Just planning a kitchen. Usually a combi fitted into a kitchen has the pipes from the bottom put through the worktop and boxed in. The layout I am working with is a bit of a pain, and I have little choice but to put the dishwasher below planned location for the boiler. At the moment neither can be moved.

As the dishwasher has little (i.e no) clearance behind I cannot plan it to allow the pipes to pass from the boiler to the left hand side of the dishwasher/sink etc. Is it acceptable to chase these pipes (inc gas) into the wall between the boiler down to behind this dishwasher and out to one side.
 
You can chase ... A thought though, could you channel them in a duct so they're accessible?
 
i always thought it was ok as long as it was protected i.e plastic coated.
 
You can chase ... A thought though, could you channel them in a duct so they're accessible?

Was just thinking about if I could do this, not sure yet. I will chase the wall / allow space for a duct, so that the installer can just run the pipe in the space.
 
Always used BI on chased work myself, surely you can still puncture plastic coated or similar........
Can the boiler be re-positioned anywhere else ....
 
Black iron is a good idea but not a legal requirement. B.S. 6891 doesn't even mention protection from corrosion for gas pipes chased into walls.
 
I also though black iron of coated copper but with a steel plate in front to protect was a requirement if gas pipe is set in a wall (sure it is in viper book somewhere) to protect from mechanical damage.
 
Metallic protection is specified for timber framed not pipes chased in masonry. Check BS 6891 section 8.9 ans figure 6.
 
Was just thinking about if I could do this, not sure yet. I will chase the wall / allow space for a duct, so that the installer can just run the pipe in the space.

I've seen a few purpose made channels in walls with just a screwed on boarding flush with the wall surface for access. It depends on what the wall construction is; cavity, timber framed....etc Leave it open top and bottom if you're concerned about gas regs, and if cavity wall, make sure you don't allow any gaps in the cement that can communicate with the cavity! AND also consider where the filling loop is going to be fitted if you happen to have an appliance that doesn't have an integral one :)
 
Status
Not open for further replies.

Reply to Can pipes to combi be chased into a wall. in the Plumbing Jobs | The Job-board area at PlumbersForums.net

Newest Plumbing Threads

Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock