81ll

Gas Engineer
Messages
74
Hi I'm new to fault finding and have come across this boiler which I haven't seen before.

- CH no problem
- DHW when the taps are mid - full no problem
- when DHW run at very low flow rate the boiler quickly displays the error code 1

What I have done:

- the temp differential between the flow & return is 18 degrees when at about 85 degrees & 6 degrees when cool
- I have removed DHW thermistor of the pipe and got the same issue
- Was thinking about checking the ohms but didn't know what valves should be, tried to call Halstead but the phone line indicated they were closed (it was only 4pm)
- The MIs state that the boiler will lock out when the temp reaches above 105 degree, when I had my probes on the flow & return the boiler was locking out at about 85 degrees

I'm thinking its the thermistors but don't want to change them if there ok.

Any suggestions, any help would be appreciated
 
Or just post it in the private gas forum which is situated in the public one .
 
Status
Not open for further replies.

Reply to Halstead Ace HE 35 Error Code 1 in the Plumbing Jobs | The Job-board area at PlumbersForums.net

Similar plumbing topics

We are from Alberta, and I own an electrical company. I have been asked by a BC Mechanical P. Eng. to install an emergency STOP button at the man-door to the boiler room. It's intent is to 'halt' the operation of the boilers in the room should there be an emergency. He is demanding that I do...
Replies
5
Views
257
  • Question
Ideal Logic 24, Previous problem was that the hot water was only cold or barely warm if the heating was in use. If heating was off and boiler cold then would get hot water most of the time. Changing the flow cartridge about 2 years ago (when I moved in) solved this problem enough to suffer it as...
Replies
2
Views
127
I have an ideal vogue max S18 boiler and I’m considering fitting auto balancing TRVs, my question relates to the boilers pump. I see a boiler pump menu for either 70% or 100%, so, is the pump set at either one of two fixed speed percentages or does the pump actually vary speed, (modulate)...
Replies
1
Views
143
Hi, Can anyone advise as to why the cold water to my bathroom keeps airlocking? This originally happened about 12 months ago and has happened 3-4 times since. It’s an upstairs bathroom, fed from a tank in the attic. The tank is about 8 Meters away and feeds a bath, sink and toilet. The tank...
Replies
9
Views
323
I have had a look at previous posts and think I know the answer to this but just before I make it worse could I just check what you think about this one. Granddaughter just moved house and this valve decided to leak when it was closed. When open its fine. Normally I have repacked the gland on...
Replies
7
Views
185
Creating content since 2001. Untold Media.

Newest Plumbing Threads

Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock