Hi all,

New here to the forum.

Got a slight problem with my UFH. Have 3 valves, DHW, Rads and UFH.

Rads and DHW work fine using the programmers, switch on and off and heat up no problem.

However whenever the UFH is calling for heat, the flow pipe at the manifold barely gets warm. Its a 4 zone system, actuators open up circuit when fired, boiler fires up. Zone value is open for UFH. The flow pipe at the boiler gets hot, but it seems by the time it gets to the UFH manifold, barely any heat is getting to the UFH flow pipe.

The run is quite a bit, but have left on the whole day, and still no heat.

Boiler is a vaillant 630 ecotec plus. I noticed that unlike when DHW or the rads are calling for heat, the boiler does not stay on constantly, as in fired up. Keeps displaying the eggtimer and on live monitor, shows pump overrun sometimes.

Assuming the reason the UFH flow pipe at manifold is not heating up is that boiler for some reason is turning itself off even though constant demand for heat is there. Wiring center at manifold shows Boiler, Value and Pump lights on. At the megaflo wiring centre, when UFH is calling for heat, switch live active and so telling boiler to come on. So I don't believe it is a wiring problem.

No air at UFH manifold, rads and HW aired too. Pump at UFH manifold is on and pulling, can be heard.

Any ideas why boiler is not staying on for long enough to get the temperature up?
 
Last edited by a moderator:
New / Old System?
Worked until this heating season?
Never Worked?
Does the UFH system have a blending / mixing valve and it's own circulation pump?
Circulation pump built into boiler or seperate?
Have you tried turning rads and dhw off, and only calling for heat on the ufh?
as above, manually opening the valve?
Need more info...
 
Last edited:
Is it in a screed floor.?

Don't expect it to warm the room that fast. May take two days to get the room up to temp
 
Sounds like poor circulation, is the underfloor heating pump running?
 
It sounds like the ufh circuit when calling is very short do not taking long to heat, either that or valve isn't opening allowing the water through and just going round the bypass, this would explain the short burst if boiler operation, is there a separate pump on the ufh manifold along with mixing valve and is the pump coming on??
 
Thanks for the replies lads.

Some answers to the questions.

It's a new system.
UFH system has its own mixing valve and pump.
System boiler, so pump built in boiler.
Rads and dhw off, call for UFH heat and boiler comes on.
Have tried manually opening value, still no difference.
Is a screeded floor.
UFH pump comes on, can hear it humming away, and pump light on heatmeiser UH3 wiring comes on.

If I try with rads on and UFH on, the flow pipe after the rads zone valve is piping hot. Cannot touch for more than a few seconds.
Try the same on the UFH flow pipe and its only warm, I can confortably keep my hand on there without having to pull off unlike the rads.

The UFH pump at the manifold light is illuminated, so defo is on and can hear it humming, plus have it set to max.
Turned all 4 zones on to call for heatt, Emmetti acctuators open up. Confirmed via the little black plastic that slowly rises up when open.

Have just tried again and seems the flow pipe just doesnt seem to heat up enough so no chance of heat reaching the manifold at this rate..?
 
have you tried turning all zones on to heat and see?
 
Hey Shaun,

Just tried that now. And seems now the heat is coming through. 35 degree on temp gauge up from 20 before. Although UFH pump is no longer making a low humming sound and is quite loud. Maybe air was trap in the system? Hopefully should quieten down and its pretty loud at the moment, can hear from upstairs landing.
 
Hey Shaun,

Just tried that now. And seems now the heat is coming through. 35 degree on temp gauge up from 20 before. Although UFH pump is no longer making a low humming sound and is quite loud. Maybe air was trap in the system? Hopefully should quieten down and its pretty loud at the moment, can hear from upstairs landing.

either that or wired wrong, turn one zone off until the pump turns off note the pump may over run for 10 - 15 mins so after you turn one zone off wait a good 30 mins before turning another one off

repeat until pump turns off and if doesnt turn off when you turn your ufh control/stat off then its wired to the wrong zone

hope you understand if not please ask
 
OK got you. I'll give that a try tomorrow. In the mean time I'll leave the system running.

Although still not sure it's functioning correctly. Gauge on manifold was showing up to 40 degrees at one point, but has since dropped back to 25 degree. The flow pipe at the manifold is warm only now.

I've been up to the boiler and monitoring the live info, and it seems like its only igniting for a really short time, sometimes only a minute or so, then it goes to "Pump Overrun" then "Anti cycling" then "Pre pump run" etc. I'm expecting it to be on ignition and pump hot water to the manifold for a lot longer time.

