Search the forum,

Discuss Immersion heater very little hot water in the Central Heating Forum area at PlumbersForums.net

Messages
8
I moved into a flat over a month ago now and realized when trying to take a shower that there was little to no hot water - at this time I would turn the water on full out, it would stay cold for maybe 30 sec, it would then get noticeably warmer (lukewarm) and then run out again in maybe 15 seconds.

I reported the issue and had someone attend who said that something had been tripped in the heater, he reset it and said it would take a while to heat up but it would be fine. The next morning it got much hotter much faster - to the point where it was scalding/uncomfortable on full heat - only to then promptly run out and be back to lukewarm in under a minute. As this was an improvement I tried to make do, but given that I was still shivering in my shower I reported that the issue hadn't been resolved.

They reattended yesterday, bled the thing, and told me everything was working fine. They even showed me and had a lot of hot water coming out for longer than I'd ever gotten it with no signs of running out. He also had me touch a little copper faucet on heater to show me it was getting hot (?). Before leaving they noticed that the timer was set for only 1 hour, so they put it longer and told me that would fix the problem.

This morning I was greeted by a return to how things were before they attended the first time - a long while to heat up just a bit before petering out. I'm at my wits end here, these contractors seem to be useless but I don't really have a reason to doubt when they say it is working correctly. I only yesterday discovered the little control panel with the settings, is this something that I can fix by setting it properly, or do I need to give in and get a plumber I'm actually paying to come take a look? I've only touched it to confirm that the schedule is now set to between 3:15-8:15, 8:16-9:16.

Thanks for the help, I've put some pictures of the heater/panel below:

20220406_092321.jpg


20220406_092328.jpg
 
If you knew the cylinder volume and immersion heater power in watts you could calculate how long it would take to heat up. Typically you would time to heat the water in advance to your usage. If you showered at 7am and the cylinder required an hour to heat up then you would time it from 6am to 7.30 for example. You seem to have adjusted the times but if you’re still having Luke warm water problems then you could have a faulty immersion heater, possible loose connection etc.
To avoid further nuisance problems I would have a decent plumber attend, or an electrician.
 
If you knew the cylinder volume and immersion heater power in watts you could calculate how long it would take to heat up. Typically you would time to heat the water in advance to your usage. If you showered at 7am and the cylinder required an hour to heat up then you would time it from 6am to 7.30 for example. You seem to have adjusted the times but if you’re still having Luke warm water problems then you could have a faulty immersion heater, possible loose connection etc.
To avoid further nuisance problems I would have a decent plumber attend, or an electrician.
Sticker on the side says:
2.7 kW 230v / 3.0 kW 240v (for both timed boost and off peak)
And primary store capacity: 150L.

I'll try to calculate that myself when I have time, seems a bit complicated but would be good to know.

That's what I was afraid of - annoying that this is definitely meant to be the landlord's problem.
 
Sticker on the side says:
2.7 kW 230v / 3.0 kW 240v (for both timed boost and off peak)
And primary store capacity: 150L.

I'll try to calculate that myself when I have time, seems a bit complicated but would be good to know.

That's what I was afraid of - annoying that this is definitely meant to be the landlord's problem.
Quick calculations suggest a 2.7kw immersion will heat 150 litres in around 3 and a half hours.
 
Don’t you have a thermostatic shower ? Or is it just manual
 
There may be two heating elements with the upper one only heating say 50 litres or so or the element(s) may just be tripping out after a very short period, even 50 litres at 60C should give a 40C shower for ~ 8 minutes at a flowrate of 10LPM.
Can you monitor your elec meter when its supposed to be on.
 
There may be two heating elements with the upper one only heating say 50 litres or so or the element(s) may just be tripping out after a very short period, even 50 litres at 60C should give a 40C shower for ~ 8 minutes at a flowrate of 10LPM.
Can you monitor your elec meter when its supposed to be on.
From everything I've gathered about this model etc. I do believe that there are 2 heating elements, there's a "boost" button that should turn the top one on for an hour. From what I can tell they've programmed a "timed boost" from 7am to 11pm which is meant to turn on the top element and the boost button is red as if it were activated during those times. Left it today to see if maybe the top element worked better than the bottom, but just checked and fails to get past lukewarm. Have shut off the timed boost since I don't need that wasting my electricity anyway.

Unfortunately the meter is in a cupboard down the hall, I need to ask the concierge for keys to access it. Not troublesome once in a while but monitoring continuously is a bit difficult.
 
If the boost element is heating the top half of the cylinder, say 75 litres, then 2.7kw should heat the water from 15C to 60C in 1.5 hrs or from 15C to 46C if you just hit the "one hour" boost button, you can easily see where this element is located, height wise in the cylinder.
 
You need to establish if both heating elements are actually working.

Those controllers fail, the meter could have changed and you don't have e7 , one of the immersions could have failed
 
From what I can tell they've programmed a "timed boost" from 7am to 11pm which is meant to turn on the top element and the boost button is red as if it were activated during those times.

With that set up you want to start by setting up the standard 'economy 7' programme, which refers to the lower element, to come on from 0200 to 0700 (Or whatever period of about 5 hours is safely inside your cheap rate period.) and no timed boost. This should get you a tank full of hot water, enough for about three baths or showers. Use the boost manual or timed if you find that is not enough to last a whole day.

My guess is that the lower element is faulty so someone is decided to use the timed boost as a temporary workaround and never got round to fixing it properly.
 
With that set up you want to start by setting up the standard 'economy 7' programme, which refers to the lower element, to come on from 0200 to 0700 (Or whatever period of about 5 hours is safely inside your cheap rate period.) and no timed boost. This should get you a tank full of hot water, enough for about three baths or showers. Use the boost manual or timed if you find that is not enough to last a whole day.

My guess is that the lower element is faulty so someone is decided to use the timed boost as a temporary workaround and never got round to fixing it properly.
This honestly feels consistent with everything that's happened, notably the original issue being that something "tripped" leaving me with no hot water, that being fixed and then having some, and then they attend again, can get hot water out, but they leave and it's back to square one. The boost button does nothing at the minute (button gets red but no hot water) so could it be that overusing the top element for long periods is what causes it to trip? Obviously I have no idea but it seems to make sense.
 
You need to establish if both heating elements are actually working.

Those controllers fail, the meter could have changed and you don't have e7 , one of the immersions could have failed
I can verify that I still have e7, and if the controller failed it's done a very sneaky job of it, although I've given it a reset to see if that changes anything. Is there anyway for me to check myself if the immersions are working, beyond the basic observations that 1/ it's been scheduled to turn on at night and that does jack and 2/ the boost button turns red but otherwise does jack?
 
I can verify that I still have e7, and if the controller failed it's done a very sneaky job of it, although I've given it a reset to see if that changes anything. Is there anyway for me to check myself if the immersions are working, beyond the basic observations that 1/ it's been scheduled to turn on at night and that does jack and 2/ the boost button turns red but otherwise does jack?

How have you verified you have E7?

Some form of proper tested is required to check that an immersion is working (about 19 - 20 ohms is a sensible reading)

I would suggest you seek a competent spark with proper test kit
 
How have you verified you have E7?

Some form of proper tested is required to check that an immersion is working (about 19 - 20 ohms is a sensible reading)

I would suggest you seek a competent spark with proper test kit
-My meter says e7 on it and gives two readings

-When I submit a reading Bulb asks for two readings and then on my bill they charge them at different prices

Is there more to having an e7 meter than that?

What kind of (electric) meter do you have?.
I've attached a photo for reference.
 

Attachments

  • Screenshot_20220412-210351_Video Player.jpg
    Screenshot_20220412-210351_Video Player.jpg
    366.4 KB · Views: 6
As a spot check, the meter will give a very good indication of whether the immersion element(s) is in use or not.
This is a good idea and I may give it a go if I can't get someone to take a proper look at it. It's just a bit of a hassle as all the meters in the building are kept locked up and you have to go ask for the key. Additionally not sure how to differentiate between everything else and the heater, but I'm sure I'll figure it out if it comes to it. Thanks for all the advice!
 
Just ensure any big users like a electric kettle, toaster, micro wave etc all off, lights etc make little or no difference. When you think the immersion should be on note the time in secs in takes for the 1000 imp/kwh LED to flash 10 times (after the first flash), if it takes 13/14 secs (13.3 to be exact) then you know the element is producing 2.7kw. If the element isn't drawing power then there will only be a flash after every 7 to 10 secs or so.
 

Reply to Immersion heater very little hot water in the Central Heating Forum area at PlumbersForums.net

Similar plumbing topics

  • Question
Ideal Logic 24, Previous problem was that the hot water was only cold or barely warm if the heating was in use. If heating was off and boiler cold then would get hot water most of the time. Changing the flow cartridge about 2 years ago (when I moved in) solved this problem enough to suffer it as...
Replies
2
Views
139
Hello, I am seeking some advice, I have a POTTERTON PROMAX 28 COMBI Boiler and I noticed yesterday that the water around the house is no longer warming up. The heat exchanger has been changed 6 months ago, so I do not believe it is that. Does anyone have any ideas on what it could be? Thanks
Replies
4
Views
232
Hi all I'm hoping someone can shine a light on this for me Since our stop tap on the pavement has now been filled with sand for whatever reason, we are relying on our property fitted stopcock (this is outside on our garage wall) Unfortunately turning this to the closed position only reduces...
Replies
3
Views
252
Hi, Can anyone advise as to why the cold water to my bathroom keeps airlocking? This originally happened about 12 months ago and has happened 3-4 times since. It’s an upstairs bathroom, fed from a tank in the attic. The tank is about 8 Meters away and feeds a bath, sink and toilet. The tank...
Replies
9
Views
339
Creating content since 2001. Untold Media.

Newest Plumbing Threads

Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.