Discuss Honeywell 3 port diverter snag? in the Plumbing Jobs | The Job-board area at PlumbersForums.net

If the valve is sticking causing your problem of both CH and HW on at same time then there’s only so much you can do to prolong its life. Like I mentioned above as well with this particular design of valve the synchronous motor is likely to burn out over time leading to nuisance replacements. You’re best bet is to save time and money and replace the whole valve, be it you or an engineer. I personally don’t like these valves because of the problems we’ve mentioned, I always preferred an S plan but again they fail over time as well
 
this particular design of valve the synchronous motor is likely to burn out over time leading to nuisance replacements.
The motor is designed to be permanently stalled. The motor is fed through resistors & a diode and my last valve failed because one of them had failed. I didn't realise that was the problem until after I had changed it to an S plan. Now have changed it back to Y on boiler mfrs recommendation to avoid need for bypass. If the spindle turns easily you don't need to replace the entire valve, just the motor or head. There should never be a long term demand for heat or HW.
 
What I meant John is if CH was last port of call then the motor will burn out over time. I know how the valve is held in mid position if you read one of my above comments. Am I wrong?
 
When the CH is satisfied the valve should move back to midpos and then be held there by the rectified pulses. However, if there is a demand for HW it will unpower and spring would take it to HW.
 
97AEDB08-7437-4684-8E3D-EC30775D24C4.png
This suggests to me that it’s last port of call is held and it doesn’t return to mid position. If I’m wrong then I’ve been wrong for years lol
 
Though this might be useful for diagnostics: I removed the powerhead then turned the supply back on (yes I put the cover back on the first!) Then turned on the CH/HW.

I can move the valve manually and I can hear it kicking over, so I’m guessing the valve is fine.

The powerhead isn’t behaving as it should, though I did wonder if that was because it isn’t physically attached to the valve?

My money is on a duff powerhead. What do you guys think?
 
If you have bought the whole valve I would keep the brass bit as the other one definitely sounded like it wasn’t moving that freely
 
If you have bought the whole valve I would keep the brass bit as the other one definitely sounded like it wasn’t moving that freely

Sure
And in the meantime it’s going to be perfect for lobbing at that cat that keeps coming to take a s**t on my lawn. :rolleyes:
 
Last edited:

Reply to Honeywell 3 port diverter snag? in the Plumbing Jobs | The Job-board area at PlumbersForums.net

Similar plumbing topics

Hi,

 Our heating stopped working today. We've got a Veissmann boiler that's under a year old, and an older Megaflow cylinder, and two diverter...
Replies
1
Views
707
Hi I have a duff Honeywell 3 Port Diverter Valve Actuator V4073A, my mate has a new Honeywell V4043, would anyone know if they are...
Replies
6
Views
1K
My 3 way actuator valve has gone on my central heating. I think it's a combination of the valve motor burning out due to a stiff valve on the...
Replies
1
Views
1K
Hi experts, i'm looking for some advice to get to the bottom of my boiler problem. The boiler is a Glowworm Ultimate 40FF so a traditional NOT...
Replies
5
Views
1K
Please can someone advise, just had a two port valve head installed. When I turn heating and hot water on the valve lever automatically goes to...
Replies
9
Views
1K
Deleted member 120897
D
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock