37
Hi

I have a Telford tempest unvented cylinder and I'm finding that when the hot water is on and I turn it off on the programmer the TPRV opens and let's the hot water out. Only stops running when it cools down again.

What I find strange is that it only happens if I turn the programmer off. If I have the immersion heater on all day it doesn't happen. I thought it would be the TPRV but surely this would open if the immersion heater was on aswell and was faulty?

Any ideas?
 
1. These cylinders need an annual service. Has this been done?
2. If the programmer is part of the indirect (heating coil boiler driven) circuit, I would suspect a problem with the motorised control valve, particularly if a three port valve has been used alone, rather than the cylinder having a dedicated 2 port.
3. The immersion heater may not be raising the temperature high enough to trigger the TPRV.
4. You need a G3 qualified technician to investigate and rectify. The cylinders are NOT DIY.
 

Reply to Telford tempest cylinder fault? in the USA area at PlumbersForums.net

Similar plumbing topics

Hi everyone, Looking for a bit of advice, recently went to a job where heating was operating when called for however not for the hot water. I...
Replies
8
Views
373
Hi, Can anyone advise as to why the cold water to my bathroom keeps airlocking? This originally happened about 12 months ago and has happened 3-4...
Replies
9
Views
421
  • Question
Ideal Logic 24, Previous problem was that the hot water was only cold or barely warm if the heating was in use. If heating was off and boiler cold...
Replies
2
Views
199
Hi all I'm hoping someone can shine a light on this for me Since our stop tap on the pavement has now been filled with sand for whatever reason...
Replies
3
Views
319
I want to reconnect some outbuildings to an existing water supply. The supply pipe is old 22mm MDPE and buried for a fair distance so not going...
Replies
1
Views
310
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock