Hi

We've got a Vaillant ecotec plus 428 that doesn't seem to want to supply any heat to the radiators despite the hot water working just fine.

Of some importance (I think) is that there is no radiator symbol displayed on the boiler screen, only a tap.

We have a wireless thermostat (Altech ALTHC015) with fresh batteries calling for heat connected to a box displaying a red and green light which I believe means power and connectivity are fine.

I have so far tried turning everything off including the Honeywell ST9400C controller and removing the batteries to reset anything that might be causing a bug as last year it turned out the wireless thermostat had just bugged and resetting it worked fine.

The boiler displays s30, indicating no call for heat. Manually firing the boiler does not make the radiator symbol appear and they don't get warm.

Any advice would be greatly appreciated.

Warmest regards, Matt
 

Attachments

  • DSC_3820 2.JPG
    DSC_3820 2.JPG
    189.8 KB · Views: 9
Is there an override on the thermostat? Try this. Could be a faulty motorised valve, or could be the thermostat. Do you have any test gear?
Thanks for your reply. There doesn't appear to be anything on the Altech unit to override; on the Honeywell controller there is an override button and I can set it to run continuously (If that's what "Cont" means in this context) but no luck on either. What would you define as test gear?

Warmest regards, Matt
 
If the receiver green light is on, that shows the communication is working.
Do you know what is happening with the motorised valve(s)?
You appreciate (I believe for your system) the Altech controls the motorised valve, and within the motorised valve is the switch that calls for heat from the boiler. If the valve is not moving that switch won't be operating.
 
If the receiver green light is on, that shows the communication is working.
Do you know what is happening with the motorised valve(s)?
You appreciate (I believe for your system) the Altech controls the motorised valve, and within the motorised valve is the switch that calls for heat from the boiler. If the valve is not moving that switch won't be operating.
Thanks for your replies. I've looked into the motorised valves and I've found two of them. Both can be moved using the manual bit on the back fully over to one side and back again. Should there be anything outwardly obvious happening with the valve when it is operating?

I have a multimeter so I can test things if required.

The controller appears to be connecting to the boiler just fine as the boiler displays when the pump is running.

Whilst I am here I have another question to add. We have always had, since we moved here, an issue with the boiler constantly cycling e.g. rapidly heating up to 70 degrees within several seconds and then shutting down with a flashing radiator symbol for a few minutes before firing again; is this anything I can change? I've got it on video, if anyone wants to take a look I'll upload it.

Warmest regards, Matt
 
Need to link out the heating thermostat
 
On the reciever need to check if it’s outputting live / call to the system as it could be just the room stat is dead
 
You need to find the wiring center and put the heating on.

Then find the live from the thermostat to the brown wire for the heating motorised valve, test (on voltage ac) between neutral/earth and the brown (live) and the reading should be 240vac or close to it. If that is good then proceed to test between neutral/earth and orange and should have 240vac.

If you don’t get 240vac on the neutral and brown, then it could be a dead room stat.
 
Last edited by a moderator:
Thank you so much for your replies so far, they've been very helpful as with your assistance I've narrowed it down to the wireless room stat being faulty; once this is bypassed the heating works. Can anyone tell me what the best replacement (same functionality) for the mentioned above thermostat and controller would be?

Warmest regards, Matt
 
There’s literally 100’s on the market, just stay clear of the same one as yours, Salus or Secure/Horstmann.
Ah, okay thanks for the heads up as I was perhaps looking at the Salus rt310rf as a fairly direct replacement but if they're no good I'll keep looking. The combi pack 4 looks great but has a lot of extra functionality I don't really need at the moment, thank you for the suggestion though, it remains on my shortlist.

Warmest regards, Matt
 

Reply to Vaillant Ecotec plus 428 No heating in the Central Heating Forum area at PlumbersForums.net

Similar plumbing topics

  • Question
Ideal Logic 24, Previous problem was that the hot water was only cold or barely warm if the heating was in use. If heating was off and boiler cold then would get hot water most of the time. Changing the flow cartridge about 2 years ago (when I moved in) solved this problem enough to suffer it as...
Replies
2
Views
160
We run a community village hall and have a large kitchen provided for the use of hirers. This includes a Lincat SLR9 gas cooker which I believe is a 23.8Kw appliance with all six burners and oven on max. This was installed some 10 years ago and has passed all subsequent Gas Safety inspections as...
Replies
5
Views
501
Hi all I'm hoping someone can shine a light on this for me Since our stop tap on the pavement has now been filled with sand for whatever reason, we are relying on our property fitted stopcock (this is outside on our garage wall) Unfortunately turning this to the closed position only reduces...
Replies
3
Views
292
Creating content since 2001. Untold Media.

Newest Plumbing Threads

Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock