After being woken up a few times by clicking pipework when heating not on looked at setup in boilerhouse. Trying to figure out why there are 2 stats in there. One is Honeywell L641B1004 on flow pipe from boiler other is a Honeywell frost stat, model unknown but lowest setting is 5degC, set at 5 degC.
I see no need for boiler to run at temp of 5deg C, yes maybe if around 0-1 degC. Have seen I can get a froststat that goes from -5 to 15 should I replace the Honeywell with one of these. Can someone enlighten me as to what this pipe stat is suppsed to accomplish.
Thanks
 
Frost stat puts power to pipestat if below set temperature runs boiler/pump,
When pipestat satisfied shuts off,
Correct honeywell frost stat is
T4360a
I certainly won't recommend setting frost stat to 0° chance of frozen pipework.
 
Hi
Yes lying in bed last night the penny dropped as to why 2 stats. I will get a replacement frosts stat as I am sure at times the system has run when the temperature has been above 5 deg C which is pointless. To my mind a frost stat shouild do what it says on the box protect from frost. Frost does not occur at 5 degC
 
To my mind a frost stat shouild do what it says on the box protect from frost. Frost does not occur at 5 degC
The frost-stat does not measure the lowest temperature at every point in the system, it samples the temperature at one place. Also, the sensors used are not exactly precision devices and aren't recalibrated annually. So, taking these observations together, allowing a 5°C margin of error seems prudent and necessary particularly as the consequences of freezing can be quite serious.
 
Frost stat kicks boiler in and pipe stat disables frost stat once warm.

Things to look out for. Frost stat screwed directly to stone/brick wall, mount it on a block of wood. Frost stat set too low, frozen pipes. Pipe stat not on return. Pipe stat set too low or too high.
 

Reply to Why 2 stats in remote boiler house in the DIY Plumbing Forum area at PlumbersForums.net

Similar plumbing topics

We are from Alberta, and I own an electrical company. I have been asked by a BC Mechanical P. Eng. to install an emergency STOP button at the man-door to the boiler room. It's intent is to 'halt' the operation of the boilers in the room should there be an emergency. He is demanding that I do...
Replies
5
Views
275
S
Hi, I seemed to have a blockage in kitchen sink. A plumber came and cleared all the pipework that is visible inside my home (there was debris and pebbles!) We saw that the pipe that takes water down the gutter was visibly full to the top. He said he will return with a coil to push through...
Replies
2
Views
112
S
Hi, Can anyone advise as to why the cold water to my bathroom keeps airlocking? This originally happened about 12 months ago and has happened 3-4 times since. It’s an upstairs bathroom, fed from a tank in the attic. The tank is about 8 Meters away and feeds a bath, sink and toilet. The tank...
Replies
9
Views
362
Creating content since 2001. Untold Media.

Newest Plumbing Threads

Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock