Discuss Reliability of fault codes potterton in the Central Heating Forum area at PlumbersForums.net

Messages
2,199
I assume that is a TMV to give the required much lower UFH temperatures required.
If one of the actual boiler trips is the deltaT between the flow & return then most trip at a deltaT of 30C so perhaps this is what is tripping the boiler but this would/should only happen if no ABV is fitted, you have which we assume is working OK, you can see the effect of by pass vs no pass in the attachments if my calcs are correct.
I think the first thing to establish is what actually are the conditions that flag this low flow circ trip, there is no explanation in your manual and mine might be completely wrong.

I am just assuming UFH requirements but the relative flows and temps should still be correct.

I see the UFH TMV is on the left of the manifold but havn't a clue what you mean by a TRV on the manifold (circled).

You don't have permission to view attachments. Attachments are hidden.


You don't have permission to view attachments. Attachments are hidden.
 

Attachments

    You don't have permission to view attachments. Attachments are hidden.
Last edited:

ShaunCorbs

Staff member
S. Mod
Plumber
Gas Engineer
Messages
28,890
Solutions
1
Yep, it has a TRV to the bottom left of the manifold, it's hidden away a bit. I've circled it in this photo.

Why? Is that significant?

Thanks :)

No sorry on the rad that the grey hep supplies can you remove it to test something eg the trv head
 
Messages
24
I assume that is a TMV to give the required much lower UFH temperatures required.
If one of the actual boiler trips is the deltaT between the flow & return then most trip at a deltaT of 30C so perhaps this is what is tripping the boiler but this would/should only happen if no ABV is fitted, you have which we assume is working OK, you can see the effect of by pass vs no pass in the attachments if my calcs are correct.
I think the first thing to establish is what actually are the conditions that flag this low flow circ trip, there is no explanation in your manual and mine might be completely wrong.

I am just assuming UFH requirements but the relative flows and temps should still be correct.

I see the UFH TMV is on the left of the manifold but havn't a clue what you mean by a TRV on the manifold (circled).

You don't have permission to view attachments. Attachments are hidden.


You don't have permission to view attachments. Attachments are hidden.

Wow John!! Thanks for doing those calculations and drawing that out. I'm embarrassed to say that I'm struggling to interpret the findings of them. Am I correct in thinking the "DeltaT" is the difference in temperature between the flow and return? And, if I have an automatic bypass fitted then I need to maintain a difference of 15 deg between the flow and return or the boiler will trip? However, if I don't have an automatic bypass fitted (which I don't now as far as I'm aware) then I can have a difference of 30 degrees between the flow and return?

So, if I'm correct above, I'm better to not have a bypass? Is that correct?

Thank you again for your hard work on this. I'll answer other questions/support in another reply on here. :)
 
Messages
24
No sorry on the rad that the grey hep supplies can you remove it to test something eg the trv head

Apologies, all. It seems that (what I thought) was a TRV on the UFH manifold is, in fact, a "TMV" (Thermostatic Mixing Valve). as oppose to a Thermostatic Radiator Valve (I got a clue when I Googled TRV and saw that the "R" stands for Radiator :) )

@ShaunCorbs yes, there's a TRV on the radiator that has the grey pipe going to it and I can remove and test anything you would like? Just let me know what you'd like me to do and I'll try it. Thanks :)
 
Messages
2,199
Wow John!! Thanks for doing those calculations and drawing that out. I'm embarrassed to say that I'm struggling to interpret the findings of them. Am I correct in thinking the "DeltaT" is the difference in temperature between the flow and return? And, if I have an automatic bypass fitted then I need to maintain a difference of 15 deg between the flow and return or the boiler will trip? However, if I don't have an automatic bypass fitted (which I don't now as far as I'm aware) then I can have a difference of 30 degrees between the flow and return?

So, if I'm correct above, I'm better to not have a bypass? Is that correct?

Thank you again for your hard work on this. I'll answer other questions/support in another reply on here. :)
Yes, the deltaT is the difference between the flow/return and ideally should be kept ~ 15/20C but with UFH only on because of the ratio of boiler flow to UFH flow then you can have a huge boiler deltaT depending on the boiler flow temp and the UFH (mixed) flow temperatures which means that you can have a very high undesirable boiler deltaT which on some boilers will initiate a trip if it exceeds 30C or so, I only used the attachments to show how the deltaT can change with/without by pass.

You have a bypass which is set very low IMO, phot 7 post#12, see posts #15&16 as well.

I find it a bit strange that the systems work fine when running separately but not with both on together.

Can you say how long it takes the boiler to trip if you have, say, the Rads on and you then call in the UFH, does it trip immediately or is there a time delay or whatever.
If its not a immediate trip can you monitor the boiler flow temperature immediately before and after calling in the second system to see if it changes dramatically.
 
Messages
24
Yes, the deltaT is the difference between the flow/return and ideally should be kept ~ 15/20C but with UFH only on because of the ratio of boiler flow to UFH flow then you can have a huge boiler deltaT depending on the boiler flow temp and the UFH (mixed) flow temperatures which means that you can have a very high undesirable boiler deltaT which on some boilers will initiate a rip if it exceeds 30C or so, I only used the attachments to show how the deltaT can change with/without by pass.

You have a bypass which is set very low IMO, phot 7 post#12, see posts #15&16 as well.

I find it a bit strange that the systems work fine when running separately but not with both on together.

Can you say how long it takes the boiler to trip if you have, say, the Rads on and you then call in the UFH, does it trip immediately or is there a time delay or whatever.

Thanks John for the clarification.

I tried this last night. I set up my phone to video the boiler temperature and the boiler pressure and then put the radiators and the UFH on. Unfortunately it didn't trip!! However, it was only a quick test as my wife was working nights so I didn't have long before we needed to eat and let her get ready for work.

I'm planning on trying it again tonight to see what happens.

I've also got the plumber coming back tomorrow as the heated floor is very 'patchy'. I'm wondering if it could possibly be a combination of air locks etc causing issues? However, he has promised to get to the bottom of it tomorrow.

I'll fire everything up properly tonight and see if it trips again. It certainly isn't tripping within a minute or two. If I had to guess I would say that it stays working for at least 20 minutes.

Obviouisly, I'll keep posting back with any developments this end - especially if the plumber gets to the bottom of it. :)
 

ShaunCorbs

Staff member
S. Mod
Plumber
Gas Engineer
Messages
28,890
Solutions
1
Apologies, all. It seems that (what I thought) was a TRV on the UFH manifold is, in fact, a "TMV" (Thermostatic Mixing Valve). as oppose to a Thermostatic Radiator Valve (I got a clue when I Googled TRV and saw that the "R" stands for Radiator :) )

@ShaunCorbs yes, there's a TRV on the radiator that has the grey pipe going to it and I can remove and test anything you would like? Just let me know what you'd like me to do and I'll try it. Thanks :)

Remove the trv the rad will act like a bypass and the 125 shouldn’t appear
 
Messages
2,199
Shaun, isn't the existing ABV acting (if in fact its opening at 1.2 M) as a huge by pass all the time with UFH on?.
 
Last edited:
Messages
24
Remove the trv the rad will act like a bypass and the 125 shouldn’t appear

Shaun, isn't the existing ABV acting (if in fact its opening at 1.2 M) as a huge by pass all the time?.

Shaun, really clever solution! Thanks.

I've spoken to the plumber and he has assured me that I already have auto bypass valve fitted and I'm hoping to keep that TRV on that radiator as I spend a lot of time in that room (converted garage) as it has my computer in there and an exercise bike (I'll melt if I can't turn that radiator down!! :) )

What is the "M" referring to in 1.2M? Is that metres cubed relating to the flow? Could the setting on the ABV be the issue?

Thanks :)
 
Messages
2,199
M = Meters, the ABV indexed setting is 0.1 to 0.5Bar which is 1 to 5 meters and as the pump head is always given in Meters (M) I just convert the ABV scale.
Regarding the garage rad, when you have the two systems on (and which subsequently trip) surely you have a number of other rads on? so one (garage) rad with a TRV should have little or no effect IMO.
That setting of 1.2M seems very low.
 
Messages
24
M = Meters, the ABV indexed setting is 0.1 to 0.5Bar which is 1 to 5 meters and as the pump head is always given in Meters (M) I just convert the ABV scale.
Regarding the garage rad, when you have the two systems on (and which subsequently trip) surely you have a number of other rads on? so one (garage) rad with a TRV should have little or no effect IMO.

Thanks for the explanation. Yes, I have rads on through-out the house - albeit at different levels on the TRV's.

Thanks :)
 
Messages
2,199
Something strange alright as ironically, the more the rad TRVs throttle in the more the set up tends to the UFH side (no trip). Is the ABV very hot on both sides of the pipework.
I think monitoring the boiler flow temperature later on will tell a lot, hopefully.

Also if the rad system is on alone then you can get huge deltaTs with no by pass and TRVs, my oil fired boiler regularly has a delta T of > 35C as I have no by pass fitted so again strange why your system doesn't trip on the rad system only.
 
Last edited:
Messages
24
Something strange alright as ironically, the more the rad TRVs throttle in the more the set up tends to the UFH side (no trip). Is the ABV very hot on both sides of the pipework.
I think monitoring the boiler flow temperature later on will tell a lot, hopefully.

Also if the rad system is on alone then you can get huge deltaTs with no by pass and TRVs, my oil fired boiler regularly has a delta T of > 35C as I have no by pass fitted so again strange why your system doesn't trip on the rad system only.
The full fault description of E125 is:
Circulation Fault (Primary Circuit)

Displayed in either of two situations:
- If within 15 seconds of the burner lighting the boiler temperature has not changed by 1°.
-If within 10 minutes of the burner lighting the boiler temperature twice exceeds the selected temperature by 30°. In these instances poor primary circulation is indicated.

So, are you saying that the DeltaT is the measurement for that second fault reason (If within 10 minutes of the burner lighting the boiler temperature twice exceeds the selected temperature by 30°. In these instances poor primary circulation is indicated.) ?
 

ShaunCorbs

Staff member
S. Mod
Plumber
Gas Engineer
Messages
28,890
Solutions
1
Can we just try removing the trv head for a day or two when you want either on will prove if there’s no flow eg no auto bypass on the primary’s
 
Messages
2,199
The full fault description of E125 is:
Circulation Fault (Primary Circuit)

Displayed in either of two situations:
- If within 15 seconds of the burner lighting the boiler temperature has not changed by 1°.
-If within 10 minutes of the burner lighting the boiler temperature twice exceeds the selected temperature by 30°. In these instances poor primary circulation is indicated.

So, are you saying that the DeltaT is the measurement for that second fault reason (If within 10 minutes of the burner lighting the boiler temperature twice exceeds the selected temperature by 30°. In these instances poor primary circulation is indicated.) ?
If it's the deltaT that its monitoring then yes, definitely a indication of poor circulation, but the actual wording doesn't say that, its says:
"the boiler temperature twice exceeds the selected temperature by 30°. In these instances poor primary circulation is indicated" which I interpret to mean that the boiler temperature must exceed the target or set point flow temperature by 30C, so if you have the boiler target (setpoint) temp set to 65C then the boiler flow temperature must exceed 95C before flagging this alarm/trip and perhaps this what is happening.
 

Reply to Reliability of fault codes potterton in the Central Heating Forum area at PlumbersForums.net

Similar threads

C
Hi, I've just noticed my diverter valve is leaking where the front part meets the rear part. The heating hasn't been on, only been using boiler for hot water lately The leak can be anything from a few drips to a few ml of water. Doesn't seem to leak all the time though. I replaced the diverter...
Replies
1
Views
264
W
D
Hi all First timer here - after reading a lot of the advice present I thought it would make sense to get stuck in and throw something into the ring. I am a Landlord and Agent operating new build properties in the Nottinghamshire areas, and have what seems to be an ongoing problem with one...
Replies
2
Views
894
Aquarius
A
Tcq889
Hi all, Homeowner here and would be really grateful of any feedback. I've had a new combi boiler installed into a 25y/o house yesterday. Now the boilers intermittently v loud and intermittently not giving hot for a little while. Signs it seems (tho not a professional) of the system being dirty...
Replies
16
Views
577
SJB060685
SJB060685
J
Hi Guys, I have a heat only boiler with two tanks in the loft. I have recently drained the system and since then i am not getting any hot water. The hot water tank front two pipes are hot, however the one coming out the top is cold. Radiators are heating up completely fine. Hot water taps...
Replies
21
Views
533
Undertrained
U
plumb_know
HI everyone, installed new ideal heat only boiler in replacement for dead potterton suprima, flushed system when boiler fitted, s plan system with bypass in working order, all works ok until circuits shut off then boiler over heats. pump overrun not provided on ideal logic and pump in airing...
Replies
71
Views
3K
John.g
J

Newest Threads (Please Reply)

Search Forum

Top