Hi Guys, i come on here a broken man LOL

Ive got a 4 yr old Vaillant EcotecPlus 831 combi boiler that over the last 2 months has been overpressurising when the Rads are on and has got worse now to the point it maxes out the pressure to 3.5 Bar the PRV opens, lowers the pressure to about 3.1 Bar, the rads still operate etc, but then, when the CH is off the pressure drops to 0 Bar but i cant find any leaks in the system !!!!!!

What i have tried so far....

When Cold, i set the pressure via the filling loop to 0.6 Bar, when CH is on, still maxes out to 3.5 then drops to 0 when cold
I have bled the rads in case any air in them, none present
I used a footpump and re-charged the expansion vessel, i put about 0.5bar into it, i used the digital gauge to see how much each pump of air from the footpump increased the vessell, still no change with the problem

So, any ideas guys ???

Cheers
 
Cheers bud, will check for that

i just want to double check im re-charging the Expansion vessel correctly (probably not LOL) my dial gauge and digital gauge built into the boiler read 0, so i pump the vessell upto about 0.7 Bar, but when i do this, the pressure gauge and the digital gauge increase and read 0.7 bar (digitally) and just under 1 on the analogue gauge, now should this happen ? i thought the expansion vessel should be charged up but not affect the pressure of the readings ?!! As when i charge the vessel up i dont need to use the filling loop to increase the pressure as its already reading 0.7 bar etc ?!?!?!

Even tho my readings are 0 on the dials of the boiler when i begin, should i be bleeding out a litre of water from the radiators to remove all water from the vessell ?

cheers again

dean
 
Agreed.

You need a gsr in to look at your boiler. We cannot and will not give advice on the installation or repair of boilers for your own safety.

Please go to Gas Safe Register | Ensure your gas engineer is registered. or post a thread in the 'I'm looking for a plumber / gas engineer' section of these forums remembering to include your location. [DLMURL="http://www.ukplumbersforums.co.uk/im-looking-plumber-gas-engineer/"]I'm looking for a Plumber or Gas Engineer[/DLMURL]

If you are gsr please increase your post count to 10+ then send a pm to either Gas man or Redsaw who will then check you and then give you access to the gsr private forum.

Thank you.

http://www.ukplumbersforums.co.uk/central-heating-forum/42241-notice-gas-safety-related-advice.html
 
Status
Not open for further replies.

Reply to Vaillant EcoTecPlus Overpressurising Only when in Use in the Plumbing Jobs | The Job-board area at PlumbersForums.net

Similar plumbing topics

  • Question
Ideal Logic 24, Previous problem was that the hot water was only cold or barely warm if the heating was in use. If heating was off and boiler cold...
Replies
2
Views
221
I have an ideal vogue max S18 boiler and I’m considering fitting auto balancing TRVs, my question relates to the boilers pump. I see a boiler...
Replies
1
Views
192
Hi, Can anyone advise as to why the cold water to my bathroom keeps airlocking? This originally happened about 12 months ago and has happened 3-4...
Replies
9
Views
459
Hello, I am seeking some advice, I have a POTTERTON PROMAX 28 COMBI Boiler and I noticed yesterday that the water around the house is no longer...
Replies
4
Views
290
We are from Alberta, and I own an electrical company. I have been asked by a BC Mechanical P. Eng. to install an emergency STOP button at the...
Replies
5
Views
325
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock