Hi All I called to service ferroli he25s lpg, water pressure fine, i re charged expansion vessel, emptied condensate trap, co2 -10, o2-6%, co- 144ppm . When the boiler has been on for half hour it starts to make a banging sound every 5 or 10 seconds and a whine. ANY IDEAS .
 
Its private supply pressure is good, i dont think it is a scale or sludge build up, When it has run for half hour during which i had it at max testing co2 its when it goes to low flame after modulating down BANG 5sec BANG with a whine sometimes
 
Have you check'd working pressure (37mbar) is he on bottle gas ? could have dirty bottle, is this banging in boiler or is it ignition ? may be fault with gas valve have you spoke to Ferroli ?
 
So boiler banging in EX ! could be small blockage causeing boiling or pump sticking not clearing heat away from boiler ,strange one, are you in hard water area ? also private water supply can cause some problems , boiler is set up to run on LPG ??
 
Whats cost of replaceing both parts ? (Ferroli Recomend) against boiler replacement, or get Ferroli out on fix'd price repair ! sometimes this is best way to go
 