Ok folks. Would appreciate more experienced eyes looking at this to see if I have missed anything important: -
2x 35KW Viessman System Boilers connecting into a 35mm primary flow/return to the LLH. Boilers connected in reverse return configuration. 22mm magnetic filters fitted to return pipework to both boilers. Obviously being system boilers they will have their own pumps in there to push water to LLH.
LLH, 67mm diameter, height to suit so that there is a gap of 400mm min. between each flow and return. Flows at the top, returns at the bottom. Drain cock on bottom of LLH, air vent on top.
Outputs from LLH - 22mm hot water flow and return, pumped from a normal domestic CH circulating pump.
CH flow/return risers - 35mm initially dropping to 28 then 22mm as it tees off to each floor. Total of 6 CH zones each under 100m2, one of these is a 35m2 underfloor heating circuit in the kitchen by the plant room. CH circuit pumped by a 10m head pump which switches on with the boilers as soon as any of the zone valves open up. Each zone plumbed without reverse return and balanced accordingly on completion of work.
Central heating zones all controlled by one programmer with each zone having it's own room thermostat. UFH obviously controlled by it's own programmer/thermostat. TRVs fitted to all radiators. 22mm Automatic bypass valve fitted at top of riser, is this necessary if both boilers have a bypass valve anyway??
Is there anything else really obvious I am missing, obviously aware of the need for blending valves and manifold for underfloor heating.
The primary side between boiler and LLH doesn't need bypass as the LLH acts as a bypass anyway, but the secondary side should have a bypass, im not familiar with Viessmann but I know Vaillant don't require an ABV if you use a LLH as the auxiliary pump switches off with the 2 ports, only the primary pump has an overrun if you use there controls.
Good luck with everything