Search the forum,

Discuss Question for those with an unvented ticket in the Plumbing Jobs | The Job-board area at PlumbersForums.net

Status
Not open for further replies.

cr0ft

Plumbers Arms member
Plumber
Gas Engineer
Messages
3,311
Hi all. I have a new condensing system boiler which our gas fitter will be installing tomorrow. It's going to be installed right above a new unvented cylinder. As the airing cupboard they are both in is in the centre of the house, I want to run the PRV from the combi-boiler into the D2 pipework of the unvented cylinder (below the tundish). This way I will be able to tell whether or not the discharge is from the combi or the unvented cylinder in a fault situation.

Does anyone see any problem with this? I can't see any regulation that stops me connecting other relief valves to the D2 pipework.
 
Hi all. I have a new condensing system boiler which our gas fitter will be installing tomorrow. It's going to be installed right above a new unvented cylinder. As the airing cupboard they are both in is in the centre of the house, I want to run the PRV from the combi-boiler into the D2 pipework of the unvented cylinder (below the tundish). This way I will be able to tell whether or not the discharge is from the combi or the unvented cylinder in a fault situation.

Does anyone see any problem with this? I can't see any regulation that stops me connecting other relief valves to the D2 pipework.
your gsr plumber will advise you..for one moment reading between the lines, i thought you were going to fit it ,ha ha i know how stupid am i,.
 
The only issue I could really see would be overloading of D2 if both discharged at the same time and D2 was near the max length. Certainly better than teeing in above the tundish where there is a very minor risk of contamination of the potable water.
 
Hi all. I have a new condensing system boiler which our gas fitter will be installing tomorrow. It's going to be installed right above a new unvented cylinder. As the airing cupboard they are both in is in the centre of the house, I want to run the PRV from the combi-boiler into the D2 pipework of the unvented cylinder (below the tundish). This way I will be able to tell whether or not the discharge is from the combi or the unvented cylinder in a fault situation.

Does anyone see any problem with this? I can't see any regulation that stops me connecting other relief valves to the D2 pipework.
confusing thread, are you and if you are,why are you getting some one in,
 
Hi folks. Sorry for any confusion. I have my unvented ticket so I have fitted the cylinder but the gas fitter will be arriving tomorrow to fit the system boiler. I'm just not sure whether there's anything specifically preventing the PRV from the boiler being plumbed into the D2 outlet of the unvented cylinder. It discharges at low level outside the front of the house.

I'm not GSR, I subcontract out the boiler fitting on all the heating installs I do and I do all of the rest, controls and everything basically.
 
Sorry, my op was confusing. It should have read 'I am planning to ask the GSR to plumb the PRV from the combi-boiler into the D2 pipework from the unvented cylinder.' I just don't want to ask if it's illegal or anything like that, don't want to look stupid. My gut instinct tells me it will be fine tbh and I'm not aware of any regulations that prevent it being done.
 
D2 works out at a hydraulic resistance of about 8 metres so run in 22mm.
 
Nothing wrong in my opinion. Seen it done on number of occasions.
Run in metallic and has a safe, visible termination outside. Fits the bill!
 
i have done this with electric boiler so i can tell which is passing, goes to an outside drain bout same length as yours an i am happy with it and tested it an it was fine :~
 
Cool, that saves having to run another discharge pipe the same way then. Thanks all!
 
From the discharge outside and no visible discharge at the tundish on the hot water cylinder. That's why it's been plumbed in below the tundish.
 
Could do I suppose, but there's no need is there? Or is there? Discharge from pipe + outside and no discharge from cylinder tundish = boiler PRV, discharge from pipe outside + discharge from cylinder tundish = TPRV passing?
 
Status
Not open for further replies.

Reply to Question for those with an unvented ticket in the Plumbing Jobs | The Job-board area at PlumbersForums.net

Similar plumbing topics

Hi, Can anyone advise as to why the cold water to my bathroom keeps airlocking? This originally happened about 12 months ago and has happened 3-4 times since. It’s an upstairs bathroom, fed from a tank in the attic. The tank is about 8 Meters away and feeds a bath, sink and toilet. The tank...
Replies
9
Views
339
Hi, basic question, any insight much appreciated. Looking to have an outdoor tap in my front porch fed from 15mm pex coming up from suspended floor. Pic 1 is inside porch, pex temporarily clipped to give an idea of pipe placement (ignore shoddy blockwork of booted cowboy builder!), Pic 2 is...
Replies
6
Views
234
Hi all I'm hoping someone can shine a light on this for me Since our stop tap on the pavement has now been filled with sand for whatever reason, we are relying on our property fitted stopcock (this is outside on our garage wall) Unfortunately turning this to the closed position only reduces...
Replies
3
Views
252
Creating content since 2001. Untold Media.

Newest Plumbing Threads

Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock