Vailant ecotec system boiler. Drayton Lifestyle controller

Hi. Yesterday I turned on my central heating. After turning it at the controller off I noticed it was still running. The hot water was set to 'timer' (but wasn't on at that time) When I turned the hot water to 'off' the boiler stopped & the central heating went off. I turned the HW back on to 'Timer'. This morning, when the HW was running during its timed programme, the rads got hot.

Could anyone point me in the direction of the possible cause for this? I'm thinking sticking zone valve at the HW cylinder but really have no idea. Could it be this, or an issue with the Drayton controller?

Thanks in advance for any replies.
 
Sticking 2 port or misbehaving 3 port.

2 port either sticking or micro switch in head stuck closed.

Thanks for that. The black manual switch on the body of the actuator is 'floppy' (no resistance) I read somewhere that this indicates the unit is stuck in mid position, supplying both HW & CH at the same time. Is this correct? I've attached a photo for reference
PB100004.JPG


Mm, it seems the photo hasn't loaded? The unit is a Drayton mid position actuator MA1
 

Reply to Central heating issue in the Australia area at PlumbersForums.net

Similar plumbing topics

Hi, I have a Worcester 28i junior boiler that has started to lose pressure, only when using the central heating. When using hot water I have no issue, however, when running the heating the pressure drops. Im looking for some ideas on what could be causing this. I have no sign of pipe leaks...
Replies
6
Views
208
  • Question
Ideal Logic 24, Previous problem was that the hot water was only cold or barely warm if the heating was in use. If heating was off and boiler cold then would get hot water most of the time. Changing the flow cartridge about 2 years ago (when I moved in) solved this problem enough to suffer it as...
Replies
2
Views
155
Hi everyone, Looking for a bit of advice, recently went to a job where heating was operating when called for however not for the hot water. I have changed the 3 port actuator Honeywell head however this doesn’t seem to have solved the issue, does this mean that the programmer is faulty? Or is...
Replies
8
Views
319
Every two weeks or so I have to go and top up the system because the hot taps are running cold. Boiler display is flashing 0.6 bar and I fill up to 1.3. I've had an engineer look inside the boiler and he can't see anything wrong. I've checked the pipes all over the house and cannot see any...
Replies
2
Views
235
P
Hi, Later this year I am going away for a 2 week holiday and as the weather will be warm there is no need for the heating to be on and arguably no need for me to needlessly heat hot water. My intention was to turn the boiler off along with the mains water when going away. Now, I have heard...
Replies
1
Views
117
Creating content since 2001. Untold Media.

Newest Plumbing Threads

Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock