Discuss servicing adverts £49 in the Plumbing Jobs | The Job-board area at PlumbersForums.net

Status
Not open for further replies.
But you will need one from April to fit a boiler or cooker.
Thats all I need my FGA for.
They may be off their heads, but they are only doing what others are doing, hence the price is cheaper.
 
But you will need one from April to fit a boiler or cooker.
Thats all I need my FGA for.
No you won't but you will need a ticket to say you know how to use and interpret one. Only needed if the manu asks for it which most won't as it will affect their sales.
 
But you will need one from April to fit a boiler or cooker.
Thats all I need my FGA for.
They may be off their heads, but they are only doing what others are doing, hence the price is cheaper.

No, is that not Boilers and Fires after April?
 
No you won't but you will need a ticket to say you know how to use and interpret one. Only needed if the manu asks for it which most won't as it will affect their sales.


I do work for a few local builders, landlords, companies. All of these will want a CPA report with every install and service, as will customers when they get wind. Plus you may be shocked by the changes to boiler manufacturers requirements from April 1st.
 
No you won't but you will need a ticket to say you know how to use and interpret one. Only needed if the manu asks for it which most won't as it will affect their sales.

How will it affect sales, every decent heating engineer I know already owns one and knows how to use it.
The only ones it will affect are the dodgy ones with no gas safe, or the ones who cannot be bothered to move with the times and adjust to todays requirements. Not many of them out there I hope, so dont see a problem with sales only with stubborn, pig headed engineers. I am sure none of us are in that category, are we??
 
Maybe every decent self employed heating engineer has one or should have one but there are tens of thousands of competent and qualified employed fitters doing installs day in day out who don't. There is no need or requirement to do a cpa on commissioning for mainstream boilers.
From some mi's

Worcester
NOTICE: The combustion settings on this
gas-fired boiler have been checked, adjusted
and preset at the factory for operation on the
gas type defined on the data plate.
No measurement of the combustion values
are necessary provided there is a meter
installed allowing the gas rate to be checked.
DO NOT ADJUST THE AIR/GAS RATIO VALVE.

Vaillant
The boiler is supplied ready adjusted and no further gas
adjustments are necessary, however both the gas inlet
working pressures and maximum gas rates should be
checked as detailed in 5.10.2 and 5.10.3.

Ideal
Please Note: The combustion for this appliance has
been checked, adjusted and preset at the factory for
operation on the gas type defined on the appliance
data plate. No measurement of the combustion is
necessary. Do not adjust the air/gas ratio valve.

Viessmann
Vitodens100 is factory-set for natural gas.
During commissioning or maintenance, the CO2 setting can be measured at the
boiler flue adaptor testpoint. Checking CO2 levels is not a requirement.

It remains to be seen what will change on mi's with regards to commissioning instructions. It will affect boiler sales as the majority of installs are done by companies who's installers don't own or have access to an analyser. If one brand of popular boiler starts insisting on a cpa the sales will go to those who don't as the manu's know fine well.
They would all like to insist on it but it will be a brave one who is first to go for it.
Things will change eventually but not overnight.
The bottom line with gas safety is really all about money if we are honest.
 
I do work for a few local builders, landlords, companies. All of these will want a CPA report with every install and service, as will customers when they get wind. Plus you may be shocked by the changes to boiler manufacturers requirements from April 1st.
i have yet to meet a builder,landlord,letting agent or customer who knows what a cpa is let alone ask for one,and unlike yourself i do a awful lot of servicing
 
It has been in my last few Landlords Magazines, so if other Landlords are reading it they should know too. So I assume these letting agents get the same or similar magazine. Always lots of info regarding Gas Safety in the magazine. Letting them know what they should be expecting from us lot.
 
How will it affect sales, every decent heating engineer I know already owns one and knows how to use it.
The only ones it will affect are the dodgy ones with no gas safe, or the ones who cannot be bothered to move with the times and adjust to todays requirements. Not many of them out there I hope, so dont see a problem with sales only with stubborn, pig headed engineers. I am sure none of us are in that category, are we??
i am!
 
You are correct. I too have worked for them in the past. How can you prove the boiler is safe inside. No holes in casing.
No safety device by-passed by a.n. other.(I have seen overheats linked out)
Don't forget, even if you haven't taken the case off. You have stiil 'WORKED ON' the appliance.
 
I don't really know what the discussion is about here.
We all know a lot of engineers now treat a service as a check (major company's included).

They FGA, gas rate, check working pressure and remove the case only to visually inspect and tightness test at the meter).(If that much)

Is this a true service and will it prevent future faults?.......................No, but you can fill out a CP12 with the info gained and thats what people want.

I'm not saying I agree with this and if I was doing a service privately and by the MI's it would take at least an hour but the people that lead this industry (eg the big companys) allow the engineers about 30 mins per service and there is no way a full and correct service can be carried out in that time.

Will Gas Safe act on it? Of course not.
Like we have mentioned in previous threads Gas Safe are Toothless wonders and there is no way they are going to take on the big companys as it would cost money and that is all industry is worried about.

The engineers out there that are doing a full and correct service I salute you but you are putting yourself at a big disadvantage against the big boys that will give the customer the same piece of paper for less.
 
As the customer wont know any difference, only that you are trying to charge double, you will also be losing work.
 
I would rather charge double and do the job properly, knowing the customer has got value for money. My rates are my rates and i wont let myself be bullied into charging less by customers or heating engineers and companies charging stupidly low rates. Anyway i dont see your argument Halesowen as BG charge more than me and your saying they just stick a FGA in, so who is providing a better quality of service, the sole trader who charges a similar rate to BG but does a strip down service or the big companies who charge the same amount but dont do a 'proper' service. Customers eventually see this, although they learn the hard way usually. (i just used BG as an example, i have no personal vendetta with them)
 
there are plenty of examples of people who have done a proper service and the customer has been like "WELL BG DIDNT DO THAT WHEN THEY DONE IT" and feel they are getting more value for their money

i usually refer to MIs which ALWAYS tell you to remove casing to clean condensate trap etc
 
Having a service done for £49.00 is a great offer. What I ask you to remember is the price of 50-60 pounds was standard by BG and to that matter everyone got to see that services cost in the region of that amount. We have charged as low as £45.00 per service. the rule of thumb was that the boiler would be strip down. Any service that included having the burner removed and the combustion chamber cleaned and all the safety devices were working constituted a good service. On modern boilers services only take around 20 - 30 mins. Thats by engineers who have done this type of work for years. I do not know of any engineer worth his salt that would take an hour to service a modern combination boiler. Now if that appliance was a back boiler I would suggest that that type of appliance is two appliances. A fire and a boiler and they both need cleaning ( see where im coming from ). If your interested we strip down service, clean and as mentioned before shove a probe up your flue and check the results for £55.00 per service nationwide.
 
For the record I too would rather have the casing removed and burners cleaned etc.
I am only saying that most companies dont do this, I have never said i dont do it as i have said numerous times, I dont do servicing, I pass this on to my Henry the Hoover colleagues.
 
I agree with mfgs, most modern boilers do not need stripping down and cleaning if the flue gas readings are correct. Stripping down new boilers for the sake of making the job take longer is a waste of time and can lead to problems in the long run. I do this for £35 and fill in the benchmark service record . If it is an older boiler then i charge accordingly.
 
There is just one thing I personally hate about the analyzer service. When you go through any safety check the cp12 askes VISUAL INSPECTION OF FLUE. How can you do that with the casing on. And how can you ensure the safety devices are operating correctly.

The GSUR demand that this is done on every service. A safety Check is not a service and should be advertised differently
:yes::yes::yes::yes:
 
BG don't charge for their check it is included in the maintenance contract.

BG started with the analyser "service" about 15 or so years ago. Part of their 3 star cover was to include an annual service. As we all know balanced flued boilers generally are normally pretty clean inside, so they decided it was a waste of manpower to have someone actually strip it down. Much quicker and cost effective to "check" if it really needed servicing. So their included service really became a check. All the major contract providers are the same.

Now analysers are commonplace and actually opening a band A is only advised if the readings say so, this practice has become the norm for all boilers. Its should be called as it is though, a combustion check which is totally different from a service.

An analyser it not necessary or required to service a std boiler but it is another tool to use as part of one. You don't need to own or have access to one either, just be able to interpret the results.
Btw, anyone who sticks an analyser in an open flue boiler as an annual check and accepts the readings as being fine is off their head.

Yeah I think you are spot on there it should be called a check and not a service if all you do is stick your probe in the flue. I understand this has become the norm now for all band A boilers, do you personally think it is worth taking the case off if the combustion analysis is perfect? Or are you just wasting time as you know everything will be fine?
 
Combustion analysis doesnt tell you if there is a leak in the boiler which is causing the case to rust does it? It doesnt tell you alot of things. I have had a vaillant with a cracked flue collector, which is ID, but it passed the intial combustion check.
 
Although most gas engineers will argue with this.
A modern gas boiler needs very little in the way of a service. In fact in may cases it is just measuring the current
burning of the boiler and if this meets requirements the boiler can be left with only a basic check of other parts.
I consider £49 reasonable. I will quite happily service gas boilers all day for £49 a shot.
 
I do a full boiler service for £40, I am just starting out on my own, i am currently employed. it's more of a temporary price till i get enough customers.
check everything for this.
remove and clean burner/heat exch, gaskets extra if condencing boiler
check bp,wp at boiler and meter, gas rate, flue annalyser, cheack all rads working, tanks in loft, loads more, ive got a full list on my website, I know thats too cheap and I don't want to lower rates in my area but its a good way to get my name out there to new customers. Once I have a decent work load and leave my company I am with now, i plan to increase prices as I would like to think the customers will come back because I did a good job not just because its cheap.
 
I do a full boiler service for £40, I am just starting out on my own, i am currently employed. it's more of a temporary price till i get enough customers.
check everything for this.
remove and clean burner/heat exch, gaskets extra if condencing boiler
check bp,wp at boiler and meter, gas rate, flue annalyser, cheack all rads working, tanks in loft, loads more, ive got a full list on my website, I know thats too cheap and I don't want to lower rates in my area but its a good way to get my name out there to new customers. Once I have a decent work load and leave my company I am with now, i plan to increase prices as I would like to think the customers will come back because I did a good job not just because its cheap.

You'll keep some customers. Others will just go for cheapest always. Pay peanuts they get monkeys.
 
Confucious Say!
It always easier to reduce prices than increase them!
 
SOme think that if you are the cheapest, then you must be the worst. I prefer to charge what others locally are doing but do a better job, customers will always come back and recommend. But do a bad job they will also slate you to freinds and family.
 
the trouble with doing a service for £40 is your customers will always expect it to be that cheap, and when you put your prices up someone else will be cheaper than you and you will lose most of them. you cant run a business on these sort of prices you will become a busy fool for a while and then go back to working for someone because of less hassle. i get really annoyed when i see vans with boiler servicing prices on the back doors not only does it look desperate, it drags the professionalism of the trade down . start as you mean to go on, charge a decent rate and promote good workmanship thats the way forward.
phew ! im goin to bed now
 
[. And how can you ensure the safety devices are operating correctly.


:yes::yes::yes::yes:[/QUOTE]

Just turn the gas off below the boiler and the boiler should try to relight. Eventually it should go to lock out.
Saftey device working correctly!
 
depends on applaince, boiler with permanant pilot should click within 20 secs, if it takes longer than safety device is not opperating in required time, also check gas valve for letby, wont always show up on tigtness test, if small drop. Gas fires have a longer time allowance on there safety device. Just turning off gas and waiting to boiler to lockout is not proof the safety device is working correctly
 
depends on applaince, boiler with permanant pilot should click within 20 secs, if it takes longer than safety device is not opperating in required time, also check gas valve for letby, wont always show up on tigtness test, if small drop. Gas fires have a longer time allowance on there safety device. Just turning off gas and waiting to boiler to lockout is not proof the safety device is working correctly

and the safety check for a gas cooker (just testing)
 
depends on applaince, boiler with permanant pilot should click within 20 secs, if it takes longer than safety device is not opperating in required time, also check gas valve for letby, wont always show up on tigtness test, if small drop. Gas fires have a longer time allowance on there safety device. Just turning off gas and waiting to boiler to lockout is not proof the safety device is working correctly

aren't we allowed 60 seconds for boilers ?
 
That was off the top of my head mate, ive got a book somewere, pretty sure its 20 but will check for sure later. Was just trying to point out that you cant test a safety device just from iscolation valve
 
FSD shutdown times
* BOILERS 60 SEC
* W / AIR HEATERS 60 SEC
* COOKERS (oven) 90 SEC
* WATER HEATERS 90 SEC
* D.F.E. GAS FIRES 120 SEC
* OTHER GAS FIRES 180 SEC
 
Last edited:
depends on applaince, boiler with permanant pilot should click within 20 secs, if it takes longer than safety device is not opperating in required time, also check gas valve for letby, wont always show up on tigtness test, if small drop. Gas fires have a longer time allowance on there safety device. Just turning off gas and waiting to boiler to lockout is not proof the safety device is working correctly

think you need to check your 20 sec for shut down of boiler FSD, regs say within 60 secs not 20

replied to this post before reading that others had done so, on the testing of the FSD its disaponiting how many reassessment guys describe the testing of a boiler FSD as "shut the gas and listen for the click" aaaahhh that drives me mad, i tell them "no i told you to confirm the FSD is working, you havent done that" they are amazed that they need to confirm the gas isnt passing through by using their u guage, dont know what these guys are doing every day while servicing the old appliances
 
Last edited by a moderator:
Status
Not open for further replies.

Reply to servicing adverts £49 in the Plumbing Jobs | The Job-board area at PlumbersForums.net

Similar plumbing topics

We run a community village hall and have a large kitchen provided for the use of hirers. This includes a Lincat SLR9 gas cooker which I believe is...
Replies
5
Views
563
  • Article
A Plumber Who Worked Illegally Gets A Suspended Sentence After Falsely Claiming To Be Gas Safe Registered. A Plumber in Herefordshire was...
Replies
0
Views
256
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock