Evening all,

So I've been losing pressure from my boiler on a daily basis and having to top it up. The pressure gauge is up at around 3.5 bar when the boiler is on so I assumed the expansion vessel has either failed or is low on pressure. I had a look on both the Cimms website (the EV is a Cimm RP250 10 litre) and it shows that it requires 1.5 bar of pressure. The sticker on the EV shows 0.8 bar (I think). Anyway, to stay on the safe side I decided to stick around the 1 bar mark. I checked the shraeder valve and air came out with no water which seemed promising. I topped it up to 1 bar and then tried again but there's no difference. It took very little to fill it to one bar (about 1 second) so I'm assuming the correct pressure is 1.5 bar. Any thoughts?

Thanks

Steve
20210106_114745.jpg
Screenshot_20210106-114511_Drive.jpg
 
What pressure are you running the system at?
Did you de-pressurize the wet side before charging the dry?
The wet side needs to remain at zero pressure whilst charging the dry side.
 
What pressure are you running the system at?
Did you de-pressurize the wet side before charging the dry?
The wet side needs to remain at zero pressure whilst charging the dry side.
The system usually runs at around 1-1.5 bar. Yeah I de-pressurised the heating circuit and then isolated the flow and return. The pressure gauge rose to 1 bar as I charged the EV. Not sure if that answers your question but thanks for the reply.
 
The system usually runs at around 1-1.5 bar. Yeah I de-pressurised the heating circuit and then isolated the flow and return. The pressure gauge rose to 1 bar as I charged the EV. Not sure if that answers your question but thanks for the reply.
You need to pressurise the dry side and use a gauge on that side.
No pressure should be allowed to build in the wet side as you charge it.
I would charge it to 1 bar.
If this is internal to the boiler you are supposed to be gas safe registered. Did you know that?
It looks on the photo as the vessel is on the rear?
 
You need to pressurise the dry side and use a gauge on that side.
No pressure should be allowed to build in the wet side as you charge it.
I would charge it to 1 bar.
If this is internal to the boiler you are supposed to be gas safe registered. Did you know that?
It looks on the photo as the vessel is on the rear?
Thanks mate. No I wasn't aware. I'll get someone round to take a look. Thanks for the advice.
 

Reply to Correct Expansion Vessel Pressure in the Central Heating Forum area at PlumbersForums.net

Similar plumbing topics

Every two weeks or so I have to go and top up the system because the hot taps are running cold. Boiler display is flashing 0.6 bar and I fill up to 1.3. I've had an engineer look inside the boiler and he can't see anything wrong. I've checked the pipes all over the house and cannot see any...
Replies
2
Views
237
P
We run a community village hall and have a large kitchen provided for the use of hirers. This includes a Lincat SLR9 gas cooker which I believe is a 23.8Kw appliance with all six burners and oven on max. This was installed some 10 years ago and has passed all subsequent Gas Safety inspections as...
Replies
5
Views
502
Creating content since 2001. Untold Media.

Newest Plumbing Threads

Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock