The pressure gauge got added when we had the expansion vessel put in above the airing cupboard in the loft. My dad tells me that was probably over 10 years ago, so well before out boiler failed. He said this used to reduce in pressure by itself, and since we got our new boiler, it has been better at maintaining the same pressure. But as was suggested by John, I've increased it just a fraction.
 
If you wish, you can quite easily put a can of that F2 into a rad, just post a photo of one of your newest rads showing the air vents and can show you then.
 
If you wish, you can quite easily put a can of that F2 into a rad, just post a photo of one of your newest rads showing the air vents and can show you then.
I will consider this then as it is easy to get hold of. It hopefully is one of these things that can me done by the inexperienced like myself and have little risk of causing any harm.

However, it does say it is intended for boiler noise, which isn't really the issue. I always hear the boiler come on and it is louder than our old one, but it just makes a noise that is only really noticeable in the kitchen or above in the bathroom and it seems a perfectly reasonable sound for what you should expect. The pipe noise surely won't be specifically boiler related will it? Especially when off.

I can't tell what is more likely to be the cause of this starting up. Not sure if emptying the system as well as adding the F1 protector was any more likely to trigger what happened rather than just adding the protector without bleeding the system.


This F2 protector doesn't cost much, but reading up about it, it still seems like it may not be the sort of thing that helps stop radiators and pipes banging / clicking. If it doesn't work, it likely will have to be will have to be wasted as the only other option i can see is the power flush.
 
If you wish, you can quite easily put a can of that F2 into a rad, just post a photo of one of your newest rads showing the air vents and can show you then.
I will get a picture when I get the chance. I just need to understand the exact location on the radiators you are on about. Is this where you bleed them? Even the newer radiators take the same key to bleed them so they likely have the same style vent.


Regarding the heating noise, this picture is quite good at showing what the sound is like over the whole period the heating is on from 06:00 until 08:30.
2021-11-03-101335_1920x1080_scrot.png


Virtually all of the lines are the clicks. I could understand more if it was when it was coming on and going off, but the fact that when it is on, the pipes randomly start doing these clicks so frequently seems odd. Just before an hour for example.
 
Was it making noises when (if) you tried it with both CH&HW off and the hot tap opened?.

This is the plug end you remove after opening the vent (screwdriver slot), you first (after first shutting valves at both ends of rad) open the vent to ensure no pressure, then remove that blank end, open the vent a few more turns, syphon off a litre or so of water and pour in the F1 via a plastic funnel or whatever, close up the rad, reopen valves top up pressure if required, flash up the boiler and wait for the silence!!.
 

Attachments

  • Vent End.JPG
    Vent End.JPG
    16.9 KB · Views: 14
  • Vent Plug.JPG
    Vent Plug.JPG
    8.5 KB · Views: 15
Thanks for this.

I am unfortunately not very good at understanding instructions, so I could do with it breaking down a bit more if that is ok.

I have highlighted in your quote the parts I don't fully understand.

Was it making noises when (if) you tried it with both CH&HW off and the hot tap opened?.
I have looked back in this thread and tried to understand what you are referring to here, but unfortunately can't work it out.
This is the plug end you remove after opening the vent (screwdriver slot),
Unless I am missing something, it does seem that my radiators are different.

Here are some examples:
1.JPG
2.JPG

This above is our main radiator where the system can be bled (left picture), and the only one without a TRV. Though it doesn't look like it, the part above the copper pipe joining the radiator is only just over a year old. I think this initially having a poor fit was possibly related to the airlocks we were first experiencing, as this is what we had to adjust to stop them when they occurred. The other image above to the right is on this radiator where it is bled.
The two below are the two newer radiators.
3.JPG
4.JPG



And this is one that seems to look slightly different again, but is one of our very old radiators. Most of the radiators in the house have the same style valve as the top left picture.

5.JPG



you first (after first shutting valves at
both ends of rad) open the vent to ensure no pressure, then remove that blank end, open the vent a few more turns, syphon off a litre or so of water and pour in the F1 via a plastic funnel or whatever, close up the rad, reopen valves top up pressure if required, flash up the boiler and wait for the silence!!.
The rest of what you have said here, I may understand when I work out how to use the vent.

I assume you mean F2 here!

I also may as well know what type may be easiest for me to use. I've seen this style in a 265ml bottle elsewhere: Boiler Noise Silencer F2 Express 400ml - UK - https://fernox.com/product/boiler-noise-silencer-f2-express-400ml/

Seems more appropriate for the number of radiators.

Hopefully I will get to understand what you mean.


Many thanks.
 
CH is Central Heating. HW is Hot Water. Thought I suggested in some post (maybe on your other thread) or other to shut both (switches) of these off at the boiler front and open the same hot tap that was opened when you heard the boiler whistling noises, if no noise, at least you know the problem is with the boiler or/and system water.

I wouldn't advise removing any of those vents, might run into problems, don't know of any other easy method to add the F2.
 
CH is Central Heating. HW is Hot Water.
Thanks. I think it is more likely to be coincidence, but maybe it is related to hot water and not just the central heating. As this morning had pretty much the same pattern as the image I showed you. Noise when it first comes on at 06:00, and then went quiet until later on, which when I think about it is often when our shower is used. I haven't noticed this pattern in the evening though, which is why I'm not so certain. Our shower is just gravity fed from a cold water tank and heated up by the boiler (if i understand correctly)

Thought I suggested in some post (maybe on your other thread) or other to shut both (switches) of these off at the boiler front and open the same hot tap that was opened when you heard the boiler whistling noises, if no noise, at least you know the problem is with the boiler or/and system water.
I haven't heard any noise from the boiler itself that sounds at all worrying. The airlocks when we had them was extreme noise and vibration from the pipes near the TRVs, but this soon got sorted. The rest of the noise is just these clicks and bangs now.

It is entirely possible that I have filtered some things out that you have said, or misunderstood them due to my poor memory though! If the hot water system for the taps and shower could be related, them that admittedly isn't something I have yet tried turning off and running cold, though I don't know how I would do that exactly.

I wouldn't advise removing any of those vents, might run into problems, don't know of any other easy method to add the F2.
Thanks for making this clear, I'm not surprised I didn't understand. At least I know that if I want to try this, i will have to try and contact a suitable plumber. We've just put this off as each time any have come, the issues seem to have got worse. At least we know that things change each time, so hopefully it will go in the right direction next time.

Just not sure if the call out cost for adding the F2 would almost make it worth finding someone that can do a power flush, though I know little about the rough price for what this could be.





This is likely unrelated, but I've found an old picture that my dad took of how the plumbers originally installed our pump, which wasn't in the position the manual stated it should be:
IMG_20200921_131526.jpg
 
I think I've mixed up threads and thought you had a combi so obviously cant carry out the "cold water" flow test.
May have asked this previously the boiler might display the temperature on its front, if so see what its showing, if > 65C reduce it to 62/63C and see if any difference.
 
I will have repeated myself enough in this thread, so don't worry that you have. Yes, you did mention this earlier and I have changed it. It was originally installed and put to 69 degrees. We now have it at 62 / 63 which we have had it at for some time now. This is the same temperature we had our old boiler at.

My next option then is probably to find someone who can add in the F2 protector correctly, and would probably be ideal if they would also be able to do the appropriate power flush should the first option fail. Or may even be better to avoid the cost for both and do a full power flush. But could do with someone working out what it could possibly be. I will look around this forum. I'm not yet sure on how or if you can ask for jobs here and if there are any limitations.

Many thanks for your help.
 
Well, no luck.

Had the radiators power flushed. The water was confirmed to be rather brown and dirty. So I should still accept that it will have done the system good, but these bangs and clicks are still there.

As every different company / plumber or any place will be like, everyone tells you different things. They said the speed of the pump should never have been touched and left on what it was when it got installed. They put it back to speed 3 which I still think is seriously overkill for a house this size with 7 radiators. The noise this pump makes is just too much on this speed. You can hear the hissing from it at ever radiator in the house. Basically making it sound like the boiler is in every room. I will try and get hold of them regarding the other sounds still being there, but despite what they say, I still plan to switch it back to speed 1, as the heating was just as effective at keeping the house warm with it set to this over the last year.


It is still really puzzling as to what this is. I would not be against it being related to pipe movement with heat expansion and shrinking it it wasn't for the fact that this suddenly started the same day that the system was bled with f1 protector them added. The pipes occasionally tinkled before, but they didn't bang and click all over the house. There has never since been a heating cycle without this happening. It is still almost exactly the same as the picture I last uploaded. There seemed to be very little noise when the plumber first tested it for half an hour when the boiler was set to the highest temperature possible. But when it was reduced to eco (69 degrees), it then started.

I can only guess that something really odd happened relating to the method they filled up the system when they added the F1 protector. This noise is not from the radiators, they are just acting as amplifiers. It is from the pipework. When downstairs, i hear bangs, clicks and pops all over the place. being very sensitive to directions, it has basically allowed me to learn where all the pipes must be, that I never knew before. Why would they be making these clicks all over, at different random stages when they didn't do so before?

Having spent £800+ on a power flush that has failed to get rid of this, as well as attempting different boiler temperatures, pump speeds and all sorts, I am baffled as to what this can be. I accept that heating is nearly impossible to get to make no noise at all. but me being as sensitive as I am, this disrupts my sleep and even focusing on listening to the TV. Although the clicks are obviously not always happening every second, they really are not quiet at all. It just sounds like someone tapping the pipes with a screw driver.

The picture of the audio is an hour of the heating in the evening. You can see just after 45 minutes, it switches off which gets rid of the pump noise, but then the clicks and bangs go crazy for a while. This was not the case until after the power flush, but may be related to the excessive pump speed. The audio attachment is the stage where the pump switches off. Where this is recorded is on the other side of the house to the pump.

I've also just found a video from ages ago before the system got bled and the F1 protector got added. This was well after we got our new boiler and pump. The heating instead sounded like the video shows unless all the TRVs were on full. Whenever they were reduced, it made this main radiator sound like a cold tap was running. This sound could be heard in my bedroom. This infact would still be far better than what is now the case with intermittent bangs. Something strange caused this, but I don't know what.

Sorry for all this info, but just trying to list everything I've tried to make it as clear as possible. I myself am desperate to reduce this noise as it is incredible disruptive.
 

Attachments

  • Pump speed 3 - evening heating.png
    Pump speed 3 - evening heating.png
    15.6 KB · Views: 12
  • Pipes.mp3
    295.9 KB
  • Prior to F1 protector and refill.mp4
    14.3 MB
Given the chaotic (but sadly not uncommon) state of the floor void: pipework, electrics, and general debris typical of any house built without care or modified on several occasions during its life, it doesn't surprise me particularly to hear clicks and noises. I do wonder whether the noise may have come into play when the boiler or pump was replaced and whether some of the existing pipes may have been moved or twisted very slightly and whether this may have led to them grip/slipping against adjacent surfaces during expansion or contraction phases while, perhaps, the air noise was masking these quieter sounds. Indeed it is incredibly hard to work on pipework that is not fully supported without moving it al least a little. That said, I may be going up a dead end in that I find it hard to entertain the idea that the F1 was a cause of the noise, and I may be wrong.

I do have a hunch (no more than that), that someone has fiddled with the balancing of the system. The balancing may now be out or it may have been out previously and is now correct (but is now making a noise it didn't used to due to the return pipes being warmer or cooler than they were in the past).

As every different company / plumber or any place will be like, everyone tells you different things. They said the speed of the pump should never have been touched and left on what it was when it got installed. They put it back to speed 3 which I still think is seriously overkill for a house this size with 7 radiators. The noise this pump makes is just too much on this speed. You can hear the hissing from it at ever radiator in the house. Basically making it sound like the boiler is in every room. I will try and get hold of them regarding the other sounds still being there, but despite what they say, I still plan to switch it back to speed 1, as the heating was just as effective at keeping the house warm with it set to this over the last year.

Essentially, the test for correct pump speed on a modern boiler is that, once the system is warm through and with all radiator manual on/off valves or TRVs fully open, the water leaves the radiators at a temperature no more than 20°C cooler than it went into the same radiator. This would be measured at each radiator; the flow though each radiator can be adjusted (called 'balancing the system') but the pump speed would be set to be fast enough for the radiator that seems to be least easy to supply sufficient water to.

In the old days, the old boilers were coupled to system that would give return water 20°F or 11°C cooler than the flow when the boiler flow was at maximum (around 82°C), but that was largely arbitrary and much to do with the need to avoid thermal stresses to the boilers of the day. This is relevant to you as your system would largely have been designed to work under these conditions: older radiators may not give enough heat on a 20°C drop, so your drop may need to be set at less than this.

At a guess, I would imagine speed 1 would be sufficient for 7 radiators, especially radiators of that age which are unlikely to require a huge amount of flow.

I can only guess that something really odd happened relating to the method they filled up the system when they added the F1 protector.

Or some small change that took place at the same time and they didn't even think to mention (I'm clutching at straws here!).

The picture of the audio is an hour of the heating in the evening. You can see just after 45 minutes, it switches off which gets rid of the pump noise, but then the clicks and bangs go crazy for a while. This was not the case until after the power flush, but may be related to the excessive pump speed. The audio attachment is the stage where the pump switches off. Where this is recorded is on the other side of the house to the pump.
Ticking noise certainly sounds like thermal expansion to me, and the plethora of ticking after the pump switches off would suggest thermal contraction.

I've also just found a video from ages ago before the system got bled and the F1 protector got added. This was well after we got our new boiler and pump. The heating instead sounded like the video shows unless all the TRVs were on full. Whenever they were reduced, it made this main radiator sound like a cold tap was running. This sound could be heard in my bedroom. This infact would still be far better than what is now the case with intermittent bangs. Something strange caused this, but I don't know what.

That running tap noise in the old video with partially open valves is the result of the water, pressured by the pump, squeezing through the restriction created by a partially open valve. It would be undesirable in a properly designed system, but can be unavoidable if modifications to an elderly system (such as fitting higher output radiators) means that the only way to shove sufficient water through some parts of the system without creating excessive flow in other parts is to up the pump speed. In such a case, the pump may need to run at top speed with some of the circuits heavily throttled back. Ideally, the radiator with the most restrictive (longest, usually) pipe run would have its valves fully open and the pump would be set just right to feed that circuit, with the rest of the radiators throttled down and you'd hope the pump would not then need to run so hard as to create this kind of noise.

From your description, I would suggest that what is happening is that the pump is set to a fixed speed (as all old pumps did - modern pumps can (if set to a proprtional pressure setting) vary their speed to give more flow when required and less flow when not required, but this setting tends to provide less pressure than the fixed-speed setting, so does not always work on a legacy system that might simply require more pressure). The fixed speed means the pressure increases when there is little flow through the other radiators, so, having nowhere else to go, it's getting shoved through your only non-TRVd radiator.

Sorry for all this info, but just trying to list everything I've tried to make it as clear as possible. I myself am desperate to reduce this noise as it is incredible disruptive.

I get it. Noise is, actually, one of the (several) reasons I switch my heating off altogether at night. Sometimes theory and practice don't quite go together and there are factors we cannot see. Which can sometimes be more annoying than the symptoms themselves!
 
Right, going over a few more things.

Now I think about it, I do remember that when the plumber had completed the power flush, they tested the system by leaving it running for about 40 minutes while they just waited outside in their van, which I think was quite nice of them as they wanted to make sure it made no noise. This test however was with the boiler set to it's maximum temperature, which obviously is overkill.

Thinking about what Chuck mentioned on the first page, maybe this new boiler does cycle on and off when set to a realistic temperature for the heating (69 degrees). So maybe this is the reason why it can sometimes be quiet for nearly 20 minutes while the heating is on, but maybe when it gets to a certain temperature, it switches off and makes the pipes contract and bang for ages. At this rate, I don't really care if I have to use a less efficient way - I will accept to have to have more input in my parents heating bills given how much I'm suffering with this noise. If there was any way of balancing the system so that when the heating is on, it doesn't constantly need to change the pressure in the pipes. I'm guessing our old boiler did things differently.

The main confusion is just that this dramatic change did occur when the system was bled and refilled with F1 protector. It may well not be the F1 protector, I just know that went in. Maybe it could be related to what happened for about a month after this? More or less instantly when they got refilled in October 2020 with F1 protector, there was loads of air / gas beign generated with no leaks anywhere. Daily, I would bleed the radiators and get a load of black dirt and froth and didn't get to just water until the radiators had been bled for over a minute. This seemed to calm down later into winter and whatever muck was in there had settled / hardened in the pipes over summer when the heating was never used.

Now, is it possible that this reaction was that strong that even a power flush has failed to clean the pipes? Long term damage or something?

The heating still functions fine, although there still is regularly small amounts of air in the radiators when bled. The water is very clean now though. But the noise is now worse than it was just before the power flush.

The only improvement I can think of myself is putting the pump back to speed 1. I will wait until after the plumbers come back as I don't think they agree, but the specific pump noise is loud enough that even my parents are wondering why that makes so much noise. Although in reality, it is quieter than the clicks, just permanent when the heating is active.

Any other suggestions for things I could try will be worth knowing. It may involve ripping up floorboards at some stage, but that should be left until I'm out of other possibilities, as I still don't get what exactly it could be that so suddenly started this banging and clicking in the October before last!
 
Had the plumbers come round again after the power flush had been done, but as i thought may be the case, they were unable to do anything further.

The system water is now perfectly clear, so i still think the flush was worth it. The pump got changed back to speed one, which is certainly quieter regarding the noise of the pump. It however hasn't got rid of this pattern of the heating cycle which still seems pretty much identical to the picture I shared further up the page. It seems that if the boiler and thermostat are at the highest temperature possible, there is virtually none of this noise. It isn't like the radiators got baking hot like this with our old boiler, so it must just be related to the system working differently when at the temperature it should be. I will try turning it back to around 63 degrees.

One thing the latest plumber told me is that the noise more likely started in one location, and travels to others as the system is all connected. I can understand that point of view, but I'm not convinced. There are different noises at different areas of the pipework under the floorboards as the frequency and volume is entirely different, and they occur at different stages. And when downstairs, I can clearly hear the noises coming from all over the place at different stages. I've basically learned the path of the pipes that I never knew before based on where the noise is coming from. I find this unbearable unless whatever I'm doing is consistently that bit louder than the clicks. It can even distract me while having conversations due to how sensitive I am.

If I knew one area started it, and that would stop it, floorboards coming up would not be as much of an issue. But it is clicking and banging everywhere...

The only pipes that I feel have any reason to have moved in the slightest when the boiler and hot water cylinder installation got done were above the boiler in the bathroom, and the bedroom with the hot water cylinder. Also where they first bled the system which was on the only non TRV radiator, but that radiator and the pipes under it don't really seem to make much noise. My bedroom is on the other side of the house to the hot water tank and boiler and the pipes can't have been sifted, other than by natural expansion and contraction. But the noise is awful here, and most other places.

I'm really stuck with where to look under the floorboards first.
 