Especially considering everything is still stone cold. Non of the individual pipe for each heating circuit are anything close to hot. Got slightly warm at one point, but not anymore, has lost heat. Shall I leave running overnight and see how it's looking in the morning? Or is there anything else I can try?
 
you can do (leave it over night ) see what happens might have some air stuck like you said
 
Can you take a picture of the manifold please. There maybe son thing obvious.
 
Are the flow and Return pipes to the manifold buried anywhere along the route?

Is there an Auto air bleed at the manifold?
 
IMG_20151220_231517.jpg

Here you go,
 
Are the flow and Return pipes to the manifold buried anywhere along the route?

Is there an Auto air bleed at the manifold?

Hi Snowhead. Yes there is about a 1.5 meter run where they are buried along the route to manifold. They have been lagged in pipe insulation for that run.

Yup there is an auto air bleed at the manifold too.
 
That's all correct. But no flow through any of the zones!
Two initial things to try.
1. Take off one of the White heads ( unscrew from manifold) make sure system us calling for heat. Then see if the flow starts. ( look at flow meter on the top)
2. Take off the red clip below the flow meter ( pull straight up) then unscrew ( anticlockwise) the flow restrictor. Again see if any flow.

After that look on you tube on how to bleed air from underfloor heating.

If this does not work and the pump on the manifold is operating.You would be best calling out an engineer to sort.
 
Another quick question. When was it installed and has it ever worked?
 
Thanks Chalked. Ill give those things a try tomorrow. It was only installed recently and has not worked. The system was filled with a hose pipe, each loop run through until air had been cleared.

Anyways I'll check those again and if still no luck will call in engineer.

Cheers.
 
It was only installed recently and has not worked.

In which case whoever installed the controls and piped it up to the boiler should come and sort it out...

With such a small ufh system and that fact that it should run (flow) at 35 - 40° max, then you are in danger of short cycling the boiler anyway.
 
In which case whoever installed the controls and piped it up to the boiler should come and sort it out...

With such a small ufh system and that fact that it should run (flow) at 35 - 40° max, then you are in danger of short cycling the boiler anyway.

OK, thanks. Looks like short cycling is what it is doing. Are there solutions to such problems?
 
OK, thanks. Looks like short cycling is what it is doing. Are there solutions to such problems?

get the installer back
 
On a new system #1 get your installer back

An emmeti system and heatmiser controls is a good set up, the only reason it's not working is something wrong with the installation.

Noise is usually caused by three items:
Air
Unclipped pipes
Excessive pressure form multiple circulators (pumps)

Low or no flow is caused by:
Incorrectly set up flow regulators (they should ONLY be set up after they have been left fully open for a while to allow the system to stabilise - we usually do it 1 - 2 weeks after we've started to put heat into the system.
Blocked Pipes
Air Lock / air in the system - it can take up to 20 mins per loop to get all the air out.
Actuators not opening
Actuators connected to the wrong zone controller :)
TMV incorrectly set.

The solution for short cycling is a buffer tank. If you have enough radiators, then the water in that circuit can act as the buffer, in conjunction with the radiator circuit, sometimes an auto bypass is all that's needed.

The problem is that the return from an ufh heating system to the boiler can be:
a) lower temperature than radiators
b) lower flow rate than the boiler wants
Hence any system with ufh needs designing and installing correctly.

Done properly they are the best heating system you can have.

You may also need an auto bypass installing for the boiler circulator (pump), it may be that with no call for heat elsewhere, when only the ufh is calling for heat the main boiler circulator is over pressurising the ufh pump and that will make it noisy. An auto bypass will also help solve a) and b) above.

Don't do any of this yourself - Your installer should have sorted all this, get them back, don't stand for any truck about it being christmass
 
Last edited:
You have a flow fault between the boiler and ufh manifold , not the ufh loops. Suggested problems are.....

Physical Blockage in flow/ return pipes, valve turned off or debris.
Zone valve not opening gate
isolation valve on manifold not truly open, although inline handle says so. ( it can happen)
Pipe work seriously undersized in screed

System needs draining down and physically testing for clearance/ flow
 
Thanks a lot guys. Appreciated.

Bit more clued up now for when I get the installer back.
 
Status
Not open for further replies.

Reply to UFH on S plan plus not getting up to temperature in the Plumbing Jobs | The Job-board area at PlumbersForums.net

Similar plumbing topics

  • Question
Ideal Logic 24, Previous problem was that the hot water was only cold or barely warm if the heating was in use. If heating was off and boiler cold...
Replies
2
Views
232
Hi, Can anyone advise as to why the cold water to my bathroom keeps airlocking? This originally happened about 12 months ago and has happened 3-4...
Replies
9
Views
477
We run a community village hall and have a large kitchen provided for the use of hirers. This includes a Lincat SLR9 gas cooker which I believe is...
Replies
5
Views
564
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock