One of these yellow tags

Screenshot_20181219-121823_WhatsApp.jpg


Screenshot_20181219-121823_WhatsApp.jpg
 
Board left of solenoid
 
There you go mip 75 mbar

Mop 23

So test would be 82.3 so 83mbar so you could test the mdpe at 100 mbar
 
There you go mip 75 mbar

Mop 23

So test would be 82.3 so 83mbar so you could test the mdpe at 100 mbar


Thanks for the calculations. As I don't have a gauge that does 100mb, I could do this as you suggested in the 1st place to 1 bar as it is only a soundness test after all. But, as you say it is commercial so should I avoid.

Well if one thing that comes out of this I have learnt a bit about cost of fittings for this size pipe and strength testing.

Thank you all
 
Upto you as it's not connected you could say your only testing the pipe for defective not carrying gas
 

Reply to Pressure testing 63mm gas pipe in the Plumbing Jobs | The Job-board area at PlumbersForums.net

Similar plumbing topics

I have done pressure test for 2" high pressure pipe line by closing the pipe with rubber plugs at the ends. It was 3 bar and I kept it for 24...
Replies
6
Views
307
I've air tested pipework for years, typically 4 bar for 30 minutes. I've never had an issue with any pipework that has passed that test...
Replies
8
Views
514
Hi, Non-professional / knowledgeable person here. I'm a Brit in Romania who volunteers for a charity building an old peoples home for needy old...
Replies
3
Views
410
I have been facing central heating low pressure on unvented hot water RM Cylinders but can't see any leak on the PRV, expansion vessels and...
Replies
2
Views
505
losing pressure
L
British Gas servicing the above boiler ramped up the boiler to maximum in the installer menu to do flue gas analysis. They also measured the...
Replies
4
Views
592
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock