I am having a problem with the boiler when after running for approx 45mins and the house is approaching temperature that the boler will start cycling (switching off and then back on again after approx 1 min)

I have detailed what is happening and used the Valliant codes. I have a weather compensator fitted as well.
Valliant codes
d0 = range rated setting
d41= return temp
d40= feed temp

When the system is cold, the system fires up, runs at a high setting (I assume d0 related) and brings the flow d40 (feed) up to flow temp target.

At this time d41 (return) will be some way behind d40 approx 20c below.

As d40 is now at target temp the boiler modulates down to maintain d40 at target temp but at the same time d41 is slowly increasingp. As d41 increase the heat requied to maintain d40 falls so the system continues to modulate down.

Now my problem!!!!

As d41 (return) increases, d40 continues to rise unless the system can modulate down to a lower enough output to stop this. My problem appears that it cannot modulate low enough so the system shuts down.

Temp then falls rapidly and about 1-2 mins later system refires at highish output and quickly exceeds target temp and the system gets into a cycle.

I have raised minimum temp (50c) which helps a bit and lowered d0 which helps a bit. I can force it out of the cycles by temporally raising min temp.

Is there anything else I can do. (ecoTEC 418)

Gary
 
Status
Not open for further replies.

Reply to New Valliant ecoTEC 418 issue in the Plumbing Jobs | The Job-board area at PlumbersForums.net

Similar plumbing topics

Hi, Can anyone advise as to why the cold water to my bathroom keeps airlocking? This originally happened about 12 months ago and has happened 3-4 times since. It’s an upstairs bathroom, fed from a tank in the attic. The tank is about 8 Meters away and feeds a bath, sink and toilet. The tank...
Replies
9
Views
310
We are from Alberta, and I own an electrical company. I have been asked by a BC Mechanical P. Eng. to install an emergency STOP button at the man-door to the boiler room. It's intent is to 'halt' the operation of the boilers in the room should there be an emergency. He is demanding that I do...
Replies
5
Views
237
We run a community village hall and have a large kitchen provided for the use of hirers. This includes a Lincat SLR9 gas cooker which I believe is a 23.8Kw appliance with all six burners and oven on max. This was installed some 10 years ago and has passed all subsequent Gas Safety inspections as...
Replies
4
Views
390
Creating content since 2001. Untold Media.

Newest Plumbing Threads

Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock