Discuss Losing pressure heating in the UK Plumbing Forum | Plumbing Advice area at PlumbersForums.net

Messages
4
Hi all not a plumber but am an engineer I have pressure drop in the system Worcester Bosch came back after repressureising the expansion vessel and he replaced the heat exchanger element. The boiler is coming up for 15 years old.

The boiler was going below one bar and not increasing when heating was on. So now he replaced the heat exchanger, the pressure vessel and the PRV. The system now seems to hold pressure and increases when the boiler does work.

The question is if I do have a small leak how do I find it?

Thanks
 
Has the boiler been ruled out as a source of the problem?

If so, go round systematically and have a careful look at every valve (zone, TRV, drain-point, etc.) and compression joint for evidence of leaks, e.g. white chalky deposits, discoloured/damp floor boards. Use a mirror, torch and reading glasses (if you normally use them) so you get a proper look. Nine times out of ten you'll find a TRV or lock-shield valve stem is the problem. Automatic air vent valves are another relative common cause of leaks.
 
Has the boiler been ruled out as a source of the problem?

If so, go round systematically and have a careful look at every valve (zone, TRV, drain-point, etc.) and compression joint for evidence of leaks, e.g. white chalky deposits, discoloured/damp floor boards. Use a mirror, torch and reading glasses (if you normally use them) so you get a proper look. Nine times out of ten you'll find a TRV or lock-shield valve stem is the problem. Automatic air vent valves are another relative common cause of leaks.
Hi Chuck the engineer said I have replace all the components that fail it’s like a new boiler so possibly. He pressure tested the boiler and said it passed. Cool I will check what you say and look for a leak.
 

Reply to Losing pressure heating in the UK Plumbing Forum | Plumbing Advice area at PlumbersForums.net

Similar plumbing topics

Hello, I am seeking some advice, I have a POTTERTON PROMAX 28 COMBI Boiler and I noticed yesterday that the water around the house is no longer...
Replies
4
Views
281
Every two weeks or so I have to go and top up the system because the hot taps are running cold. Boiler display is flashing 0.6 bar and I fill up...
Replies
2
Views
269
PSxxxxxx
P
  • Question
Ideal Logic 24, Previous problem was that the hot water was only cold or barely warm if the heating was in use. If heating was off and boiler cold...
Replies
2
Views
204
Hi everyone, Looking for a bit of advice, recently went to a job where heating was operating when called for however not for the hot water. I...
Replies
8
Views
380
We run a community village hall and have a large kitchen provided for the use of hirers. This includes a Lincat SLR9 gas cooker which I believe is...
Replies
5
Views
541
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock