Just wondered if anyone had experienced anything like this before I call Glow Worm on tuesday. Have just fitted new Ultracom 18 sxi system boiler to an existing system. System is Y plan and have also fitted new Honeywell 7 day programmer and roomstat - although this problem is not related to external controls. Calling for heat or hot water or both and everything works fine however if HW and CH are switched off at programmer the boiler still stays running. Putting a meter on the switched live at the boiler shows no voltage so the controls arent calling. I have even removed the switched live wire from the boiler so that it just has the power supply, switched the boiler back on and after a few minutes it will fire up and stay burning at a low rate. the boiler is inside the house and there is no frost stat wired up.??
Many thanks
 
you may have your permanent live and switch live the wrong way around ,good luck
 
i would tend to agree,hope you sort it sounds like the boilers getting 240 from somewhere
 
its a nice easy one to sort out ,it only took me about a day and a half to sort out as my wiring skills are not that good and my mate who has a failed physics degree wired the bloody thing up wrong lol good luck
 
according to the manual there is a built in frost protection device that operates according to the temp of the water (8 deg) operating the pump and eventually the burner if temp not met irrespective of any external controls
hope this helps
 
have you left your 3 port valve manually open after your flush
 
There is a link(for 24v roomstat) in the left hand side on the pcb for low volt controlls which needs to be removed if being fitted to an existing system.
They neglected to put this in the mi's.
Remove and all will be well!
 
There is a link(for 24v roomstat) in the left hand side on the pcb for low volt controlls which needs to be removed if being fitted to an existing system.
They neglected to put this in the mi's.
Remove and all will be well!

Many thanks, that sounds exactly the problem and would give the symptoms i'm experiencing - I didnt think to check for a loop on the low voltage side and the MI's do not mention this. Will be going back to the clients on tuesday and will confirm findings.
Cheers
 
Actually, couldnt wait, went to customers yesterday after reading the post from prs1. Absoloutely spot on and problem now fixed. Many thanks.
 
Status
Not open for further replies.

Reply to New Glow Worm Ultracom 18sxi wont switch off !!! in the Plumbing Jobs | The Job-board area at PlumbersForums.net

Similar plumbing topics

Hi, Can anyone advise as to why the cold water to my bathroom keeps airlocking? This originally happened about 12 months ago and has happened 3-4...
Replies
9
Views
510
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock