S

skaly

Hi All I called to service ferroli he25s lpg, water pressure fine, i re charged expansion vessel, emptied condensate trap, co2 -10, o2-6%, co- 144ppm . When the boiler has been on for half hour it starts to make a banging sound every 5 or 10 seconds and a whine. ANY IDEAS .
 
If in hard water area could be scale build-up in EX or dirty system. are they on mains water or private supply ?
 
Its private supply pressure is good, i dont think it is a scale or sludge build up, When it has run for half hour during which i had it at max testing co2 its when it goes to low flame after modulating down BANG 5sec BANG with a whine sometimes
 
is there a way to set up min gas rate on these thats what it sounds like to little gas getting through causing exsplosive ignition
 
Not on this model on HE Plus 25s you can, I think you are on the mark it sounds like a good reason for fault.
 
Have you check'd working pressure (37mbar) is he on bottle gas ? could have dirty bottle, is this banging in boiler or is it ignition ? may be fault with gas valve have you spoke to Ferroli ?
 
So boiler banging in EX ! could be small blockage causeing boiling or pump sticking not clearing heat away from boiler ,strange one, are you in hard water area ? also private water supply can cause some problems , boiler is set up to run on LPG ??
 
Whats cost of replaceing both parts ? (Ferroli Recomend) against boiler replacement, or get Ferroli out on fix'd price repair ! sometimes this is best way to go
 
Its still under waranty so will hand it over to ferroli, Thanks for the help out its very usefull.
 
Status
Not open for further replies.

Reply to Optimax he25s - Banging in the Plumbing Jobs | The Job-board area at PlumbersForums.net

Similar plumbing topics

Hi, Can anyone advise as to why the cold water to my bathroom keeps airlocking? This originally happened about 12 months ago and has happened 3-4...
Replies
9
Views
418
Hi All I have a leak coming from within my Mira Elite QT shower. It seems to be flowing from behind the switching Control. Any ideas what could...
Replies
0
Views
261
The fittings below are for a mixer bar attached to a self contained shower. i.e not a wall. The attaching screws have snapped. I could get two new...
Replies
1
Views
243
Hi all I'm hoping someone can shine a light on this for me Since our stop tap on the pavement has now been filled with sand for whatever reason...
Replies
3
Views
312
Hi, basic question, any insight much appreciated. Looking to have an outdoor tap in my front porch fed from 15mm pex coming up from suspended...
Replies
6
Views
278
Creating content since 2001. Untold Media.

Newest Plumbing Threads

Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock