with the front cover removed the flame died out quietly, making it look like I was inventing the problem. However, when he replaced the cover it started popping again.
That might be significant. How does the air flow to the burner with the cover on? Perhaps there's an obstruction, dust build-up or something, in the air path
 
That might be significant. How does the air flow to the burner with the cover on? Perhaps there's an obstruction, dust build-up or something, in the air path
That's a good point. It's not a sealed unit. There's a 2" gap along the bottom of the inner cover at the front of the boiler allowing free flow of air beneath the burners. The outer cover has a cutout grille on front and sides and there aren't any obstructions. In fact it's in a pretty draughty outhouse so I thought at first it might be the wind blowing out the pilot, but the pilot will stay lit for weeks when the boiler's not being used and it wasn't until I heard it pop that I realised what was causing the problem. The HE says it's not dangerous and has issued his safety check certificate but it's annoying to come down on a cold morning when the boiler has gone out. Our paying guests are a bit prickly, too, when they feel they aren't being looked after properly.
 
Thanks Gasmk1, that sounds logical too. Since it was okay with plenty of air does that mean there could be more gas than there should be? Would you think the jets might have become enlarged and are letting too much through? The flame doesn't seem too fierce though.
Has your engineer checked the injectors
 
Status
Not open for further replies.

Reply to Compatible gas control valve for obsolete Honeywell in the Plumbing Jobs | The Job-board area at PlumbersForums.net

Similar plumbing topics

Hi everyone, My customer has a gas fire (Gazco Logic HE fire, about 10 years old). It's a slide control fire. The fire has become difficult to...
Replies
1
Views
301
  • Locked
Replacing a remote gas control valve with its manual equivalent. My daughter has a gas coal effect fire. First, I know they're crap, she'll just...
Replies
8
Views
967
Hey all Looking for a consensus on an issue that has arisen. Disclaimer is that my ideal icos 12 boiler Is over 10 years old but has been...
Replies
12
Views
2K
Hi there, thanks for your time to look at this record long post!! I work on the operational management side or a small building contracting firm...
Replies
9
Views
1K
H
Hi there, thanks for your time to look at this record long post!! I work on the operational management side or a small building contracting firm...
Replies
0
Views
656
HRP123
H
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock