jaydebruyne

Plumbers Arms member
Plumber
Gas Engineer
Messages
2,718
ive just changed the 2 port on the heating side as I thought it was letting by as all rads started to get hot when only water on demand.

Fired up boiler on demand for water once changed 2 port, flow pipe to rads underneath 2 port stone cold but rads still warming up at a slow rate.

Checked bypass and it's fine. I put 10 replacement rads a couple months ago and when heating on demand all heat up nicely.

Heat only boiler, unvented cylinder.

**update**
I've just noticed it's the return pipes from rads heating up when hot water is on

Any suggestions? Blockage somewhere?
 
Last edited:
Is the pipework following the three tee rule?
Not sure as return paths are concealed. "Apparently" this only started happening when I changed the rads! Pffft
 
I wonder if the old rads had unidirectional TRV's (if they had TRV's) which prevented this reverse circulation? Now you have new rads in with bi-directional valves the problem has been able to show itself?
 
I wonder if the old rads had unidirectional TRV's (if they had TRV's) which prevented this reverse circulation? Now you have new rads in with bi-directional valves the problem has been able to show itself?
Good point!! I'm gonna try pop back today so I'll see if I can get a butchers at the return path and order of the heating, water and bypass.
 
Good point!! I'm gonna try pop back today so I'll see if I can get a butchers at the return path and order of the heating, water and bypass.
So the order after the pump is:
DHW, Heating, Bypass
Should be:
Bypass, DHW, Heating. Same order on return. But return pipework is concealed.
That right?
 
Yes, KingDoey has it right. The original installer didn't follow the 3 tee rule. DHW last connection before boiler. This diagram shows you what happens when you tee in the DHW return before the Heating circuit. I reckon that's what you've got going on and it has only shown as a problem with your new bi-directional TRV's.
http://www.hertsboilers.co.uk/tech/backflow.jpg
 
Status
Not open for further replies.

Reply to Rads coming on when hot water is on in the Plumbing Jobs | The Job-board area at PlumbersForums.net

Similar plumbing topics

  • Question
Ideal Logic 24, Previous problem was that the hot water was only cold or barely warm if the heating was in use. If heating was off and boiler cold...
Replies
2
Views
227
Hi everyone, Looking for a bit of advice, recently went to a job where heating was operating when called for however not for the hot water. I...
Replies
8
Views
402
When I put the central heating on the hot water gets drawn through the pump but is then being diverted straight back to the boiler instead of the...
Replies
3
Views
420
So a strange conundrum regarding water temp if anyone can help resolve, would be much appreciated. Ive tried to give as much info as possible to...
Replies
1
Views
188
M
Hello, We’ve recently moved into a fairly old, fairly big detached house (i.e. fairly draughty, but not too bad by any means) with a fairly new...
Replies
0
Views
287
MartinPod81
M
Back
Top