Discuss Procombi exclusive 24 in the Plumbing Jobs | The Job-board area at PlumbersForums.net

Jacko

Gas Engineer
Messages
58
Hello all, advice needed please..... I have an intimintent F2 L2 fault on the above boiler, gas inlet pressure above 19 mbar, good spark achieved on ignition electrode, flue and condensate all clear, flame sensing electro replaced ( by the previous engineer), gas valve vaultages 220 DC on demand, gas valve resistance on two outer pins, 4.1 kohms, I have carried out a full stripped down service and hope this has cured the fault. If I receive the dreaded recall what else could be the fault?
 
Have you checked continuity on the flame sensing lead or other leads whilst giving them a good wiggle as that may show up a fault.

Sometimes if it is a lead/cable the heat can cause signal loss issue's which you will only sort be replacing the lead.

Could eventually end up as PCB but best to have a chat with Ideal tech line, never had a problem with them,

Andy
 
Have you checked continuity on the flame sensing lead or other leads whilst giving them a good wiggle as that may show up a fault.

Sometimes if it is a lead/cable the heat can cause signal loss issue's which you will only sort be replacing the lead.

Could eventually end up as PCB but best to have a chat with Ideal tech line, never had a problem with them,

Andy
All ideal tech tell you is to do a full service, and pour water down the heat exchanger.... they tell you to do that even when you have sludge in the system and overheat issues...as the flame sensing lead has been replaced they reckon it’s either the gv or pcb...... too expensive to guess.... ideal boilers rubbish when they come to fault finding it’s always either this that or the other !!!!!
 
If it’s a gamble then fixed price repair from Ideal is the best way
 
Isn’t L2 normally electrodes / condense / PCB?
very rarely pcb fault. you need to measure flame current to see what is happening on ignition. intermitant ignition faults can be caused by trap not emptying properly if connected below sink trap with other traps on drains airlocking trap and not allowing atmospheric pressure to work syphon properly. detection leads not a problem
 

Reply to Procombi exclusive 24 in the Plumbing Jobs | The Job-board area at PlumbersForums.net

Similar plumbing topics

Hi all, having an issue with a Logic Heat Only. On a few occasions early this year the boiler was going to fault code L2/F2. The electrodes, gas...
Replies
1
Views
2K
Deleted member 120897
D
L
  • Locked
been trying to get this blighter working! called out recently, only firing on low rate with lot of woomping noise and as soon as it tries to go...
Replies
26
Views
374
lame plumber
L
  • Locked
AGC Fanfare range of Wa units Transformer 240v AC 1.2ohms Secondary Circuit AGC Fanfare range of Wa units Transformer 240v AC 20 ohms Primary...
Replies
35
Views
654
  • Locked
I had a part fit job off one of the other guys at work - fit a PCB for a Glow-worm 24CXI, easy job.... I couldn't get hold of him to find out the...
Replies
19
Views
122
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock