Just to close this one out, I decided to try and change the valve as a last resort. It turns out it was that that was restricting flow, even though the motor and spindle were operating fine - the innards (diaphragm?) must have been buggered!

So the e majority of you were right all along! Moral of the story: just because all appears well, doesn't mean it is!

Thanks again.
 
Seems I spoke to soon, the error is back. I hear gurgling in the primary coil so it must be air that's trapped somehow because there's only water coming from the air release valve again.
 
Don't open the air release when the pump is on. Wait until it stops as it will allow the air to settle
 
Worth flushing with Sentinel X400? Possibly a blockage rather than air in the coil?
 
Quick update for anyone still interested (or coming across this with a similar problem):

I now have enough flow to operate both CH and HW, I assume the air has settled and escaped.

However, now I get a trickling sound from the boiler when either CH or HW valve opens (eventually the trickling stops after ~1min). I assume this means there is air in the boiler (which will hopefully eventually find its way out)?
 
Status
Not open for further replies.

Reply to No hot water but central heating fine in the Plumbing Jobs | The Job-board area at PlumbersForums.net

Similar plumbing topics

  • Question
Ideal Logic 24, Previous problem was that the hot water was only cold or barely warm if the heating was in use. If heating was off and boiler cold...
Replies
2
Views
227
Hi, I have a Worcester 28i junior boiler that has started to lose pressure, only when using the central heating. When using hot water I have no...
Replies
6
Views
277
Hi everyone, Looking for a bit of advice, recently went to a job where heating was operating when called for however not for the hot water. I...
Replies
8
Views
401
Every two weeks or so I have to go and top up the system because the hot taps are running cold. Boiler display is flashing 0.6 bar and I fill up...
Replies
2
Views
292
PSxxxxxx
P
We run a community village hall and have a large kitchen provided for the use of hirers. This includes a Lincat SLR9 gas cooker which I believe is...
Replies
5
Views
562
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock