Search the forum,

Discuss Cheers not reaching temp. F and E overflows. in the Plumbing Jobs | The Job-board area at PlumbersForums.net

Status
Not open for further replies.

armyash

Esteemed
Plumber
Gas Engineer
Subscribed
Messages
2,653
One of my neighbours came to me about 8 weeks ago and said the "small tank" was overflowing. I jumped in the loft and ball valve was running. Assumed just letting by, replaced ball valve. Heard nothing assumed all sorted.

Neighbour came back to me a couple of weeks later and said it's still happening. It doesn't overflow all the time just occasionally. I said if you want me to investigate I will, he said not urgent. (I think he is after a freebie). Told him to turn the pump down to see what happens, he said this has helped but not cured. Said the water level in the F and E goes up and down.

His wife called me yesterday, said its still intermittently overflowing but also the radiators are not reaching temperature. She said she changed the batteries in the stat but still the same. I said I'd need to have a look and it likely will not be a 5 minute job.

What does this sound like? Split coil or blocked cold feed or dodgy pump or something else? :D

I'm going over tomorrow to investigate so hoping to go armed with a few ideas.

Thanks for any info.
 
Possibly, will find out tomorrow, I didn't think about that. Only seen that on cwst.

Is that the most likely? Would it affect the ch?
 
Won't have that on a f and e tank Darren

Could be a blockage on the feed / blockage
 
Is the F&E lower than Cold storage tank ? is it getting warm ? how old is cylinder ? Hard water area ? likely pin hole in coil.
 
Didn't think that could happen on f and E.

I'm sure the 2 tanks are sitting on the same support.
 
Water in tank is cold.

Cylinder is pretty old.

It is a hard water area.

What is the quickest way to check if its the coil?
 
OK thanks so if sitting on the same support I can raise the F and E and see if that solves it.

How can this only start happening if its been this way for years.

This won't affect the rads getting hot though will it.
 
Blocked cold feed sounds most likely. A pin hole in the coil would mean it would constantly overflow and wouldn't be intermittent.
 
OK thanks so if sitting on the same support I can raise the F and E and see if that solves it.

How can this only start happening if its been this way for years.

This won't affect the rads getting hot though will it.
That’s if the coil has split,check cold feed an vent for blockages.If your happy that there is no restriction there,cap cylinder flow an return if they have an immersion heater on the cylinder an leave it couple days.I can’t say I know a quick way of proving the coil is split,others may

* re read what you said about rads not getting hot now,I’d definately go with blocked cold feed first.
 
Thanks for the replies, I said to him likely to be blocked cold feed or if unlucky a split coil.

Will update once looked and job is done (if I get it).
 
I'm heading over to have a look in 20 minutes, taking a magnet with me to check the cold feed.

Will look at tanks in loft to see if f and e water level is lower than cwst.

I doubt they will want me draining down tonight to check the coil (if it's not the cold feed). I'm free Saturday to do that if needed. Plus I can still check the coil if it's the cold feed once it's drained.

Hoping it's the cold feed because I know they won't want to pay the going rate for a new cylinder and I don't want to be labelled a rip off in my own street.
 
Just been to have a look.

Front room rad (middle floor - town house) wasn't getting hot, needed bleeding.

There was a call for heat when I got there but boiler/pump etc was doing nothing, rads lukewarm on 30. Customer said hw has been really hot, and a couple of weeks ago rads started to warm up with hw turned on.

Switched ch off.

Set hw to on, pump kicked in. Double checked cyl stat working. All OK.

Switched hw off.

Lever on 3 port slack and moving with no demand on.

Switched ch on. Nothing. Gave lever a nudge, all fired up rads now getting nice and hot.

A few compression fittings on cold feed arrangement, magnet not sticking so looks like cold feed was an issue before but has been sorted.

Poked my finger in vent pipe, it was wet, saw the odd drip.

Putting it down to a faulty 3port, I have left hw switched off and told them they should still be getting hw as the valve is stuck and letting by. I'm thinking with the 3 port the way it was it was acting as a restriction on the ch. Rads have likely been getting warm when the hw demand comes on and turning off once cyl stat is satisfied.

Have told them to text me tomorrow evening about the o/f whether it has stopped dripping. They said ch normally comes on at 1630 and they notice the o/f around 1900.

Does that all sound about right to you pro's?

Thanks
 
Can the title of this thread be changed to CH from Cheers please, I don't seem to be able to change it. Thanks to predictive text on my phone.
 
Yea sounds like it's boiling over best if you can convert to s plan
 
Will replacing the 3 port not solve the issue?

if its suck with the micro switch always on yes

did you do any elec testing?
 
Getting 240 on the white when calling for heat. 240 goes when demand is turned off. That's what I should be getting?
 
white one is heating

are you getting anything on grey and orange (when hot water off?)
 
Thank you for taking the time to read the thread and reply ShaunCorbs.

Thanks for everyone else's replies.
 
Status
Not open for further replies.

Reply to Cheers not reaching temp. F and E overflows. in the Plumbing Jobs | The Job-board area at PlumbersForums.net

Similar plumbing topics

S
Hi, I seemed to have a blockage in kitchen sink. A plumber came and cleared all the pipework that is visible inside my home (there was debris and pebbles!) We saw that the pipe that takes water down the gutter was visibly full to the top. He said he will return with a coil to push through...
Replies
1
Views
45
Every two weeks or so I have to go and top up the system because the hot taps are running cold. Boiler display is flashing 0.6 bar and I fill up to 1.3. I've had an engineer look inside the boiler and he can't see anything wrong. I've checked the pipes all over the house and cannot see any...
Replies
1
Views
132
Hi, Can anyone advise as to why the cold water to my bathroom keeps airlocking? This originally happened about 12 months ago and has happened 3-4 times since. It’s an upstairs bathroom, fed from a tank in the attic. The tank is about 8 Meters away and feeds a bath, sink and toilet. The tank...
Replies
9
Views
323
Hello all, I’m replacing a concrete paving slab patio in the back yard. The original patio used 50mm deep concrete slabs on hardcore & sand. I’m planning to pour a 100mm deep concrete patio on 100mm hardcore. In order to achieve the same final height to line up with the rest of the patio, I...
Replies
6
Views
231
We run a community village hall and have a large kitchen provided for the use of hirers. This includes a Lincat SLR9 gas cooker which I believe is a 23.8Kw appliance with all six burners and oven on max. This was installed some 10 years ago and has passed all subsequent Gas Safety inspections as...
Replies
5
Views
443
Creating content since 2001. Untold Media.

Newest Plumbing Threads

Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock