Discuss Trianco Eurostar Oil Boiler Conundrum in the Plumbing Jobs | The Job-board area at PlumbersForums.net

Status
Not open for further replies.
Did you post pics and tips on replacing the seals on a trianco eurostar balanced flue? I am at present wrestling with this cycling which goes away if I remove the air inlet hose, blanking off resulting hole to the flue. Any help would be much appreciated!
thanks creens
Is there enough combustion air in the room to leave as conventional?
 
Is there enough combustion air in the room to leave as conventional?

the boiler is in a dedicated room vented to the rest of the house. Noisy but appears to run ok. probably less efficient using cold air?
thanks creens
 
Work out the air needed for the output and you may need to add some air bricks (which the wife will cover up).
 
Work out the air needed for the output and you may need to add some air bricks (which the wife will cover up).

Thanks for the reply. Seems to be running OK. Will get it checked when engineer becomes available. I would still like to look at replacing the two O rings in the flue though if it's not too difficult.
 
It's not 'O' rings, it 2 x red rubber seals that go hard, shrink and crack letting combustion products escape. I have changed some on a flue, then about 6 months later the same problem occurred, so I ended up installing a new Grant.
Changing the gaskets was a half day job, then to do it again did not out way the savings they would make with a newer boiler, turns out they are very pleased with it as they have saved a lot of money in the few years of having the new boiler.
My suggestion, replace the boiler, Trianco's are naff.
 
It's not 'O' rings, it 2 x red rubber seals that go hard, shrink and crack letting combustion products escape. I have changed some on a flue, then about 6 months later the same problem occurred, so I ended up installing a new Grant.
Changing the gaskets was a half day job, then to do it again did not out way the savings they would make with a newer boiler, turns out they are very pleased with it as they have saved a lot of money in the few years of having the new boiler.
My suggestion, replace the boiler, Trianco's are naff.

Thanks for the comments MarkOil - stuck with the Trianco for present
 
Photos attached


P1050732.jpgP1050730.jpgP1050731.jpg




Photos 2 and 3 showing new gaskets in place before reassembly. Some earlier models used heat resistant silicone rather than gaskets so if thats the case, be prepared to get messy!
 

Attachments

  • P1050729.jpg
    P1050729.jpg
    53 KB · Views: 21
Last edited:
Status
Not open for further replies.

Reply to Trianco Eurostar Oil Boiler Conundrum in the Plumbing Jobs | The Job-board area at PlumbersForums.net

Similar plumbing topics

I'm looking for some advice on a frustrating problem I'm having with my old Eurostar 50-60s oil boiler please? Although it's old, most parts...
Replies
3
Views
761
I have a customers trianco burner that starts from cold ok for a few minutes (say 3minutes) then locks out then will not stay on. Boiler had not...
Replies
1
Views
633
Oil boiler (now~15 years old) unvented system with 17 radiators. We moved in 5 years ago and I had to keep bleeding the same radiator. The bleed...
Replies
1
Views
261
Hi, Over the past few months, my wife and I have noticed a constant pulsing sound throughout the house which is particularly noisy at night (this...
Replies
4
Views
678
Had our gas Baxi Combi inspected and serviced today, as it has been every year. Gas safety cert issued and says all okay, but engineer gave what I...
Replies
4
Views
586
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock