Imagine the flue is in a corner next to eaves. Only one of the 2 could be 25mm
Thanks for clearing that up. But, it can be that close to the eaves without a heatshield?
The flue can go 25mm from eaves/soffits etc. The issue is the soffit vents which flue must be at least 300mm from.
As long as you block off any ventilation opening within 300mm of flue you are good to go.
As mentioned a bit of plastic weather strip siliconed on will do. Stick a couple screws in to be on safe side.
if your using that existing hole then just extend flue past the eaves job done . Sometimes just go with your instinct. I find that the minimum distance below eaves the plume still goes under the eaves so i tend to extend past.[/QUOT
Not using existing hole as it is too close to window. Now it is 200mm below eaves. Do ideal say it is ok to use standard flue externally like that or a plume kit
not that straightforward sadly,lots of manuf now saying no white on show so vents need blockingif your using that existing hole then just extend flue past the eaves job done . Sometimes just go with your instinct. I find that the minimum distance below eaves the plume still goes under the eaves so i tend to extend past.