Something strange alright as ironically, the more the rad TRVs throttle in the more the set up tends to the UFH side (no trip). Is the ABV very hot on both sides of the pipework.
I think monitoring the boiler flow temperature later on will tell a lot, hopefully.
Also if the rad system is on alone then you can get huge deltaTs with no by pass and TRVs, my oil fired boiler regularly has a delta T of > 35C as I have no by pass fitted so again strange why your system doesn't trip on the rad system only.
I think monitoring the boiler flow temperature later on will tell a lot, hopefully.
Also if the rad system is on alone then you can get huge deltaTs with no by pass and TRVs, my oil fired boiler regularly has a delta T of > 35C as I have no by pass fitted so again strange why your system doesn't trip on the rad system only.