Hi all

got called out to service a boiler today asked customer if there's any problems ? Oh the heating not worked for 3 weeks ! So switched the heating on to the Icos 12he boiler fires up then burner goes out and burner light flashes, I went to check the pump to find the new grind dos alpha2l pump , any ideas how to check see if it's wirking ? The power is on as it displays "on" but I'm not sure if it spinning ? I pressed the arrow under the display but nothing changed ? Unplug it and plug back in I see the lights all come on them they go down one by one until off ? The pump sounds like it's pumping but what carnt check it any ideas guys

are thes pumps meant to show the speed of the pump when on ?

Cheers all
 
ALPHA2 L | Grundfos

Push the arrow button so that you have the the lines on the left on, thats speed 3.

The display should show a number, at speed 3 this should be in the 40's. If it isn't then it isn't shifting water, these things can be a real to clear air from.
 
These need to fitted properly or will give issues.
Make sure fitted on correct plane and cable drops directly down from bottom of pump.
Put on to stage 3 and run for about 10mins to clear air from pump. Then should show 40-45w on display if all is well.
 
Status
Not open for further replies.

Reply to Alpha 2l pump in the Plumbing Jobs | The Job-board area at PlumbersForums.net

Similar plumbing topics

I have an ideal vogue max S18 boiler and I’m considering fitting auto balancing TRVs, my question relates to the boilers pump. I see a boiler...
Replies
1
Views
192
Hi All I have a leak coming from within my Mira Elite QT shower. It seems to be flowing from behind the switching Control. Any ideas what could...
Replies
0
Views
273
Every two weeks or so I have to go and top up the system because the hot taps are running cold. Boiler display is flashing 0.6 bar and I fill up...
Replies
2
Views
283
PSxxxxxx
P
Can anyone recommend a decent multi meter, preferably under a 100 pounds. It's for checking boiler components so I don't need a top spec one...
Replies
7
Views
305
  • Question
Ideal Logic 24, Previous problem was that the hot water was only cold or barely warm if the heating was in use. If heating was off and boiler cold...
Replies
2
Views
221
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock