Hi guys,

customer has a glowworm hideaway 100B BF and the pilot keeps going out. Been to relight it a few times and I fires up straight away. Thinking the gas valve might be faulty as thermocouple has been replaced. The customer however has now told me that everytime the pilot goes out. Her 2 channel danfoss FP7175 display goes blank and only way to get it to come back on is to press the reset on it

now the programmer should cause the pilot to extinguish should it? Just the man burner. So if that's the cause, why is it found to be blank on the display when the pilot is also found to be out?

any ideas
 
Clean & Adjust pilot, could be main burner is pulling pilot away, bad draft from somewhere, or even someone slamming a door shut, but adjust pilot first
 
Does this model have a overheat interrupter on the thermocouple ?

No mate it doesn't. As for clock, I know the clock can't interfer with thermocouple, it's just if the customer is right in saying everytime the pilot goes out, the clock display is also off, why is this or is it just a coincidence
 
Coincidences happen. On Saturday went to a burnt out pump on a vaillant. Changed it and then no switch live to boiler.!
Crappy Drayton wireless stat receiver working intermittently! Replaced that, then Alls well.

two separate problems but both at the same time.
 
Its a total impossibility. New thermocouple, clean the injector, adjust the flame and tell her to put the smirnoff away :smile:
 
Maybe not the thermocouople , if the pilots not very strong then clean injector out as maybe just dirty, depending on if been done might aswell offer a service while there,
 
Its a total impossibility. New thermocouple, clean the injector, adjust the flame and tell her to put the smirnoff away :smile:

Never dismiss anything. I had a problem with a Baxi Bermuda years ago. Boiler kept going out despite new thermocouple etc. The customer was convinced it happened when the heating switched on. I tried it and, lo and behold, turn the room stat up and the pilot extinguished. Further investigation revealed that the earth to the property had been disconnected and when the heating switched on a small current was induced in the earth wire. This small current was enough to cancel out the current generated by the thermocouple and the pilot dropped out.
 