I fitted a vaillant eco tecplus 630 in July. Underfloor heating now required. It will only come on when the towel rails are calling for heat and zone valve open. I know this is a wiring problem. I didn't wire the boiler a colleague did. Live, neutral earth ok. But I can see only one of the wires on a separate wire is connected to the 240v rt. Any suggestions before I hire a sparky? Thanks
 
You have a separate port valve on the under floor correct?
 
There is only zone valves on the towel rails and hot water. No zone valves on either underfloor manifolds

There’s your problem need them on and that’s why it’s only running with the towel rads
 
As above, each area (water/heating/ugh) should have its own valve. That’s why it is working with the towel rails. Who did the spec for the UFH?

Please like this post if you have found it helpful.
 
Update electrician been, needed one extra live than normal. Wiring from underfloor has an electronic switch on the rails that switches the boiler on that, also has all the other heads wired to it. That's why I am not a sparky, even he found it wasn't straightforward.
 
Update electrician been, needed one extra live than normal. Wiring from underfloor has an electronic switch on the rails that switches the boiler on that, also has all the other heads wired to it. That's why I am not a sparky, even he found it wasn't straightforward.

That means your going to get the slab warning on it’s own with other circuits on eg like reverse circulation
 
That means your going to get the slab warning on it’s own with other circuits on eg like reverse circulation
There is no reverse circulation, tested all, valve on towel rails and hot water. The underfloor was fitted 12 years ago no problem till new boiler went in. Now working perfectly.
 

Reply to New Vaillant boiler fitted, problems with underfloor heating. in the Plumbing Jobs | The Job-board area at PlumbersForums.net

Similar plumbing topics

  • Question
Ideal Logic 24, Previous problem was that the hot water was only cold or barely warm if the heating was in use. If heating was off and boiler cold...
Replies
2
Views
295
Every two weeks or so I have to go and top up the system because the hot taps are running cold. Boiler display is flashing 0.6 bar and I fill up...
Replies
2
Views
334
PSxxxxxx
P
I have had a look at previous posts and think I know the answer to this but just before I make it worse could I just check what you think about...
Replies
7
Views
322
Hi, Can anyone advise as to why the cold water to my bathroom keeps airlocking? This originally happened about 12 months ago and has happened 3-4...
Replies
9
Views
511
Back
Top