Hi all new to the forum, I have recently moved into a new build house with underfloor heating installed throughout the ground floor, 4 zones, kitchen (tiled),lounge (carpet), hallway (tiled), mancave/front room (carpet). It’s an Emmeti system with manual thermostats in each zone.

I turned it on for the first time yesterday as I was bored and it was slightly cooler, I gather to get the best out the system should be on 24/7 when it’s on in anger.
I noticed the carpeted rooms took longer to feel any difference, I appreciate the installer wouldn’t of known I would have this floor covering as I had it fitted after purchasing. I was just wondering what ideal temperature differntial I should be looking at for the flow and return temperatures, I don’t think it’s been balanced properly as all flow rates look to be set the same. I’m assuming if a play with the flow rate I can get the temperature differentials across the flow and return the same for all zones.
I have just been looking at salus auto balancing actuators, are these a worthwhile upgrade, looks relatively simple to install.

Thanks for any help and advice.
 

rpm

Esteemed
Plumber
Will, I`m not being rude but ufh with carpet in St Google brought up answers from ufh manufactures. It is worth a read.
 

ShaunCorbs

Staff member
S. Mod
Plumber
Gas Engineer
I would stick to the manual balance

If you phone emmeti they might have the drawings still on file with the correct loop lengths and balancing values
 

rpm

Esteemed
Plumber
I don’t even know what your about. Not trying to be rude
No worries.
Put "ufh with carpet" in to whichever search engine you use, using google there was around 5 ufh manufactures replies talking about the tog value of the carpet and how that effects the heat in the room.
 

ShaunCorbs

Staff member
S. Mod
Plumber
Gas Engineer
Is there a temperature diffential between flow and return that should be aimed for ?
Normally around 10 Degrees difference on the main flow and return into the manifold
 
Yes sorry, I’ve followed this advice when i had carpet fitted, low tog underlay, and not a combined tog of anymore than 2.5. But when I had the system running yesterday all the flow rates were set pretty much the same, I don’t know, this might be correct. But I didn’t know if there was a standard way of balancing the system by getting the difference between the flow and return temperatures all the same.
 
Normally around 10 Degrees difference on the main flow and return into the manifold
So if I get no where with emetti If i play with the flow rates and aim for this, I won’t go far wrong !

One other thing is some of the flowmeters have air in and some don’t, is this normal.
 

ShaunCorbs

Staff member
S. Mod
Plumber
Gas Engineer
Emmeti should be able to guid you through the balancing task as really ufh goes off loop length and floor type

As for the air depends how much you can't hear any in the loops can you ?
 

ShaunCorbs

Staff member
S. Mod
Plumber
Gas Engineer
No can’t hear anything going through the pump or anything.

You think emmeti will have all the details ?
There a chance but could of been bought via a supplier

Could you ask the builders ??
 
CorgiDirect - Discounted Corgi Related Documentation and Plumbing Supplies
This official sponsor may provide discounts for members

Reply to New build UFH help and advice in the Water Underfloor Heating Installations area at PlumbersForums.net. Plumbing questions, answers, tips and tricks.

Plumbase - Plumbers Forum Sponsor
This official sponsor may provide discounts for members

Plumbing and Plumbers

Plumbing Workwear

Shower Power Booster

Plumbase Spares - Plumbing Supplies and Spare Parts

Water Underfloor Heating

CORGI Direct for Plumbers

The Wetroom Store

Plumbase Spares

New Posts Threads Members

Top