Hello all, advice needed please..... I have an intimintent F2 L2 fault on the above boiler, gas inlet pressure above 19 mbar, good spark achieved on ignition electrode, flue and condensate all clear, flame sensing electro replaced ( by the previous engineer), gas valve vaultages 220 DC on demand, gas valve resistance on two outer pins, 4.1 kohms, I have carried out a full stripped down service and hope this has cured the fault. If I receive the dreaded recall what else could be the fault?
 
Have you checked continuity on the flame sensing lead or other leads whilst giving them a good wiggle as that may show up a fault.

Sometimes if it is a lead/cable the heat can cause signal loss issue's which you will only sort be replacing the lead.

Could eventually end up as PCB but best to have a chat with Ideal tech line, never had a problem with them,

Andy
 
Have you checked continuity on the flame sensing lead or other leads whilst giving them a good wiggle as that may show up a fault.

Sometimes if it is a lead/cable the heat can cause signal loss issue's which you will only sort be replacing the lead.

Could eventually end up as PCB but best to have a chat with Ideal tech line, never had a problem with them,

Andy
All ideal tech tell you is to do a full service, and pour water down the heat exchanger.... they tell you to do that even when you have sludge in the system and overheat issues...as the flame sensing lead has been replaced they reckon it’s either the gv or pcb...... too expensive to guess.... ideal boilers rubbish when they come to fault finding it’s always either this that or the other !!!!!
 
If it’s a gamble then fixed price repair from Ideal is the best way
 
Isn’t L2 normally electrodes / condense / PCB?
very rarely pcb fault. you need to measure flame current to see what is happening on ignition. intermitant ignition faults can be caused by trap not emptying properly if connected below sink trap with other traps on drains airlocking trap and not allowing atmospheric pressure to work syphon properly. detection leads not a problem
 

Reply to Procombi exclusive 24 in the Plumbing Jobs | The Job-board area at PlumbersForums.net

Similar plumbing topics

We run a community village hall and have a large kitchen provided for the use of hirers. This includes a Lincat SLR9 gas cooker which I believe is...
Replies
5
Views
610
Hi all. Hope you have all been keeping well. A while back I decided I only wanted to fit one brand of boiler and decided on Viessmann due to...
Replies
9
Views
403
Every two weeks or so I have to go and top up the system because the hot taps are running cold. Boiler display is flashing 0.6 bar and I fill up...
Replies
2
Views
331
PSxxxxxx
P
Hi, Can anyone advise as to why the cold water to my bathroom keeps airlocking? This originally happened about 12 months ago and has happened 3-4...
Replies
9
Views
507
Back
Top