I have a customers trianco burner that starts from cold ok for a few minutes (say 3minutes) then locks out then will not stay on.

Boiler had not been serviced in a long time and oil filters were bunged up as was the nozzle.

I decided to service it with hopes it was simple starving of fuel from dirt

I left fuel pressure gauge on at startup to see how things went.

Again about 3 or 4 minutes later it locked out again. 😭

The fuel pressure remained good.
I happened to have a control box and photocell to hand and this made no difference. I also tested lead going to it.

I was pushed for time and customer lives out in sticks so decided to take burner with me to test on bench.

Having looked at flame and ignition it seems that it's a fuel cut out caused by either the solenoid or pump valve. (Oil pressure remains good till after lockout)

When it tries to start again it sparks good but no fuel coming through.

It's just strange to me that every time I try from cold it behaves for a while. Once it cuts out after warming up you cannot get it going again until left for some time.

Any thoughts guys?
Really appreciate any help at all

Thank you
 

Reply to Trianco burner locking out in the Central Heating Forum area at PlumbersForums.net

Similar plumbing topics

  • Question
Ideal Logic 24, Previous problem was that the hot water was only cold or barely warm if the heating was in use. If heating was off and boiler cold...
Replies
2
Views
205
I have a green star ten yrs old keeps increasing pressure, feel on off filling valve not working, drain off to recommended, but after few days...
Replies
1
Views
190
Hi, Can anyone advise as to why the cold water to my bathroom keeps airlocking? This originally happened about 12 months ago and has happened 3-4...
Replies
9
Views
426
Every two weeks or so I have to go and top up the system because the hot taps are running cold. Boiler display is flashing 0.6 bar and I fill up...
Replies
2
Views
272
PSxxxxxx
P
Hi all Noticed bad smell in my drain out side put my hand down and it unclogged it for now however I checked my sewer drain and after flushing my...
Replies
3
Views
566
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock