Discuss Boiler not lighting when divert valve in 'Mid' position in the Plumbing Jobs | The Job-board area at PlumbersForums.net

Status
Not open for further replies.
U

Ukdodger

Hi, I changed this divert valve like for like.

ACL Drayton (Invensys) MA1/679-3 Mid-Position Motorised Valve

When only heating is required the valve moves to 'H' as it should and the boiler lights.

When only hot water is required the valve moves to 'W' as it should and the boiler lights.

But when both water and heating are required the valve moves to 'M' as it should but the boiler doesnt light.

I've checked and double checked the wiring from the valve to the junction box. They are correct. When I changed valves I changed each wire one for one. So I took orange out from the old divert valve connector and replaced it with the orange from the new valve and so on for each of the four wires. I dont think the problem is with the wiring. Any help greatly appreciated. Thanks
 
Unlikely I thought as it's new and isnt it the Controller that turns the boiler on/off not the valve?
 
give the valve a whack, had one just before xmas. hit on the side made it work again?
 
give the valve a whack, had one just before xmas. hit on the side made it work again?

Thanks Redsaw. I'll give it a try. But is there a diagram anywhere that details the circuitry between the Controller, Valve, heating and water thermostats. For the pump to operate it must get a signal from either or both thermostats and the Valve. If I knew which wires were which I could check for a voltage?
 
Status
Not open for further replies.

Reply to Boiler not lighting when divert valve in 'Mid' position in the Plumbing Jobs | The Job-board area at PlumbersForums.net

Similar plumbing topics

  • Question
Ideal Logic 24, Previous problem was that the hot water was only cold or barely warm if the heating was in use. If heating was off and boiler cold...
Replies
2
Views
220
Hi all I'm hoping someone can shine a light on this for me Since our stop tap on the pavement has now been filled with sand for whatever reason...
Replies
3
Views
339
I have had a look at previous posts and think I know the answer to this but just before I make it worse could I just check what you think about...
Replies
7
Views
257
Hi, I have a Worcester 28i junior boiler that has started to lose pressure, only when using the central heating. When using hot water I have no...
Replies
6
Views
265
I have an ideal vogue max S18 boiler and I’m considering fitting auto balancing TRVs, my question relates to the boilers pump. I see a boiler...
Replies
1
Views
191

Newest Plumbing Threads

Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock