Malcz86

Hello,

I'm trying to replace a stuck thermostatic radiator valve on a radiator in a combi boiler system. The valve is stuck in the off position and I've closed the other valve.

I've looked at several advice pages online and a few youtube videos. I started by loosening the nut attaching the valve to the rad to drain the radiator expecting a lot of water to come out. But was just a few trickles. So then moved on to the nut on the pipe coming out of the floor. Now some of the advice I'd seen said that there may be a bit of water coming out here so had towels ready, but as I loosened the nut more and more water started spurting out until the several towels I had were soaked, so I stopped and tightened up again.

What did I do wrong?

I switched the central heating and the hot water to the off position before I started, should I have switched the combi off at the wall?

Should I have just kept loosening the nut and eventually the water would have stopped? obviously wasn't keen on trying this incase it didn't!

Or do I need to drain the entire system to change this one valve? I thought I should be able to do it with just draining the rad?

Any help or advise would be appreciated.
 
It will usually just be the small pin that's stuck on the valve body,a pair of pilers and some lubricant would have probably done the trick.
To do it the way your doing it you will need drain the heating system first.
 
Dump the system pressure through the drain off, if you can find it. If you can't you'll have to dump it through a radiator bleed vent which will take a little bit of time.

Close the lockshield valve on the other end of the rad, taking a note of how many turns it takes to close it - this will save you from having to balance the system later.

Wrap a towel or two round the pipework of your trv. Swap the trv body moving a bit sharpish.

Make sure all nuts are tight, open the lockshield the same amount of turns as you closed it, add inhibitor while you've got the system pressure down, top up to about 1bar.

That'll be a tenner please.....
 
Unless its something you are 100% confident on doing ! call some one in, if you are gong to do it , yes drain the system or you could finish up with very wet floors, and don't forget to replace the inhibitor when you refill system, its the so called simple jobs that cause the most problems,
 
Thanks guys, I think I'll have to get someone out. I'm happy working with a spanner but draining the system sounds like a lot of trouble and I wouldn't know where to start with getting the pressure right or adding an inhibitor.
 
I did try WD40 but the actual thermostatic valve top won't come off. Have tried loosening the screw below it but it won't turn either. So I think replacing the valve is the only option.
 
Dump the system pressure through the drain off, if you can find it. If you can't you'll have to dump it through a radiator bleed vent which will take a little bit of time.

Close the lockshield valve on the other end of the rad, taking a note of how many turns it takes to close it - this will save you from having to balance the system later.

Wrap a towel or two round the pipework of your trv. Swap the trv body moving a bit sharpish.

Make sure all nuts are tight, open the lockshield the same amount of turns as you closed it, add inhibitor while you've got the system pressure down, top up to about 1bar.

That'll be a tenner please.....

You're cheap!
 
You're cheap!

Look at it this way, once I've got his bank details I write a quick promissory to my good friend M'butu Ndonkwe of the nigerian central bank.

He's found tens of thousands of pounds belonging to me, just need to send him 500 for admin fees.

What could possibly go wrong?
 
I did try WD40 but the actual thermostatic valve top won't come off. Have tried loosening the screw below it but it won't turn either. So I think replacing the valve is the only option.

what valve have you got?
 
Status
Not open for further replies.

Reply to Trying to replace thermostatic radiator valve in the Plumbing Jobs | The Job-board area at PlumbersForums.net

Similar plumbing topics

Hi, Can anyone advise as to why the cold water to my bathroom keeps airlocking? This originally happened about 12 months ago and has happened 3-4...
Replies
9
Views
465
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock