Hi Guy's,

Looking for some advice on an issue I have having with a recently installed thermostatic mixer shower in my ensuite. Everything was working fine for a coupe of months however now the valve has started misbehaving which is resulting in having to turn the temperature valve round further to get any heat but then once you get to the point that the water is warm turning even just a millimetre further means it can go from warm to almost scalding.

A couple of years ago we had a unvented cylinder installed and I have just checked it over and I dont think any of the cold outlets have been fed off the balanced supply as the valve that the cold mains comes into in the attached diagram does not have a balance supply coming from it and has just been capped off. I suspect that this may be the issue but im a bit confused as to how its not effected our other shower in our main bathroom or the old shower in my ensuite that i have recently replaced. Any advice welcome.

Heating.PNG
 
Get the shower installer back. It is more likely to be a shower cartridge and / or inlet filter rather than the lack of a balanced cold supply.

If not balanced, the cold water flow rate will be equal or greater that the hot after a short period off running
 
Get the shower installer back. It is more likely to be a shower cartridge and / or inlet filter rather than the lack of a balanced cold supply.

If not balanced, the cold water flow rate will be equal or greater that the hot after a short period off running

Unfortunately that would be me :) . My first thought was the shower cartridge but I read that they don't fail very often and its a brand new shower. I would swap it our to test but they cost almost as much as the whole shower did. I will take it out and give it a clean and see if that sorts it.
 

Reply to Issues with thermostatic shower valve in the Bathrooms, Showers and Wetrooms area at PlumbersForums.net

Similar plumbing topics

  • Question
Ideal Logic 24, Previous problem was that the hot water was only cold or barely warm if the heating was in use. If heating was off and boiler cold then would get hot water most of the time. Changing the flow cartridge about 2 years ago (when I moved in) solved this problem enough to suffer it as...
Replies
2
Views
121
The fittings below are for a mixer bar attached to a self contained shower. i.e not a wall. The attaching screws have snapped. I could get two new brackets, dismantle that existing one and start again or I could try and re attach via those screws, removing the broken ones from the plate and wall...
Replies
1
Views
194
I have had a look at previous posts and think I know the answer to this but just before I make it worse could I just check what you think about this one. Granddaughter just moved house and this valve decided to leak when it was closed. When open its fine. Normally I have repacked the gland on...
Replies
7
Views
184
Hi, Can anyone advise as to why the cold water to my bathroom keeps airlocking? This originally happened about 12 months ago and has happened 3-4 times since. It’s an upstairs bathroom, fed from a tank in the attic. The tank is about 8 Meters away and feeds a bath, sink and toilet. The tank...
Replies
9
Views
322
Hello, I am seeking some advice, I have a POTTERTON PROMAX 28 COMBI Boiler and I noticed yesterday that the water around the house is no longer warming up. The heat exchanger has been changed 6 months ago, so I do not believe it is that. Does anyone have any ideas on what it could be? Thanks
Replies
4
Views
223
Creating content since 2001. Untold Media.

Newest Plumbing Threads

Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock