Guys,

After a long lay-off I am looking at getting back into the gas industry. I have tried to attach a drawn pic, but was unable to due to a repeated error.

My question is, if a conventional boiler is fitted within an airing cupboard (above the DHW cylinder - vertical flue) and the F/R pipes had a topside exit, I can simply connect the vent and cold feed to the flow above the boiler before dropping down to the pump, to then feed by-pass valve and so on...?

Also, just to confirm, would a manual air pip also be best placed on the return pipe out of the boiler, as well?

Thanks in advance.
 
Best to check head height and configuration in manufacturers instructions before committing. Are you registered to do this work?
 
Thanks for the reply, Vee.

I actually completed a full apprenticeship in plumbing and heating and passed my ACS, but that was some ten years ago. I am planning to re-enter the field in a few months, and was just recapping on a few things...

I am not planning to undertake any work. This is more for theory. Basically, an attempt to jog my memory...

I remember completing a few of these back in the day (Baxi solos conventional - some sealed - some open vented), but for the life of me I forgot how I configured the exiting pipework out of the boiler...
 
Guys,

After a long lay-off I am looking at getting back into the gas industry. I have tried to attach a drawn pic, but was unable to due to a repeated error.

My question is, if a conventional boiler is fitted within an airing cupboard (above the DHW cylinder - vertical flue) and the F/R pipes had a topside exit, I can simply connect the vent and cold feed to the flow above the boiler before dropping down to the pump, to then feed by-pass valve and so on...?

Also, just to confirm, would a manual air pip also be best placed on the return pipe out of the boiler, as well?

Thanks in advance.
Are thinking of going straight down into the pump, so it's pumping downwards? That's possible but I believe it's not ideal. Perhaps others will comment. Alternatively you could add a U-bend before the pump.
By manual air pip(e) do you mean a manual air release point? That would be useful to aid venting on initial fill and commissioning. You wouldn't want an open vent pipe there.
 
Thanks for the reply. And yes, going straight down to the pump. I have managed to attach a drawing of what I am trying to write...

147dc1fcc040e017486428a4eae6a58a.png
 
The above diagram assumes that the boiler is sited above the HW cylinder in the airing cupboard... And yes, I meant manual air release point :)
 
The above diagram assumes that the boiler is sited above the HW cylinder in the airing cupboard... And yes, I meant manual air release point :)
Just for interest, is pip a term for an air release point? I thought you'd misspelled pipe?
 
Sorry for the confusion. I was taught the correct terminology in college, but the engineer I shadowed during my apprenticeship always termed it 'air pip', or sometimes even just 'pip'.
 
My question is, if a conventional boiler is fitted within an airing cupboard (above the DHW cylinder - vertical flue) and the F/R pipes had a topside exit, I can simply connect the vent and cold feed to the flow above the boiler before dropping down to the pump, to then feed by-pass valve and so on...?
You need to check that the static head for the boiler and the pump meets the manufacturer's requirements. That's the drop from F/E tank water level to the boiler and pump inlets. If it's not sufficient the F/E tank may need raising (which could have a knock-on effect on the relative positions of F/E tank and cold water tank!).
 
Status
Not open for further replies.

Reply to Flow and return in airing cupboard. in the Plumbing Jobs | The Job-board area at PlumbersForums.net

Similar plumbing topics

Hi all. Hope you have all been keeping well. A while back I decided I only wanted to fit one brand of boiler and decided on Viessmann due to space for servicing and changing parts if ever needing to. I am finding my decision rather hard due to the different clearances on flue runs and cupboards...
Replies
9
Views
178
Hi, Can anyone advise as to why the cold water to my bathroom keeps airlocking? This originally happened about 12 months ago and has happened 3-4 times since. It’s an upstairs bathroom, fed from a tank in the attic. The tank is about 8 Meters away and feeds a bath, sink and toilet. The tank...
Replies
9
Views
316
We run a community village hall and have a large kitchen provided for the use of hirers. This includes a Lincat SLR9 gas cooker which I believe is a 23.8Kw appliance with all six burners and oven on max. This was installed some 10 years ago and has passed all subsequent Gas Safety inspections as...
Replies
5
Views
425
Creating content since 2001. Untold Media.

Newest Plumbing Threads

Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock