Discuss Pipe diameters challenge in the Plumbing Jobs | The Job-board area at PlumbersForums.net

Status
Not open for further replies.
Messages
7
Hi, new to forum and would like a bit of advice if possible.

I have a heating system and a plumber has said I need to increase pipe diameters.

I am confused by this as I can not make numbers stack up to justify the diameter increase.

I have a 22mm diameter feed into a manifold which has 4 16mm diameter pipes feeding radiator network. Each branch has either 3 or 4 radiators on.

The valves on radiators have 8mm internal opening.

When I crunch flow and velocity through pipes etc the total still I'd greater than supply.

I can not understand how increasing from 16 to 20mm will improve system as radiator all heat up very quickly with current configuration.

Cheers

Dickspanner
 
It's the capacity of the rads (kw) are probably more than the capacity of the pipes

15 mm normally around 5kw max but if you have mlcp pipe this will be down to 4kw
 
It's the capacity of the rads (kw) are probably more than the capacity of the pipes

15 mm normally around 5kw max but if you have mlcp pipe this will be down to 4kw

Cheers for response.

Each branch has a maximum of 4kw on it.

The pipes are plastic rather copper.

Regards.

Dickspanner
 
Cheers for response.

Each branch has a maximum of 4kw on it.

The pipes are plastic rather copper.

Regards.

Dickspanner

Would say there fine and if your happy with how it's running I would leave it alone

Why did you call a plumber out if you don't mind?
 
I have a complex hybrid system that I want modifying. It is a long story.

Basically, I want to bypass a part of my system and the engineer said he would not connect the oil fired boiler to the distribution manifold for radiators unless pipe diameter increased.

Cheers.
 
Got to note that pipes can carry enough heat needed to radiators in warmer weather, as much less heat loss, but in depths of winter same pipes, if too small, will not get radiators up to full heat.
Plastic pipes have smaller internal bore compared with copper equivalent.
 
What rating is the boiler? If it's more than about 17kW you'd need to think about 28mm from it to the distribution. You can get higher flow rates through the pipes but run into issues with noise and pressure drop and if it has a built-in pump, higher resistance with smaller pipes might mean you don't get the recommended flow through the boiler.
So far as the rest of the system is concerned, if you've 4 circuits at 4kW each and 80/60C flow and return then 22mm copper feeding them is okay. 15mm copper gives about 5kW. Internal diameter of plastic is a bit less so I'd drop the capacities of the pipes a bit.
 
Hi,
Thanks for response.

The plastic pipe has a internal bore of 13mm. At present the manifold is fed by 22mm from storage tank but the intention is to bypass the storage tank and connect the boiler straight to the radiator manifold and underfloor manifold to give instant heat from the oil boiler instead of drawing heat from the heat exchangers in the storage tank.

I do have a picture of current configuration but do not know how to put a picture on the thread.

I am willing to increase the diameter of pipes from manifold but this will cost circa 1k and when doing the maths of flow vs velocity I am struggling to see benefit of bigger pipes.

Boiler is 22.5kw oil fired.

Sorry if my questions are stupid but I am trying not to spend 1k if I do not need to.

Cheers

Dickspanner
 
Hi,
Thanks for response.

The plastic pipe has a internal bore of 13mm. At present the manifold is fed by 22mm from storage tank but the intention is to bypass the storage tank and connect the boiler straight to the radiator manifold and underfloor manifold to give instant heat from the oil boiler instead of drawing heat from the heat exchangers in the storage tank.

I do have a picture of current configuration but do not know how to put a picture on the thread.

I am willing to increase the diameter of pipes from manifold but this will cost circa 1k and when doing the maths of flow vs velocity I am struggling to see benefit of bigger pipes.

Boiler is 22.5kw oil fired.

Sorry if my questions are stupid but I am trying not to spend 1k if I do not need to.

Cheers

Dickspanner
 
15047172022741203698768.jpg
 
Upgrading the pump could be an option instead of increasing pipe sizes.....
 
Hi,
Thanks for response.

The plastic pipe has a internal bore of 13mm. At present the manifold is fed by 22mm from storage tank but the intention is to bypass the storage tank and connect the boiler straight to the radiator manifold and underfloor manifold to give instant heat from the oil boiler instead of drawing heat from the heat exchangers in the storage tank.

I do have a picture of current configuration but do not know how to put a picture on the thread.

I am willing to increase the diameter of pipes from manifold but this will cost circa 1k and when doing the maths of flow vs velocity I am struggling to see benefit of bigger pipes.

Boiler is 22.5kw oil fired.

Sorry if my questions are stupid but I am trying not to spend 1k if I do not need to.

Cheers

Dickspanner

From the description it sounds like you've got the boiler running into a buffer tank then a heating circuit from the tank to the manifold. For the rating of the boiler and assuming 20C temperature difference on the system you can get away with 22mm but the resistance is quite high and if you're using the same pump to circulate through the boiler and the rads you'd need to check you're getting the correct flow rates. Another issue would be what happens when one or more rads shut down. Do you have a bypass valve on the system to keep the flow up through the boiler?
 
Status
Not open for further replies.

Reply to Pipe diameters challenge in the Plumbing Jobs | The Job-board area at PlumbersForums.net

Similar plumbing topics

Hello all, I’m replacing a concrete paving slab patio in the back yard. The original patio used 50mm deep concrete slabs on hardcore & sand. I’m...
Replies
6
Views
314
  • Question
Ideal Logic 24, Previous problem was that the hot water was only cold or barely warm if the heating was in use. If heating was off and boiler cold...
Replies
2
Views
217
Hi, Can anyone advise as to why the cold water to my bathroom keeps airlocking? This originally happened about 12 months ago and has happened 3-4...
Replies
9
Views
441
Copper pipes, I think its fair to say, is not what it used to be, the copper is getting thin while the cost is going up. Meanwhile, plastic...
Replies
2
Views
309
We run a community village hall and have a large kitchen provided for the use of hirers. This includes a Lincat SLR9 gas cooker which I believe is...
Replies
5
Views
552
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock