Hi,
I'm looking for a little help. I bought a new build and have heating issues since we moved in. The builder wants the installer to resolve the issues, but hes been back now about 5 times and still the issue persists. I was hoping for a little advice. We have 2 circuits 1 upstairs and 1 downstairs. When the downstairs is on the rads upstairs start getting hot one by one via the return. Whats the best way to get to identify whats causing the issue. Is this issue generally caused by the way the pipes have been run i.e. 22mm to microbore or is it generally the pipework around the boiler. I'm reluctant to pay someone to resolve it, as its the builders responsibility but the plumber the builder keeps sending (the installer) is not fixings the problem and seems to not be able to identify the issue either. Any help or direction would be greatly appreciated.
 
It's the plumbers fault for teeing in the returns wrong

What system do you have combi or unvented eg cylinder ?
 
It’s an unvented cylinder and Worcester condenser boiler. I could post a photo of the pipe work near the boiler tonight if that would help identify. I’ll be honest there are. Lot of pipes coming and going
 
Photos would be helpful almost certainly. If I can't work out the problem somebody here will. They are a good lot.
 
If the installer understands gravity they should be able to work it out. If there's hot water below cold in a vertical pipe, they will start to mix even if no circulation.
Agree that photos would help, ideally annotated with which pipe is which if not clear.
 
Thanks everyone. I’ll take a photo and post tonight. Your help is much appreciated!!
 
If the installer understands gravity they should be able to work it out. If there's hot water below cold in a vertical pipe, they will start to mix even if no circulation.
Agree that photos would help, ideally annotated with which pipe is which if not clear.
But it's not gravity or convection that causes this problem. All the CH return pipes must be commoned before the HW cylinder return comes in. My first house in 1973 had it, the builders/plumbers had piped it wrong. Got them to change it and everything OK.
 
Last edited:
Oh right maybe i misunderstood it then! So what does cause it?
What happens if it's piped wrong is the HW return entering the other pipe has 2 ways to go - the "right" way, to the boiler, or the other way, through one set of rads in the reverse direction, then the other set in the forward direction and back to the boiler. If you do a sketch you can easily see it.
I think that's the most likely explanation for what's going on here. A schematic, or a photo if the pipes are identified would be useful.
 
Last edited by a moderator:
Is it a 2 port or 3 port system?
 
through one set of rads in the reverse direction, then the other set in the forward direction and back to the boiler.
interesting, so upstairs has a closed zone valve, but somehow the backflow through the upstairs circuit can get through to the boiler by going forwards through the downstairs circuit (a second time?)

I'm even more confused, and I'm not quite sure what diagram to draw, but I'd agree the piping would be seriously messed up to have that kind of flow.
 
having read your original post, your 1973 system was different and had two heating loops on one zone but teed in separately. In this case the OP has two heating circuits on two zones, so that circulation wouldn't happen.

From reading your description, your system could indeed have also suffered from convection on top of the circulation you mentioned, as the hot return from the DHW side connected with a vertical pipe going back to the upstairs rads:
"The boiler is in the kitchen, ground floor. The return from the HW cylinder comes down from the ceiling. The common return from the upstairs rads also comes down from the ceiling. The common return from the downstairs rads comes up from the floor. Originally the upstairs rads return and the HW cylinder return were commoned, then the downstairs rads return came in - problem! Modified to common the rads returns, then the HW cylinder return comes in​
"
 
Last edited by a moderator:
Hi All,

Here is a photo of the pipework. I've labelled everything that is labelled on the pipes. Any ideas if there is an issue here?

IMG_8900.jpg
 
Hi All,

Here is a photo of the pipework. I've labelled everything that is labelled on the pipes. Any ideas if there is an issue here?

View attachment 33772
I think the pipe labelled Return is upstairs return. I can see where the HW cylinder return comes in, below the boiler. No pipe is labelled Downstairs return, but my guess is it is off the photo to the right. I can just about see a tee right on the edge of the photo. If that's it, that's the source of the problem, IMO.
 
having read your original post, your 1973 system was different and had two heating loops on one zone but teed in separately. In this case the OP has two heating circuits on two zones, so that circulation wouldn't happen.
Glad you found that, I thought it was on a different forum I visit! Or I would have just referred OP to it, where it was discussed at some length. And the problem was as I and others predicted.

I don't believe Jeff's system is piped differently, at least not different enough to avoid the problem. See my reply to his #14.
I've attached hand sketch to illustrate what I was saying.
upload_2018-6-5_19-33-42.jpeg
 
Glad you found that, I thought it was on a different forum I visit! Or I would have just referred OP to it, where it was discussed at some length. And the problem was as I and others predicted.
it was, you linked it in your post (although part of the url at the start was ******* for some reason)
I don't believe Jeff's system is piped differently, at least not different enough to avoid the problem. See my reply to his #14.
I've attached hand sketch to illustrate what I was saying.
Yes I realise what condition you mean now that you mention, basically with two heating loops joined after the diverter valve, and teeing into different point of the DHW return.
in this case we can see two zone valves in the photo, so that doesn't apply.
Regarding the OP on the other forum, he stated there are 3 zones and HW, of course that doesn't rule out the configuration you mention in all of the zones separately, but unlikely (he stated if any of the zones are on, it migrates to both the rest of them)
 
Any ideas if there is an issue here?
I can't quite see the Tee mentioned by fixitflav so I'm going to offer an alternative viewpoint for consideration if that's alright with everyone - I think the "return" from above is shared between the two zones, and when downstairs is on, water from there rises upstairs due to convection. It appears that there's a check valve on the visible section of return, presumably to keep the bypass from causing convection, but not protecting the two CH circuits from each other.

Any chance of a photo of where the downstairs return joins the rest of the return?
 
Sorry the photo isn;t the best. I had trouble trying to get it all in. The boiler is in the garage on ground floor all pipes are run into the first floor floor. Then either drop to the rads downstairs or up out of the floor to the rads upstairs. The return looks like the only return.
IMG_8901.JPG

I've added a mother photo of all pipes going up into the ceiling(first floor floor) the lagged pipe right under the boiler is the only one there is no other joining it to the right (i've added another photo)
IMG_8902.JPG
 
t was, you linked it in your post (although part of the url at the start was ******* for some reason)
Interesting, you live and learn!
Yes I realise what condition you mean now that you mention, basically with two heating loops joined after the diverter valve, and teeing into different point of the DHW return.
in this case we can see two zone valves in the photo, so that doesn't apply.
Having 2 zone valves doesn't necessarily prevent the problem. I'll do another sketch tomorrow.
Regarding the OP on the other forum, he stated there are 3 zones and HW, of course that doesn't rule out the configuration you mention in all of the zones separately, but unlikely (he stated if any of the zones are on, it migrates to both the rest of them)
But following the forum's recommendations, it cured the problem.
 
Having 2 zone valves doesn't necessarily prevent the problem. I'll do another sketch tomorrow.
Interesting, so the configuration you mention may exist within a zone. I thought unlikely but now I can see it would be easy done.

So in this OP's case we are looking for the downstairs circuit goes all the way back to the return, and on the return leg, there are two distinct points where upstairs rads tee in. Therefore due to the moving water there's a small pressure difference across the two upstairs returns causing a small flow.
But following the forum's recommendations, it cured the problem.
True, but the OP there repiped all the returns separately unnecessarily in that case.
If the forum's recommendations were true, he could have still had a shared return as per original, but just made sure that all pipes on each circuit joined together first, then joined the main shared return.

Interested to see what the result is on this one though.
 
Then either drop to the rads downstairs or up out of the floor to the rads upstairs.
As per fixit and my exchange, a question arises -
That return pipe, do the upstairs and downstairs rads:
A) all combine into two separate pipes, before joining together in a single place and flowing into the return pipe visible, or
B) are they interleaved so some (but not all) upstairs pipes are combined with some (or all) the downstairs pipes, and the remaining upstairs pipes combine later in the run?
 
Hi so the piping looks ok in the garage then and follows the 3 t rule? And you think it’s the way the pipes have been run. So if they have the rads from both upstairs and downstairs connecting onto to the same return it’s a problem(interleaved) ? Should they be 2 separate returns for each zone that then combine to the one return that goes back to the boiler? I’m not sure which way it’s been done, but can ask the plumber.
 
so the piping looks ok in the garage then and follows the 3 t rule?
No, that's what we are trying to establish
So if they have the rads from both upstairs and downstairs connecting onto to the same return it’s a problem(interleaved) ? Should they be 2 separate returns for each zone that then combine to the one return that goes back to the boiler? I
Correct, and correct.
 
Hi,
Thanks for the help with this. I've got a response from the plumber. The rad returns all go into the one return (interleaved)
 
Hi

He’s saying to put one way valves on all the radiators now. Is this the best approach?
 
Sounds like the problem is exactly what fixitflav said in the first place :)
I would say best depends on your point of view. That is probably the cheapest option at this stage. But extra valves would reduce the reliability of the system slightly.
 
No that's a bodge
 
What affect will it have? I know it will stop rads warming, is it just that the boiler pump will ware out quicker?. I’m not sure how difficult it would be to run another return would it mean taking all the ceilings down?
 
No, that's what we are trying to establish

Correct, and correct.

Sounds like the problem is exactly what fixitflav said in the first place :)
I would say best depends on your point of view. That is probably the cheapest option at this stage. But extra valves would reduce the reliability of the system slightly.
The thread identified in your #12, can you locate it? I found it the other day by searching for melross (the OP) but it seems to have disappeared. I think it would interest Jeff. One poster (and possibly the installer) suggested a non-return valve, somebody else said (a la ShaunCorbs above) why install extra kit, which could cause problems later, when it wouldn't be needed if the job were done right. The installer made some futile suggestions like smaller pump, but finally modded the pipework. Unfortunately we never saw a pipe layout schematic.
Per my #21, I won't bother posting another sketch as you clearly understand what I mean.
On this job. I haven't got my head round all the piping, but with the cylinder next to the boiler you'd have to make a serious effort to pipe it wrong! On the other job I suspect it was a case of a convenient connection point.
On latest photo, I can see the right-hand pipe into the boiler is an elbow, not a tee, so that theory doesn't hold.
I think I'd like to see a pipework schematic before taking the plumber's word that it's done correctly! I don't know what interleaved means in this context, but to put it simply, the HW cylinder return should join the pipework last, after all other flows are commoned.
Another thought - is it possibly something simple like one of the zone valves failed open?
 
Hi,

Interleaved was mention in a question:

A) all combine into two separate pipes, before joining together in a single place and flowing into the return pipe visible, or
B) are they interleaved so some (but not all) upstairs pipes are combined with some (or all) the downstairs pipes, and the remaining upstairs pipes combine later in the run?

The answer from the plumber was B.
He suggested one way values on each radiator, but people have suggested this is a botch job. So I’ve asked him to pipe it as per A above. Hopefully this should resolve the issue. Anyone think different before they start tomorrow? Sounds silly having to ask when I have the plumber, but I’ve been messed about so much. Appreciate everyone’s input!
 
the HW cylinder return should join the pipework last, after all other flows are commoned.
You've helped me understand, now maybe ii ca help you in return!
Don't be confused by the dhw circuit being special, the issue can occur between any two circuits. In this case delete the cylinder completely, and the tees rule applies to the returns from the two circuits. That is, the return needs to have a single tee/joining point for the whole of each circuit.
 
Please don't spam the forum with links
 
You've helped me understand, now maybe ii ca help you in return!
Don't be confused by the dhw circuit being special, the issue can occur between any two circuits. In this case delete the cylinder completely, and the tees rule applies to the returns from the two circuits. That is, the return needs to have a single tee/joining point for the whole of each circuit.
In the case of a 3-port valve, or a CH zone valve, feeding all CH circuits, the problem doesn't arise, as all circuits are being fed, in the right direction, at once. I hadn't thought about it, but you're right, with a zone valve for each CH zone it can happen if piped in a certain way. Interesting, as one might think individual zone valves would be better. Of course it would be less of a problem than rads getting hot when DHW called, as if heat is wanted in one zone, it's unlikely to be a big issue if another zone gets warm. Not that the mistake shouldn't be avoided. But in hot weather the last thing you want is rads getting hot, apart from the cost of the gas.
 
Status
Not open for further replies.

Reply to Reverse circulation new build in the Plumbing Jobs | The Job-board area at PlumbersForums.net

Similar plumbing topics

Hi everyone, I'm a (somewhat, I hope...) competent DIYer and just want to get some advice if my suspicion on a problem we're having is correct...
Replies
2
Views
730
Hi could anyone give advice please ? I went to look at a new build for sale they are apartments/ one house on top of another all properties will...
Replies
3
Views
461
Hello, I'm seeking advice on resolving the persistent blockage issues with my downstairs toilet. A year ago, I replaced an 80s close-coupled...
Replies
1
Views
429
Hi, I have just had my central heating system "upgraded" for a four bed-roomed detached house. The heating company recommended going from the open...
Replies
9
Views
1K
Just had extension built with 1 new rad and 1 plumbed in towel rail. Since this was connected I have had problems with radiators getting hot with...