onslaught!
 

Reply to Viessmann boiler question in the Central Heating Forum area at PlumbersForums.net

Similar plumbing topics

Every two weeks or so I have to go and top up the system because the hot taps are running cold. Boiler display is flashing 0.6 bar and I fill up to 1.3. I've had an engineer look inside the boiler and he can't see anything wrong. I've checked the pipes all over the house and cannot see any...
Replies
2
Views
204
P
  • Question
Ideal Logic 24, Previous problem was that the hot water was only cold or barely warm if the heating was in use. If heating was off and boiler cold then would get hot water most of the time. Changing the flow cartridge about 2 years ago (when I moved in) solved this problem enough to suffer it as...
Replies
2
Views
139
Hello, I am seeking some advice, I have a POTTERTON PROMAX 28 COMBI Boiler and I noticed yesterday that the water around the house is no longer warming up. The heat exchanger has been changed 6 months ago, so I do not believe it is that. Does anyone have any ideas on what it could be? Thanks
Replies
4
Views
232
Hi everyone, Looking for a bit of advice, recently went to a job where heating was operating when called for however not for the hot water. I have changed the 3 port actuator Honeywell head however this doesn’t seem to have solved the issue, does this mean that the programmer is faulty? Or is...
Replies
8
Views
292
Creating content since 2001. Untold Media.

Newest Plumbing Threads

Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock