Hi again everyone

Just about finished all my heat loss calcs with Stelrad Stars.

I just wondered about the ventilation / air changes. These significantly affect the heat requirements.

Currently they are set as the following changes per hour :

  • Living Room - 3
  • Drawing Room - 3
  • Dining Room - 2
  • Hall - 2
  • Kitchen - 3
  • Utility Room - 2
  • Landing - 2
  • Bathroom - 3
  • Bedrooms - 1.5
All the upper floor rooms have double glazed windows. The ground floor rooms are mostly single - weatherstripped - soon to be double glazed. Ground floors are suspended timber. Living & Drawing rooms have open fires with requisite chimneys.

Are these air changes per hour about right?
 
without checking my notes i think i normally allow 3 for rooms with extract fan and 1.5-2 for other rooms. Its been about 8 months since i have done long hand calculations tho.
 
Hi again everyone

Just about finished all my heat loss calcs with Stelrad Stars.

I just wondered about the ventilation / air changes. These significantly affect the heat requirements.

Currently they are set as the following changes per hour :
  • Living Room - 3
  • Drawing Room - 3
  • Dining Room - 2
  • Hall - 2
  • Kitchen - 3
  • Utility Room - 2
  • Landing - 2
  • Bathroom - 3
  • Bedrooms - 1.5
All the upper floor rooms have double glazed windows. The ground floor rooms are mostly single - weatherstripped - soon to be double glazed. Ground floors are suspended timber. Living & Drawing rooms have open fires with requisite chimneys.

Are these air changes per hour about right?

i use 1.5 for every room
 
Slight tongue in cheek remark but don't these figures get thrown out of the window when the windows are open? And if it's blowing a gale ...
 
Would two changes suffice for the rooms with open fires (chinmeys) and suspended timber floors with plenty of underfloor ventilation?

The house by the way is a victorian semi with 10ft ceilings - and a bit draughty here & there - though I'm attending to that as best I can with weatherstripping etc.
 
Lol. Just to add. New builds should have an air change of 0.5 per hour !!!!
 
1.5 should be fine, the size of the room is part of the calc in a different area so no need to compensate here as well
 
Status
Not open for further replies.

Reply to Heat Loss Calcs - Air Changes in the Plumbing Jobs | The Job-board area at PlumbersForums.net

Similar plumbing topics

  • Question
Ideal Logic 24, Previous problem was that the hot water was only cold or barely warm if the heating was in use. If heating was off and boiler cold then would get hot water most of the time. Changing the flow cartridge about 2 years ago (when I moved in) solved this problem enough to suffer it as...
Replies
2
Views
150
Hi, Can anyone advise as to why the cold water to my bathroom keeps airlocking? This originally happened about 12 months ago and has happened 3-4 times since. It’s an upstairs bathroom, fed from a tank in the attic. The tank is about 8 Meters away and feeds a bath, sink and toilet. The tank...
Replies
9
Views
365
We run a community village hall and have a large kitchen provided for the use of hirers. This includes a Lincat SLR9 gas cooker which I believe is a 23.8Kw appliance with all six burners and oven on max. This was installed some 10 years ago and has passed all subsequent Gas Safety inspections as...
Replies
5
Views
499
Creating content since 2001. Untold Media.

Newest Plumbing Threads

Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock